Neutral and ground should only be bonded at the service equipment. This could be at the meterservice drop, the main disconnectmeter, or the main panelservice disconnect (250.24(A)(1)).

Looks like the neutral is bonded in your main panel, via the bonding screw.

enter image description here

The second panel is then fed using four wires, to keep ground and neutral separate.

enter image description here

Neutral and ground should only be bonded at the service equipment. This could be at the meter, the main disconnect, or the main panel.

Looks like the neutral is bonded in your main panel, via the bonding screw.

enter image description here

The second panel is then fed using four wires, to keep ground and neutral separate.

enter image description here

Neutral and ground should only be bonded at the service equipment. This could be at the service drop, the meter, or the service disconnect (250.24(A)(1)).

Looks like the neutral is bonded in your main panel, via the bonding screw.

enter image description here

The second panel is then fed using four wires, to keep ground and neutral separate.

enter image description here

added 162 characters in body; added 168 characters in body
Source Link
Tester101
  • 132.4k
  • 79
  • 324
  • 612

Neutral and ground should only be bonded at the service equipment. This could be at the meter, the main disconnect, or the main panel.

Looks like the neutral is bonded in your main panel, via the bonding screw.

enter image description here

The second panel is then fed using four wires, to keep ground and neutral separate.

enter image description here

Neutral and ground should only be bonded at the service equipment. This could be at the meter, the main disconnect, or the main panel.

Neutral and ground should only be bonded at the service equipment. This could be at the meter, the main disconnect, or the main panel.

Looks like the neutral is bonded in your main panel, via the bonding screw.

enter image description here

The second panel is then fed using four wires, to keep ground and neutral separate.

enter image description here

Source Link
Tester101
  • 132.4k
  • 79
  • 324
  • 612

Neutral and ground should only be bonded at the service equipment. This could be at the meter, the main disconnect, or the main panel.