19 votes

How can I move an outlet from the back of an enclosed space to the front wall?

If moving the outlet forward makes the cable to it shorter, no problem. If you need to add cable, you either need to go back to the next junction box and fish a new cable, or you need to make the ...
Ecnerwal's user avatar
  • 201k
7 votes

Electrical Code Compliance Question

There are two definite issues, some possible additional issues: Grounding The only place ungrounded receptacles are allowed is if they are original equipment installed when a building was built (or ...
manassehkatz-Moving 2 Codidact's user avatar
7 votes

Melted electrical outlet

It is safe, as long as there is a cover (or the old outlet) covering the wires (even though they are taped up). I personally hate tape and would use a connector block to isolate the different wires. ...
Rohit Gupta's user avatar
  • 5,090
5 votes

Melted electrical outlet

It's safe - as long as you only have adults in your household, that can be told not to touch the wires. If you have a youngster, it's dangerous as it allows tool-free access to live wires... A better ...
vidarlo's user avatar
  • 1,800
4 votes

Why can't I find a plug for inside a breaker box

North America answer. In an oversized equipment or control cabinet, if work is performed within the cabinet often enough to make this worthwhile, you can assemble an outlet in a junction box within it ...
jay613's user avatar
  • 34.3k
4 votes

Splitting Standard Outlet with 2 different hot wires (light switch and normal) and shared neutral into 2 double outlets

First, it's a code violation to put a dimmer on a socket. The only way this is allowed is if the socket is uniquely designed to reject normal plugs, such as this Lutron line of special sockets and ...
Harper - Reinstate Monica's user avatar
3 votes
Accepted

Outlet no ground but upsteam grounded

“Continuity” between the upstream hot and ground can’t be a short between the black wire and ground. If it were, the breaker would trip and you’d have no power! This probably means that you have a ...
DoxyLover's user avatar
  • 12.6k
3 votes

Electrical Code Compliance Question

To answer your questions: It is not grounded (you can see the ground wire cut off and not connected to the outlet). It is not code compliant for multiple reasons (not in a junction box, not grounded, ...
Milwrdfan's user avatar
  • 3,773
2 votes

New GFCI Tamper Resistant Outlet not working

Basic trouble-shooting for GFCI/receptacle: Disconnect all wires. Determine which wires are incoming/line. Connect hot and neutral from that set (wires or cable) to the incoming/line side of the GFCI....
manassehkatz-Moving 2 Codidact's user avatar
2 votes
Accepted

How do I add a always on duplex receptacle under sink on same circuit as switched garbage disposal

This could be anywhere from super-easy to moderately hard to impossible. There are two key issues in being able to tap into the existing circuit: Existing Load If a circuit has hardwired equipment ...
manassehkatz-Moving 2 Codidact's user avatar
2 votes

Why can't I find a plug for inside a breaker box

If your breaker panel uses a DIN rail system (common in Europe) then you can easily find outlet that will fit on there. In the american-style busbar design the convenience outlet is usually put in ...
ratchet freak's user avatar
2 votes

Options for using this electrical box to add new outlet above

Alternately, if you can't work the angle for drilling a hole per Robert Chapin's answer—since the box appears to be fairly deep—the box can simply be replaced. You should be able to use a sawzall or ...
Huesmann's user avatar
  • 2,707
1 vote

Options for using this electrical box to add new outlet above

This is a Bakelite box. You can drill through the top or bottom near the back and feed cable through the holes you make there. See How can I bring cable into a junction box with no knockouts?
Robert Chapin's user avatar
1 vote

Is it ok to replace all 2-prong receptacles with GFCI ones without identifying head of circuit?

The other answers cover the basic requirements, so I'll get to a requirement not mentioned. To comply with the National Electrical Code (NEC), replacing a receptacle requires Arc-Fault Circuit-...
Nigel Redmon's user avatar