Aug 22, 2017 at 19:23 comment added user74603 What do you mean by power bar? Just a power strip, or a UPS? – Hart CO 1 hour ago a power strip. Standard run of the mill type stuff with a reset button etc. I have tried three different bars with the same result.
Aug 22, 2017 at 18:00 comment added CactusCake It's possible you have a loose connection somewhere. Once you start drawing a certain amount of current, the resistance generates enough heat in the wire to (physically) move it, causing a break in the circuit. When it cools, it moves back and the connection is restored. Backstab connectors on cheap outlets are a common culprit. Use the breaker to disconnect the circuit and inspect your connections inside the outlet boxes, move wires from backstabs to the screw terminals if you encounter their use.
Aug 22, 2017 at 17:48 answer added Natificent timeline score: -1
Aug 22, 2017 at 17:40 comment added Hart CO What do you mean by power bar? Just a power strip, or a UPS?
Aug 22, 2017 at 17:36 comment added user74603 Plugged in a lamp to the 110v and the lamp worked (two prong). I then plugged the laptop into one plug on the box and the power bar into the othe. The laptop would run by itself and one item from the PB would run by it self but as soon as I added more draw by turning on other device it would go down. By go down I mean the Laptop would shut down or the hub would cycle on and off etc. It still would not throw the breaker though. Again the 110v has nothing to do with the 220v other than they both go to the same panel.
Aug 22, 2017 at 17:09 comment added user74603 @Tyson the equipment is / are 3 x 15a 220v input Delta Power Supply Units 2,400W Max 13v (output). The draw on each was 1,300W peak I believe and they are 3 wire devices (one neutral two hot) C19 style plugs.
Aug 22, 2017 at 17:04 comment added user74603 The circuits are totally separate other than they go to the same B panel. it's in an out build unrelated to my house. all other lights in the building work. I wired the 220v and the 110v was done years ago by an electrician.
Aug 22, 2017 at 16:46 comment added Tyson @Harper sure, unless it's 4-wire equipment that also needs neutral because part of its not really 240v.
Aug 22, 2017 at 16:38 comment added Harper - Reinstate Monica Do the two circuits share any wires? (Other than ground, we don't care if they share ground). Who wired this? Do you have any other loads in this house? Does the rest of the house work? @Tyson a lost neutral wouldn't affect 240V equipment, but a lost phase would.
Aug 22, 2017 at 16:28 comment added user74603 I'm in Canada. I have not plugged anything else into the circuits; mostly because I don't have anything else that runs on 220v and I have not tried the lamp idea. I will give that a go on the 110v circuit and see what happens. I have the breakers turned off to both at the moment to avoid damage to anything else.
Aug 22, 2017 at 15:59 comment added Tyson You likely have an open neutral -- be careful you my fry other stuff. Also, in what country are you located?
Aug 22, 2017 at 15:51 comment added CactusCake Have you plugged a lamp into any of those outlets? Need to determine whether the issue is with the equipment vs the circuit. A wire tester can still show continuity even if the current is really low. A lamp will tell you if you're getting more than just phantom voltage.
Aug 22, 2017 at 15:43 review First posts
Aug 22, 2017 at 19:19
Aug 22, 2017 at 15:41 history asked user74603 CC BY-SA 3.0