Skip to main content
17 votes

Can I use a hose clamp to ground a wire to EMT?

There's the Code answer, and the practical one: Start from NEC 110.2: The conductors and equipment required or permitted by this Code shall be acceptable only if approved. Approved means listed and ...
KMJ's user avatar
  • 11.8k
10 votes
Accepted

Can I use a hose clamp to ground a wire to EMT?

To give a bit on insight, electrical connections are degraded by oxidation of the conductors. If two bare metal conductors have a good, low-resistance connection at first, the resistance between the ...
JS.'s user avatar
  • 548
10 votes
Accepted

not sure why this ground wire keeps tripping the breaker

This diagram makes no sense as drawn. It is not clear how much of that is limitations in the drawing software vs. misunderstanding how 3-way switches are wired. Among other problems, I see: screws not ...
manassehkatz-Moving 2 Codidact's user avatar
6 votes
Accepted

Why do electrical fixtures with multiple live/neutral terminals have only one earth terminal?

Ground must be kept connected. Removing one device/receptacle/light/switch from a circuit must not disconnect the ground path. With two screws you might have ground in and ground out. The next idiot ...
crip659's user avatar
  • 25.1k
5 votes
Accepted

Can I bond a ground wire to a junction box that is using metal conduit for ground

Not only can you, code requires it if the length of FMC is more than 6 feet. Those ground wires should be connected together and then connected to their junction boxes. you do not need to run a ground ...
JACK's user avatar
  • 81.8k
4 votes

Using a section of copper pipe as a stop gap for ground

No. This is a code violation. And you know it is a sketchy idea, which is why you are asking. "There is no chance any section of the pipe will ever be replaced with plastic." You don't ...
Questor's user avatar
  • 886
3 votes

Do I need to ground the junction box for a security light/camera?

Yes, ground the junction box. Connect the Romex ground to the box and pigtail it to the light/camera. Use a multimeter to ensure 120V between hot and ground, and 0V between neutral and ground.
AlexanderAnthony's user avatar
3 votes

Can I bond a ground wire to a junction box that is using metal conduit for ground

I'm trying to clean up a situation where there's originally rigid metal conduit and no ground wires from the panel. Metal conduit 101: There's nothing wrong with that. You're perfectly welcome to use ...
Harper - Reinstate Monica's user avatar
2 votes

Can I use a hose clamp to ground a wire to EMT?

Sheet metal style strap clamps are allowed in NEC. Just not for what you are doing. Communications grounds for TV or satellite or telephone can use a listed version per 250.70(B). A non-listed hose ...
cde's user avatar
  • 726
2 votes

not sure why this ground wire keeps tripping the breaker

Always connect ground FIRST Because when you don't, you create lies (a false narrative). It is impossible for ground to break a circuit - unless it's already broken. So the lie is "It breaks when ...
Harper - Reinstate Monica's user avatar
2 votes
Accepted

Is my light switch box grounded and how to use the ground wires properly

You've got a brown Bakelite, non metal, switch box that doesn't need to be grounded. The two cables coming into the box have bare copper grounds crimped together. The best way to connect a switch ...
JACK's user avatar
  • 81.8k
1 vote

Why do electrical fixtures with multiple live/neutral terminals have only one earth terminal?

Rule #1: Manufacturers never include anything extra The second set of hot and neutral screws is not for convenient daisy-chaining. Yes, they are commonly used that way, but that is not the reason they ...
manassehkatz-Moving 2 Codidact's user avatar