Is it safe to use the ground wire in /2 as neutral (with no ground)?

Absolutely not. Completely illegal. You need a ground WIRE even if your buddy doesn't know that. A lot of people are stuck in 1966 (1996 for dryers; 2008 for outbuilding feeders) and think neutral ...
Harper - Reinstate Monica's user avatar
8 votes

Is it safe to use the ground wire in /2 as neutral (with no ground)?

UNSAFE!!! There are three problems: Bare Neutral There are certain situations, including feeder to the meter and from the meter to the main panel, and some grandfathered-without-ground branch ...
manassehkatz-Moving 2 Codidact's user avatar
5 votes

Dishwasher and disposal wiring on seperate circuits to one yoke and common neutral

This is a mess What you have here is the result of someone who doesn't care about the "no loops" rules in NEC 300.3(B) and 310.10(H). If you feel comfortable replacing both runs of 12/3 and ...
ThreePhaseEel's user avatar
4 votes

Dishwasher and disposal wiring on seperate circuits to one yoke and common neutral

Yeah, pull one of the two circuits off that to a new separate box (because it simplifies or enhances the safety of maintenance, even if it's not STRICTLY required to handle-tie two circuits in one box ...
Ecnerwal's user avatar
  • 174k
4 votes

Is it safe to use the ground wire in /2 as neutral (with no ground)?

simple answer: UNSAFE AND ILLEGAL Your neighbor is wrong when he says that it is unsafe to use just one half of a two pole breaker. If either side of the breaker detects an over-current situation, ...
ddemic's user avatar
  • 41
3 votes

Is it safe to use the ground wire in /2 as neutral (with no ground)?

My neighbor said that only using one pole of a double pole is dangerous. No There should be a metal tie between the breaker handles. If one side trips, both flip. That's by design. The downsides of ...
Machavity's user avatar
  • 23.2k

Only top scored, non community-wiki answers of a minimum length are eligible