0

I have an old gas furnace without a circuit board. Just a 4064 fan limit control, 24v transformer, gas burner control and fan. I wired a new wifi thermostat in. It works great. I would like to be able to use the fan only control of the thermostat. Can I do this? Where would I connect the G wire? I was thinking I could remove the jumper in the 4064 limit controller. But if I use low voltage on the limit side will it still only allow the fan to run by temperature? There is a fan/auto switch on the 4064 that works.

1
  • 1
    Can you post photos of the furnace wiring, and a link to the manual for this fan limit control of yours? Commented May 18, 2020 at 23:49

1 Answer 1

1

You will need to add a 24 volt relay that is controlled by the green wire and a common and wire the relay contacts to bring on the fan by jumping the contacts in the 4064 fan/limit control. You can use a RIB relay or similar one.This is how it was done in the "old days".

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.