47 votes
Accepted

Can I cut out a leak, in the middle of a stainless braided water line, and splice it back, under the kitchen sink?

Unless you have a considerable array of specialized hose-crimping equipment - No, they are disposable, not repairable.
Ecnerwal's user avatar
  • 220k
19 votes

Can cable splice devices be concealed?

The use of these devices is limited to specific situations, which are described in 334.40(B) of the National Electrical Code. The 2011 version of the code had this to say. National Electrical Code ...
Tester101's user avatar
  • 132k
17 votes

Can I cut out a leak, in the middle of a stainless braided water line, and splice it back, under the kitchen sink?

Totally agree with other answers. Replace the leaking jacketed flexible faucet supply line. These things are not that expensive. A typical 12 inch or 16 inch Braided Stainless Steel Flexible Faucet ...
Michael Karas's user avatar
  • 65.1k
11 votes
Accepted

Can I splice large wire for long runs?

Your run is too long for your GFCI Your GFCI is tripping, not necessarily because your pump is faulty or your GFCI is broken, but because you are well outside the 250' maximum cable length limit in ...
ThreePhaseEel's user avatar
9 votes
Accepted

Are split bolts wrapped in splicing tape rated for live connections?

If you are discontent with the quality of wire nuts, you can go to a proper splice block. These are my go-to for anything larger than 6 AWG. Source The wires are inserted in the side, then they ...
Harper - Reinstate Monica's user avatar
9 votes

Can I cut out a leak, in the middle of a stainless braided water line, and splice it back, under the kitchen sink?

You probably could do that and have it last for a few minutes. By the time you found the proper size rubber connector and hose clamps, you'd have spent more than buying a new supply line. And that ...
JACK's user avatar
  • 82.1k
9 votes

Can I splice large wire for long runs?

Wire's insanely expensive The trick with bumps for voltage drop This is the death of countless power projects: "Either I didn't check, or I know the Load Calc will force me into several wire ...
Harper - Reinstate Monica's user avatar
7 votes
Accepted

Safest Way to Contain Spliced Lamp Cord

This family of lights uses all 120v wiring which means the full weight of NEC applies. You cannot "freestyle" splices in the manner you are talking, you must use listed products, which those cheapie ...
Harper - Reinstate Monica's user avatar
7 votes

Are split bolts wrapped in splicing tape rated for live connections?

To answer your question, split-bolts properly insulated (as you've done) certainly ARE rated for "live" conductors. Ask your inspector to provide the code citation prohibiting them. For decades split-...
Speedy Petey's user avatar
  • 16.4k
7 votes
Accepted

Connecting 6 gauge aluminum wiring to 10 gauge copper with AlumiConn

Use a mechanical lug connector ("Polaris" or equivalent) AlumiConns are only rated for a maximum of 10AWG wire. For fatter work, you'll want their bigger brothers, mechanical lug connectors (...
ThreePhaseEel's user avatar
7 votes

pigtailed wires downstream of a gfci

If I understand your question correctly, the answer is it is irrelevant how you connect the standard receptacles past the GFCI one. What determines whether they are GFCI protected is how you connect ...
Jim Stewart's user avatar
6 votes
Accepted

Are splices made with insulated cable connectors required to be inside a junction box?

You'll need a box, and a pretty chunky one at that Splicing wire this large is indeed done with insulated mechanical splice connectors like the one you linked -- you will need one per wire, and a ...
ThreePhaseEel's user avatar
6 votes

Live wire spliced in a switch to provide power to other parts of the room!

Your analysis of the current situation is correct and quite normal. The fact that this type of switch allows two wires to be attached under the switch makes it that much easier to do, as opposed to ...
DoxyLover's user avatar
  • 12.7k
6 votes

Can you use Wago lever connectors with feruled wires?

If you're talking about the Wago 221 with levers, the manufacturer's instructions and datasheet say no ferrules are necessary. There doesn't seem to be any pros or cons to using ferrules. I sure ...
bobflux's user avatar
  • 10.1k
6 votes

What's the proper way to extend wiring into a replacement panelboard?

This is a tiny 8-space box. Simple solution. Don't replace it with another 8-space (or even 12-space) box. Put in a much bigger panel. 20-space or 24-space would be quite reasonable. It can even have ...
manassehkatz-Moving 2 Codidact's user avatar
6 votes

What's the proper way to extend wiring into a replacement panelboard?

I completely agree with manassehkatz about getting a Nice Big Panel. We have a 24-space in our shop fed by #6 THHN wire (65A, smaller than your 85A) which more than half full and we haven't even ...
Harper - Reinstate Monica's user avatar
5 votes
Accepted

Is it OK to splice NM and NM-B cable?

You can splice diferent sizes, temperatures or types (NM, UF, THHN, SJOOW) cable anywhere it's legal to splice cable. It needs to be inside a junction box. The boxes need to be someplaces boxes ...
Harper - Reinstate Monica's user avatar
5 votes

Splicing 8 gauge wire to a 6 gauge?

Actually, that ground wire likely is smaller, but it is perfectly OK. While in an emergency the ground wire may need to carry the full load of the circuit (or more - when that happens it is often a ...
manassehkatz-Moving 2 Codidact's user avatar
5 votes

Can you use Wago lever connectors with feruled wires?

The instructions say strip and insert wires. Ferrules are not called out. If not following the manufacturer’s instructions you are not using them in a listed way.
Jon Custer's user avatar
5 votes
Accepted

Seeking ideas on how best to splice+move breakers from one panel to adjacent panel

Your panels also count as large junction boxes. What I would do there is run a short run of EMT or RMC between the two panels. The panels appear to be the same brand and size so it is likely the ...
Chris O's user avatar
  • 6,795
5 votes

Can I splice an existing wire in a wall where I want to put an outlet?

In rare instances like this, I have added two junction boxes about 14 inches apart and two outlets instead of the one I needed. I cut the existing wire so there was enough wire going into each box and ...
JACK's user avatar
  • 82.1k
4 votes

Are splices made with insulated cable connectors required to be inside a junction box?

Yes, it must be in a junction box. There are splice connectors available for installation in a space where a junction box is not possible, but those splice connectors are explicitly rated for such a ...
longneck's user avatar
  • 21.3k
4 votes

How to replace AC/DC adapter but keep old connector

Chop and solder. Of course, if the current adapter is dead, it can be difficult to establish correct polarity - but I think I see that labeled nicely on the present adapter (it's not always, though it ...
Ecnerwal's user avatar
  • 220k
4 votes

Connecting 6 gauge aluminum wiring to 10 gauge copper with AlumiConn

Splitting #6 strands to fit on two #10 lugs No, it's illegal to split wires like that. Aside from failing on 110.12 "neat and workmanlike", it is also paralleling (not allowed without special ...
Harper - Reinstate Monica's user avatar
4 votes

In wall splice for 4 wire cable

You can't, but no need. If you're referring to the Tyco Electronics Romex splice kits, yes, they make those for 3-wire w/ground as well as 2-wire w/ ground. If you mean some other splice method, ...
Harper - Reinstate Monica's user avatar
4 votes

Splicing 8 gauge wire to a 6 gauge?

Two probable issues here, NEC and Listing (UL/CSA/ETL/other). If the Instructions (which are part of the Listing) for the tub specify #6 or #8 sized copper ground then most versions of NM won't be ...
NoSparksPlease's user avatar
4 votes
Accepted

Can I extend 22 gauge stranded wire with 18?

Yes, that's perfectly fine. A comparable situation with 120V wiring is where a 15A circuit has 14 AWG wiring and is extended using 12 AWG wiring. Larger is always fine. In some cases, this is done ...
manassehkatz-Moving 2 Codidact's user avatar
3 votes

Connecting 6 gauge aluminum wiring to 10 gauge copper with AlumiConn

This was my solution to a very similar issue. I used a Square D 30 Amp Safety Disconnect Switch. The cost factor was about the same as purple twist on things that may or may not catch fire or Polaris ...
Robert King's user avatar
3 votes

What is the best way to handle house wiring cables with short sheathing?

I would get some white heat shrink slide it over the conductors and make sure it extends inside the box the 1/4” and at least it’s width past where the sheath was removed. I have skinned the outer ...
Ed Beal's user avatar
  • 103k
3 votes
Accepted

Splice to repair damaged 100A aluminum feeder

You'll need a pretty chunky box for those splices Wires 4AWG and up can't be spliced in any old junction box as they're simply too stiff and fat to fit into junction-box-sized boxes. Instead, you ...
ThreePhaseEel's user avatar