1

Your pool subpanel mounts on the side of the garage, so it doesn't have any underground runs. There's disagreement as to whether NM cable is allowed to "stick its nose outside" to service a panel mounted on an exterior surface; but no question of either UF stapled, or THHN/THWN-2 dual-rated wires in conduit. Wires from the subpanel toward the pool need ...


1

All of your questions you have the correct answers, thhn is dual rated thwn so it can be used in conduit both inside and outside as required. You do need an insulated ground. You can put in a 100 amp panel at the pool and feed it with a 30 amp breaker or the size you want . the 1.5 hp 240 v motor is rated at 6 amps + 25% (motors require 125% of the FLA ...