1

In my garage I have a single 15 Amp circuit that has 4 receptacles on it. One of the receptacles has a refrigerator and an upright small freezer on it, all are non-self defrosting type. Nothing else is on the other receptacles. The 4 recepts are protected with one of them being a GFCI type.

I put in some shelving and am about to covered one of the recepts so I installed a 5th receptacle about 14 feet down the wall with wire-mold yesterday. Simple 14 ga wire with ground, 14 feet of wire. I simply connected it to the terminals on the 4th receptacle I intend to leave behind the shelving.

Turned the breaker back on after everything was installed correctly and with that 5th receptacle installed the GFCI recept will not reset? Why would that 14 feet of #14 wired to an added receptacle with no load applied anywhere,(except the two refrig/freezers plugged in), cause the GFCI Receptacle to stay tripped when a 50' extension cord plugged into that 4th recept works just fine?

After reading several of the comments here about how touchy some of these refrigerator and freezers are with GFCI protected circuits my next step will be to unplug the refrigerator and freezer from the circuit and reconnect the added on 5th receptacle and see if that works.. If so I'll simply run a new, dedicated circuit to the refrigerator & freezer location for them to have their own circuit.

Do you think replacing the GFCI receptacle with a regular non-GFCI recept and replacing the breaker with a GFCI breaker would also help so I can leave the refrigerator and freezer plugged into the circuit ? I am a former US NAVY repair electrician so I know how to wire properly.. but I must admit the intricacies of these GFCI recepts have me puzzled .. LOL..

1
  • 3
    Just for clarity, does the gfci trip/ not reset when nothing is plugged in? If so, I suspect a loose wire in something you assembled. And could you be specific about whether you tapped the line or the load terminals for your extension? Commented Aug 11, 2018 at 18:31

1 Answer 1

1

The fridge/freezer are a red herring. Cable length is a red herring. These are not the problem.

Here, simple logic applies. It worked before; you changed it; and now it doesn't work. I'm sorry, that's inescapable, and it tells us where to look.

Noting your credential, it may be a bit afield of mains wiring in buildings. Mains wiring is weird, that's the only way I can really describe it to an electrical professional. Different things are done for their own set of reasons. If you deep-dive into the gory details of the reasons, you eventually find they are well-founded - but until you do, they seem arbitrary and stupid, and it is tempting to ignore them and do what seems right.

In your case, first, go after the forehead-slappers. Look in both your new box and the box you tapped from (which I assume is not the GFCI) -- and look for anything out of order, but even more, focus on that floppy-doppy bare ground wire touching any of the screws. If you're using backstabs, stop using backstabs, but make sure you haven't left any bare wire sticking out for a ground wire to snag and touch. Contact between neutral and ground is super-bad. Normally it's a "silent but deadly, but in the case of GFCI, it will result in instant trip.

One common tactic is, after attaching all the wires to screws, run all the other screws down and wrap tape around the receptacle so it covers all the screws.


Now if you did tap the GFCI device, you are using the LOAD terminals but not correctly. You must use them for both hot and neutral. Using LOAD hot and LINE neutral or vice versa is a guaranteed trip. The nut of what's going on with GFCIs isn't that hard to understand:

enter image description here

Disregard the dashed lines, those are for extra phases on GFCIs equipped for extra phases. Do note the fact that the GFCI device completely ignores ground.

A GFCI+receptacle combo device is extra hard to understand because it's doing 2 totally unrelated things at once, like a destroyer that's a fleet oiler, or an E-2 that also does Prowler-style SEAD. What's actually happening is that it's exactly the black box with supply/LINE and protected-zone/LOAD -- except it also has 2 sockets hardwired to the LOAD terminals. (it still doesn't use ground, but the sockets use ground.)

On the right side, both hot and neutral are in the "protected zone". Most of my work is in conduit, and I intentionally use a different color - brown and gray - for protected-zone hot and neutral. Every load must tap protected-zone hot and neutral together.


Now: you may have a wrong read on the issue with GFCIs and refrigerators and freezers. It's not that they're "touchy" (by which I read: more likely to trip GFCIs all on their own). It's that there's a very severe risk of a nuisance GFCI trip for any reason destroying valuable food. A fridge is no more or less likely to trip a GFCI than any other motorized device.

However, Fridges/Freezers on a well-grounded circuit are not the use-case for GFCI, they are the exact opposite of the use-case.

  • GFCIs are there to protect humans from accidental shock. The grounded steel chassis of the fridge/freezer already does that.
  • GFCIs protect where humans are likely to come in contact with AC-energized parts. All that stuff in a fridge is at the bottom rear, where you can't get within 6' of it if it's installed in kitchen counters
  • GFCIs protect humans from 2-prong ungrounded equipment. Fridges are well-grounded.

Simply put, Code does not call for protecting fridges with GFCI. This discussion (uselessness of GFCI and cost of lost food) has been had within NFPA, and they chose to exclude fridges from GFCI requirements. The only way fridges get haled into GFCI is when they are placed in rooms where all receptacles have to be GFCI, and even then, only because you are choosing a cord-and-plug connection for your appliance.

Hardwire it, poof, GFCI requirement goes away.


So, because of the risk of food loss, having a fridge/freezer on GFCI is a bad idea. What's an even worse idea is having the fridge/freezer on a shared circuit with general receptacles. So yes. You should definitely run a separate dedicated circuit to power the fridge/freezer.

And since that might require pulling a permit, you should go have a talk with your AHJ (the guy who issues the permits) and ask him if GFCIs are really necessary on receptacles that serve only fridge/freezer. He may say "That's fine, 1 circuit, 1 socket" -- Because usually these conversations assume ONE refrigerator OR freezer and so require a 1-socket receptacle so you can't plug anything else into that circuit. So you'd have to have the "I have both" discussion and see whether he'll allow a duplex receptacle or want 2 dedicated circuits with 1-socket receptacles. If you've got the panel space, Romex is cheap, so why not.

Plan Charlie, is hardwire the fridge-freezer, by having their cords enter a junction box with a quality strain relief, then splicing in the junction box. This means lopping off their sockets, or my preference, go to the electrical supply and get wet-rated cordage of appropriate rating and replace the whole cord, saving the old cord for when you sell it.

1
  • Harper,we aren't supposed to say"thanks".. so I won't.(but Thanks).. I unplugged the refrigerator and freezer from the circuit. Through process of elimination discovered that the brand new Levitron had a defective ground.. replace with new Levitron.. everything works perfectly.. I always use side screws and tape..it's how I was trained. and it's a great habit to get into if someone doesn't do that...LOL.. Good information on GFIC receptacles.. Have a good day.. Commented Aug 15, 2018 at 17:13

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.