69 votes

Why don't electrical receptacles have more than one ground?

This is because removing a device isn't allowed to interrupt grounding connections Removing a wiring device from the circuit cannot break grounding connections, or else you are violating NEC 250.148(...
user avatar
62 votes
Accepted

Why is my garage grounded ONLY when it rains?

To me it sounds like the conduit was used as the grounding conductor, as allowed by code, and it rusted through, therefore it works when the ground is wet and you have a ground connection through the ...
user avatar
  • 95.5k
39 votes

I live in an older home without ground wiring. Is it safe to install 3-prong GFCI with only a hot and neutral?

Absolutely! There are a number of different functions that an ordinary ground wire performs. A GFCI, despite the "G", does not actually need a ground wire to function. In fact, a properly ...
user avatar
33 votes

Is it OK to create a third prong ground from a cold water pipe, for a 2-wire circuit?

When or is it NEC code compliant to upgrade a 2-wire circuit, by adding a third prong equipment ground from a nearby galvanized cold water pipe? Never! Article 250.118 of the National Electrical ...
user avatar
  • 19.3k
27 votes
Accepted

Buying a home with 2 prong outlets but the bathroom has 3 prong outets

Grounding is no longer red-alert essential Since there are other ways now to provide better protection. Particularly, GFCI protection is so good that you're allowed to fit 3-prong outlets as long as ...
user avatar
26 votes
Accepted

Why don't I have ground wiring on any of my outlets?

Your house is wired using the EMT conduit wiring method. Individual wires are carried inside metal conduit. The conduit is the ground path. Most commercial and industrial buildings look exactly ...
user avatar
26 votes
Accepted

What are these orange outlets directly attached to my breaker box?

That recep appears to be right next to your service panel, connected to the panel by a 1" conduit nipple. That makes it the "magic electrician's outlet". It's not required by Code. It's just a "...
user avatar
26 votes
Accepted

Is it safe to use the ground as a neutral when other grounds are available?

What could possibly go wrong? If the ground wire is bare copper, you massively increased the risk of a ground fault, which can kill somebody or burn the house down. If the ground wire has a smaller ...
user avatar
  • 593
24 votes

Why don't electrical receptacles have more than one ground?

I am glad you are finding it convenient that some devices allow themselves to also be used as splice blocks. However, that is prohibited for certain types of wires: Any and all ground wires ...
user avatar
23 votes
Accepted

Looking for some guidance on knob and tube

Thus far, I've replaced the first receptacle in most of the series of receptacles with an AFCI/GFCI because I'm so confused. Don't do electrical work in a building owned by someone else. To do that ...
user avatar
22 votes
Accepted

What purpose does a 3+1 outlet/circuit provide when the neutral bus is grounded?

Yeah, the root problem is, you see they are both tied together in the panel, but you don't know what that thing is... or you don't even realize that is a thing. Its name is the Neutral-Ground ...
user avatar
22 votes

What does it mean if the electric is out in a room, but the breaker is not tripped?

Those outlet testers can be horribly misleading, there are multiple different faults that could cause any particular combination of lights and the ones they print on them are often not the most likely ...
user avatar
  • 4,189
20 votes
Accepted

Safe way to remove paint from ground wire?

Just some sand paper will be fine. You don't want to use a chemical stripper as it may interact poorly with the copper.
user avatar
  • 18.8k
20 votes

Can ground attached to neutral fool a receptacle tester?

The tester can't tell the difference. One way to look at is that electrically, since neutral and ground are already bonded at one location (normally the main panel), the electrons don't know the ...
user avatar
20 votes

What are these orange outlets directly attached to my breaker box?

The orange colored outlets are installed for an isolated ground. They are electrically the same as regular outlets, except they're built better and the yoke of the outlet is not tied to the grounding ...
user avatar
  • 53.3k
20 votes

Why is my garage grounded ONLY when it rains?

An outbuilding needs two kinds of grounds Electricity wants to get back to source, not ground. Source is the supply transformer, or in the case of natural electricity (lightning, ESD), then yeah, it'...
user avatar
19 votes

Can I use green wire in a residential wall box?

Green wire is perfectly legit. If you are really lazy or in a hurry you can even get pre-cut pre-stripped green grounding pigtails ready to go. Ground is the only thing it can be used for, but "...
user avatar
  • 133k
18 votes
Accepted

Had ground rod connection added to my electric panel, should old ground to copper water pipe be disconnected?

No -- that bond wire could save your life! It is very important that all non-current-carrying metal, including the cold and hot water pipes, be bonded to the electrical system ground. This prevents ...
user avatar
18 votes
Accepted

Why am I getting shocked by a water heater?

Filipino electrical service is a morass. There is some Euro 230V single leg service, and there is some American style 120/240 split phase service. And if those services are wired to Euro or USA ...
user avatar
18 votes
Accepted

How to electrically ground a gas furnace connected with an armoured cable

Someone forgot a fitting Normally, armored cables (like yours) are brought into a box using a fitting designed to clamp the the cable armor, grounding it to the box and also providing a strain relief ...
user avatar
18 votes
Accepted

How did my ground and neutral become energized by a short in the buried main line?

I think the power guy's assessment was spot-on He said it appeared that the buried cable coming in from the street had degraded or been damaged and that the "hot must have nipped the neutral." ...
user avatar
  • 19.7k
17 votes
Accepted

What do I do with the ground wire in a smoke detector install?

That looks like a plastic box to me. If it is metal, code requires that the box be grounded. If all the external parts of the smoke detector are plastic then a ground is not required (the same is true ...
user avatar
  • 95.5k
15 votes

Buying a home with 2 prong outlets but the bathroom has 3 prong outets

There are a few possibilities: The bathroom outlets were changed to three-prong and the ground screws are unattached. This means they're not grounded and are potentially unsafe. New wiring (or ...
user avatar
  • 104k
15 votes

Is it safe to use the ground as a neutral when other grounds are available?

You have ground being used as neutral. That is a serious code violation and can cause a number of dangerous problems. In the old days, the only real solution would be to run a new cable. Fortunately, ...
user avatar
14 votes

Dryer Outlet - 4 prong to 3 prong

Switch the cord, not the socket You have a proper NEMA 14-30 dryer receptacle with a ground wire, which is good. However, your "new" (old) dryer has a 3 prong (NEMA 10-30) cord. This can be ...
user avatar
14 votes

Why don't electrical receptacles have more than one ground?

In addition to what @ThreePhaseEel said, the purpose of having two screws on each side is not so that receptacles can be wired in series. While that is allowed, the purpose is for "split receptacle" ...
user avatar
14 votes
Accepted

No ground wire or GFCI for a dishwasher

That metal cladding is a valid ground path, provided it is connected properly to a metal box with either a ground wire from the breaker panel connected to the metal box or the metal box connecting to ...
user avatar
14 votes

Is it wrong to run ground wires all the way through conduit to each junction box?

Yeah, what you did was "belt and suspenders". Doesn't hurt, doesn't help much. Feel free to do that anytime you want. I tend to do it when I am concerned with physical damage to the EMT, e....
user avatar
13 votes

I live in an older home without ground wiring. Is it safe to install 3-prong GFCI with only a hot and neutral?

Safety In terms of safety, GFCI is all you need. The ruling factor for safety is that the GFCI will shut off if more than 5ma leaks (e.g. via a human being shocked). That is better human protection ...
user avatar
13 votes

Alternative GFCI Wiring in Strict 240V Scenario?

Put the GFCI breaker at the supply panel. Done & dusted! Now, I think it’s very prudent (and generally mandated) to have a local disconnect with a GFCI breaker... Not quite right. There is no ...