Code changes require all living areas to be arc and ground fault protected. Finishing basement and initially used standard breakers with no issues. When I learned of code changes, replaced all breakers with dual function breakers. One of the light circuits immediately trips when energized. Tried another new dual function and got same result. Tried standard breaker again and it worked fine. Pulled all switches to ensure connections were right/tight. Looking for troubleshooting ideas.

2
  • 2
    One of the light circuits immediately trips when energized. Tried another new dual function and got same result. Tried standard breaker again and it worked fine. Q.E.D. you have a fault at least one of the two additional function types (Arc Fault or Ground Fault or both) on that circuit. Find it and fix it.
    – Ecnerwal
    Commented Oct 2, 2022 at 22:49
  • 1
    I had the same problem with a radon detector. No detector = no beeps in my basement. Radon detector installed = many beeps in my basement. It seems to only occur when I have the radon detector installed. 3 different detectors did the same thing. It's a mystery. Shrug, not sure why we even need it... Commented Oct 3, 2022 at 0:40

1 Answer 1

5

The first thing to do is to check the manual and find out how to distinguish between arc fault, ground fault and overcurrent types of breaker trips.

Since a regular breaker works fine, that should rule out overcurrent problems. Since this is new wiring, that should rule out arc faults. Not an absolute guarantee, but the typical arc fault problems are thinks likely faulty insulation, nails through wires, loose connections, etc. all of which should not be happening on a reasonably well done new installation.

That leaves ground faults, provided the troubleshooting in the instructions agrees. That can easily happen if you have:

  • Neutrals shared between circuits
  • Neutrals crossed between circuits
  • Neutrals connected to the neutral bar instead of to the breaker (an ordinary breaker doesn't have a neutral connection, AFCI/GFCI breakers do)
  • Neutral and ground combined anywhere in the circuit. For example, a neutral screw touching a metal box will not cause a problem for a regular circuit breaker but will result in some current going through ground, resulting in an immediate GFCI trip.