32 votes
Accepted

What could be causing changes to a smart bulb to affect a regular bulb on the same circuit?

You're looking at the problem upside down. You are thinking the smart bulbs are causing it. Actually, the Lutron Caseta dimmer is causing it. The smart bulbs are behaving normally, however their ...
user avatar
20 votes

Can a 12 gauge wire be clamped onto a light switch using the side screw?

Using the hole(s) in the back is called a "back stab", and, while technically code-legal, they're frowned upon because they can come loose and cause arcing and, if left alone long enough, ...
user avatar
  • 29.4k
19 votes
Accepted

How can I install an on/off indicator for a lighting circuit?

It sounds like you have light bulbs or fixtures directly controlled by Alexa/Google Home. A better solution, though sometimes a bit more work to install, is a smart switch. With a smart switch, the ...
user avatar
10 votes
Accepted

Odd wiring setup in light switch

Someone ran out of white wire It appears the previous installers ran out of white wire to use for running neutrals, so they grabbed the spool of green wire off the back of the truck to keep the job ...
user avatar
10 votes

Can a 12 gauge wire be clamped onto a light switch using the side screw?

Yes, I see several problems. Wire just stuck under a screw, and not using a proper shepherd's hook with a more than 180 degree bend (i.e. squeezing it together after forming it. Watch a Youtube ...
user avatar
9 votes
Accepted

Can I connect the neutral wire ends via a single switch terminal (without a pigtail)?

"Never" is a bit strong. This is not a plain "screw terminal" where that would be true. This is a "screw and clamp" and appears to be designed to correctly hold 2 wires, ...
user avatar
  • 133k
9 votes

Running neutral wire between two circuits

The reason this trips the breaker isn't really relevant, since you're not allowed to do this thing. You can't steal neutrals from other boxes NEC 300.3 all related wires must be together in the same ...
user avatar
9 votes

When installing a smart switch, can I pigtail off of the neutral from the existent outlet in the same box on the same circuit?

Yes, that's the correct neutral. Hot goes to inside receptacle and then to switch. Which means the receptacle controlled by the switch, and any smart switch itself, must use the same neutral as the ...
user avatar
9 votes

Why are there three sets of wires for two switches, and how to wire up the neutral?

To clarify a little, your setup is one of two common setups: (Ignoring ground - everything should have ground, all grounds always go together.) One incoming cable from the circuit breaker (may stop ...
user avatar
8 votes

Is there a way to remotely control gas valve?

Yes, there are electronically controlled gas valves. A better idea might be to install a "grill timer". It's like a kitchen timer that you twist to set the time, but instead of ringing a ...
user avatar
  • 18.8k
8 votes
Accepted

Alternatives to running a single Neutral wire?

My plan: I can get 10' of 14/3 (it's the cheapest thing by the foot that I can find available at my hardware store... I could get 12/3 for a little more Hold on there, you need to go find your ...
user avatar
7 votes
Accepted

Box too small for TP link Kasa smart switch

This is a common problem. I had a similar problem simply replacing a ~ 60-year-old 2-wire duplex receptacle with a new (but nothing fancy, not GFCI) 3-wire grounded duplex receptacle. The solution: A ...
user avatar
6 votes

Trying to install smart switches - came across something that looks wrong

The nut of the problem is the ground wire joining the neutrals in drawing 1. This is a bootlegged attempt to fix a fundamental problem of bringing 5 wires: 2 travelers, always-hot, neutral and ...
user avatar
6 votes

Why do these LED light bulbs flicker when my remote control has turned them off?

The remote you use to turn the light on and off is not compatible with LED bulbs. One reason people love LED bulbs is because they use so little power. Unfortunately, some devices in the past used ...
user avatar
  • 26.6k
6 votes

Odd wiring setup in light switch

As you know, "green = ground" and "white = neutral". As you probably also know, ground and neutral should only be connected in one place (main panel) and not in individual switches or other devices. ...
user avatar
6 votes

Live wire spliced in a switch to provide power to other parts of the room!

Your analysis of the current situation is correct and quite normal. The fact that this type of switch allows two wires to be attached under the switch makes it that much easier to do, as opposed to ...
user avatar
  • 7,852
6 votes

Running neutral wire between two circuits

You are NOT allowed to do that, for several reasons: If both circuits happen to be on the same leg/phase of your utility service, you can overload the neutral back to the panel by a factor of two, ...
user avatar
  • 2,776
6 votes
Accepted

Which Circuit Does this Switchbox Common Wire Belong To?

There is no such thing as "common" in AC mains wiring. Each circuit is wired in a full loop. If you do automotive wiring, you tend to think of the metal vehicle chassis as the "common&...
user avatar
6 votes
Accepted

Why are there three sets of wires for two switches, and how to wire up the neutral?

Note the updated diagram at the bottom with some additional labeling. Why are there only three black wires, and not four? I'd expect each switch to have two black wires, one load and one line. You ...
user avatar
  • 29.4k
5 votes
Accepted

Confused by wiring in box

It's simply a splice. They are using the screw and the backstab to accomplish what they could do with a pigtail. In particular, they are grabbing "always-hot" because this is the first switch. ...
user avatar
5 votes

Odd wiring setup in light switch

Mark that green wire white That green wire behaves at both ends like a neutral. I think it is one. I would get some white tape and spiral wrap it around that green wire, to mark it most of the ...
user avatar
5 votes

Do metal outlet boxes act as grounds?

Switches (only) can ground through the mounting screws No need to run a ground wire to the switch. Presuming the switch has a metal yoke, it will ground via the grounding screws to the metal box (...
user avatar
5 votes

How does a Smart Switch that does not require a neutral work?

Whoever you're listening to on this is spouting technobabble I'm sorry to say, but you probably should find a better source to read, as whoever's been feeding you information is spouting total ...
user avatar
5 votes
Accepted

Can I steal a neutral from another fixture on the same circuit?

So, given the comments, although electrically this would work, it is unsafe and a code violation. This is because the hot and neutral are to be in the same raceway to have the magnetic field of the ...
user avatar
  • 243
5 votes

How can I install an on/off indicator for a lighting circuit?

What you need is a combination of smart switch and smart bulb You are correct that smart bulbs allow local control of color. However you still need at-the-switch control of on/off, and that is because ...
user avatar
5 votes

Adding a smart switch to a box originally containing two single-pole switches

Legal colors in conduit wiring: ALWAYS-HOT: black, brown, red, orange, yellow, pink, blue, or purple SWITCHED-HOT: black, brown, red, orange, yellow, pink, blue, or purple There's a convention of ...
user avatar
5 votes
Accepted

Does this 3-Way Wiring Violate 300.3(b)?

No, you're actually fine on that front here The C-D conduit meets 300.3(B) despite not having a neutral in it for the same reason old-style switch loops were compliant with that rule: all the power is ...
user avatar
5 votes
Accepted

How do I search for a mixed smart-normal switch plate?

The large rectangular opening is called "Decora" There are only 3 popular shapes: Small slot: the traditional switch, like you have now. Two ovals: for traditional receptacles (also dual ...
user avatar
5 votes

Selecting smart plug

Two very important safety things to consider: Certification Electrical devices should, in general, be tested and certified by an independent laboratory. The two that come to mind, at least for the US, ...
user avatar
5 votes

Smart switch not working with correct setting

I see a whole bunch of white in the back. I suspect you pulled one white neutral at random from a bunch and connected that to the switch. All neutrals need to stay together - i.e., in one wire nut or ...
user avatar

Only top scored, non community-wiki answers of a minimum length are eligible