I have an ungrounded circuit in my house with three-wire grounded receptacles. If I install a GFCI, will the downstream receptacles be protected even if the GFCI is ungrounded?

1 Answer 1

8

Absolutely, as long as you place the load wires going to the downstream receptacles onto the LOAD terminals of the GFCI receptacle.

A GFI does NOT need an equipment grounding conductor to function properly. In fact, using a GFI at the beginning of the circuit is what will allow you to legally and safely use 3-prong receptacles downstream. Thing is, this does not create an equipment ground for equipment protection for things such as surge suppressors.

By code you are supposed to label any non-grounding downstream receptacles "No equipment ground present".

3
  • Is there a limit to the number of receptacles protected by a single GFI? Commented Sep 6, 2015 at 13:09
  • From checking various seemingly reputable online sources, as well as checking my Leviton GFCI, it seems there is no limit on the number of outlets you can protect. Bonus advice: the cheap GFCI testers won't trip the GFCI if they're not grounded. I thought I got a bad GFCI until I realized this. Commented Sep 7, 2015 at 1:43
  • 1
    There is no limit technically. We typically limit load side devices to 5-6. Every device will have a tiny amount of leakage, so with too many on the load side there is an increased chance of nuisance tripping. Commented Sep 7, 2015 at 18:05