A few months ago I came home and turned on a light switch with no result. Checked the breaker panel and found the a lighting circuit breaker tripped. It reset with no issue.

A few days/weeks go by and the same thing happens again. This time the breaker can't be reset. Waiting a few hours or until next morning allows the breaker to be reset. At the present time the breaker was able to be reset but after turning on lights on the circuit it popped again (can't definitively tie it to a particular light or switch). I'm leaving it off.

Each time this has tripped no lights have been turned on and nothing has been plugged into the lone receptacle on the circuit.

I tightened the screws on the breaker at the panel, no joy. I swapped the wire to a different 15A breaker and that tripped also, so I think the breaker is ok.

I checked the wiring and the connections at the only receptacle and that seem good.

I can check all the switches and see if the connections are tight and look for shorts there.

Items on the circuit: Fluorescent ceiling and closet lights, one receptacle, one exterior flood light with a motion detector.

Question: Does having a light switch off isolate the associated light fixture from the circuit for trouble shooting purposes or do I physically have to disconnect the wires at the light fixture to see if that fixture is causing a short?

6
  • Do you have a multimeter? With the lights switched off, can you try disconnecting the hot wire from the breaker, and measure the resistance from that to your neutral bus?
    – Nate S.
    Commented Apr 16, 2019 at 15:45
  • AFCI, GFCI or just regular breakers? Commented Apr 16, 2019 at 15:46
  • Do not neglect the possibility that the problem is NOT at a fixture/junction. 99% are, but sometimes things happen in walls...
    – Ecnerwal
    Commented Apr 16, 2019 at 15:57
  • Nate i do have a multimeter. Would I have to turn off the main breaker in order to do the resistance test?
    – Genki
    Commented Apr 17, 2019 at 2:21
  • manassekatz: it is a regular breaker.
    – Genki
    Commented Apr 17, 2019 at 2:21

3 Answers 3

3

Even though you call them CBs, I'm trusting that you know the difference between a plain breaker and a GFCI/AFCI. If your breaker has a TEST button, this advice is no good.

The usual reason for this, particularly in a lighting circuit, is a ground hitting a hot wire/screw, typically on a switch - switches can shift when you operate them. It's either hitting the bare ground wire in the box, or it's hitting the side of a metal box. *

So if you remember a flash or sudden failure when you operated a switch, that's the first place to look.

One thing we often see is people using backstab connections. Those are a lazy shortcut used by builders in a hurry, but they provide generally poor connections. Those cause opens not shorts, so they aren't directly responsible for this. But it using backstabs means they didn't use the screws, and often the screws are left in the full, all-the-way-out** position. These are much more likely to snag a ground wire or hit the side of the box.

Once the screws are down (preferably with the wires under them and tightened to torque), you can avert further trouble by wrapping electrical tape around the perimeter of the switch (or receptacle) so the screws are covered up. I do that to make them safer to handle.

Another way hot wires trip is when they are wearing their "Daisy Dukes", that is, when the wire is stripped too much for the backstab, and leaving exposed conductor for a ground wire to find. That is bad workmanship, but then, so are backstabs generally :)

* Metal boxes are very much your friend. They provide a better safety shield for the wiring, they conduct heat away from hotspots so they stay too cool to start a fire, and (annoying though this may be right now) they assure trips in cases like this instead of leaving a problem to smolder. We've had people tear them out and go plastic in cases like this, but that's just hiding the symptom.

** screws have a detent/stop to keep them captive. It damages the threads to unscrew them any further. For screw-to-clamp types, it will make the anvil fall off, and the receptacle is scrap at that point!

8
  • They are regular breakers. No flashes when operating a switch. The fault happens normally over night or when away from the house or the circuit has not been activated in a while. The switches are in plastic boxes and are back stabbed with the screws left turned out. i'm going through each one to correct that and inspect the wiring. Some wire is exposed because too much insulation was stripped from the backstab wire. I'll try your taping suggestion too.
    – Genki
    Commented Apr 17, 2019 at 2:25
  • Does having a light switch off isolate the associated light fixture from the circuit for trouble shooting purposes or do I physically have to disconnect the wires at the light fixture to see if that fixture is causing a short?
    – Genki
    Commented Apr 17, 2019 at 2:34
  • @Genki yes, if it's wired correctly. When correcting backstabs, don't snip the wire off because that wastes wire length - patiently twist it out (it helps to jab a tiny screwdriver in the release slot). Backstabs cannot be used twice, however doing so won't cause this symptom. (they lose grip because spring strength is lost when the wire is pulled out.) Usually if you've got Daisy Dukes, that's just the right length for the screw :) Commented Apr 17, 2019 at 13:15
  • @ Harper, Thanks. So if I understand you correctly, turning off the light switch takes the associated fixture out of the circuit IF, it's wired correctly. So if I check, test all the switches and turn off all the switches I should be able to turn them back on one at a time to find the short. Is that correct? Assuming the short is not in the wall caused by a nail or mice.
    – Genki
    Commented Apr 17, 2019 at 14:02
  • Also, with double and triple pole switches I'm just going to have to use trial and error to find the off for the lighting circuit correct?
    – Genki
    Commented Apr 17, 2019 at 14:05
3

Coming back to this after more than a year. I wanted to give feedback about the solution to my problem and can't remember if I did or not.

I found that the electrician that wired the house had used the back stab method to attach the wires to the light switches. The plastic of the switch body surrounding the wire entry hole had fatigued after 20+ years of resisting the pressure of the bent wire inside the switch box and had cracked. This made a loose connection which shutting doors and even bumping the wall near the switch caused a short. Moral of the story, for me, never backstab.

1
  • 1
    Thanks for the followup, and yeah, backstabs are so named because they will stab you (or a future resident) in the back... Commented Feb 24, 2021 at 23:35
2

I had this once, checked the circuits, bulbs, fittings then finally thought "ok, replace the breaker", put a new breaker in and it was cured...

Another one, was a downstairs lighting circuit that was ok when going to bed and not working every morning - breaker off... Checked everything for weeks... Finally was redoing the upstairs wiring and took up a floor board and found 1 long nail that had punctured one wire... I stepped on that board every morning getting out of bed : every time I stepped on it > blown breaker...

Some faults take a huge amount of detective work...

2
  • 1
    I switched the wire from the faulty circuit to an adjacent breaker and that one tripped immediately also.
    – Genki
    Commented Apr 17, 2019 at 2:29
  • Oh brother, that's a tough one. I had one where romex cable was left exposed to the sun on an exterior light for many years. The plastic insulation deteriorated enough for the hot to short on the neutral blowing the breaker. Took me forever to find.
    – Genki
    Commented Apr 5, 2021 at 23:37

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.