Skip to main content

New answers tagged

0 votes

Light switch and electrical socket placement from sink

Here are the main NEC rules for locating outlets near a kitchen countertop sink: 210.52(C)(1) Wall Spaces. Receptacle outlets shall be installed so that no point along the wall line is more than 600 ...
Robert Chapin's user avatar
2 votes
Accepted

Power consumption of GFCI+CAFCI combo breaker (Siemens Q115DFN)

I meanwhile did my own thorough measurements. Results are shocking and disappointing. Siemens Q120DFN 20A breaker: 229mW (turned on, no load) Bryant BRN120A1CS 20A breaker: 906mW (turned on, no load)....
divB's user avatar
  • 1,531
7 votes
Accepted

Melted GFCI receptacle

Most likely a poor connection - connection not properly torqued (to a measured value, with a calibrated tool, neither too loose nor too tight - some folks think "properly torqued" means as ...
Ecnerwal's user avatar
  • 221k
5 votes

How can I protect an unprotected hot tub outlet?

If you can get cabling from the panel to underneath the tub without breaking any walls do that. It doesn't matter if it's hard wired or if you put a receptacle under there. Either way it will be GF ...
jay613's user avatar
  • 41.7k
1 vote

Adding outlets to a room via daisy chain using wiremold raceway

Wiremold raceway is expensive and as noted you are not allowed to install it in a rental even if the landlord agrees. If the goal is to avoid messy extension cords, consider a solution that plugs in ...
jay613's user avatar
  • 41.7k
6 votes

Adding outlets to a room via daisy chain using wiremold raceway

Since this is a rental, it is highly unlikely that either you or the landlord can do this work. (assuming USA's typical jurisdictions) If this were your house and you were allowed to do this work ...
Triplefault's user avatar
  • 8,458
4 votes
Accepted

Does under sink outlet need to be GFCI?

Yes, GFCI is required under a sink where you can measure less than 6 ft from the top inside edge of the bowl to the receptacle. This requirement was added in 2011 NEC 210.8. There was a loophole for ...
Robert Chapin's user avatar
2 votes
Accepted

Why is my GFCI tripping when I turn the breaker on?

Only 2 clear ways to go about troubleshooting now. Some devices have a very stiff reset button. Make sure it's bottomed out, even if you need to use a hand tool to mash it in there. We haven't seen ...
Robert Chapin's user avatar
1 vote

Why is my GFCI tripping when I turn the breaker on?

Did you read the instructions that came with the receptacles? Tripping on first power-up (as a mandatory self-test) is normal behavior for many GFCI receptacles. If it stays reset after you press the ...
nobody's user avatar
  • 6,779
5 votes
Accepted

Dust Collector Fries GFCIs

I'd check the bearings - a fan (a dust collector is basically a big one, at its heart) really should not be that hard to start. It should have very low power requirements until it spins up, so hard ...
Ecnerwal's user avatar
  • 221k
-1 votes

Using smart switch to control GFCI outlet

I had the same problem after installing a smart switch to control a GFCI outlet for deck lighting. I discovered the problem of the outlet’s GFCI tripping when activating the switch was solved by ...
Ken B.'s user avatar
  • 9
3 votes

Diagnosing tripped breaker on the dishwasher circuit?

When the breaker is flipped back on, the arc fault indicator is illuminated. Arc faults frequently turn into fire hazards. Somewhere, you have electricity jumping between two conductors that should ...
bta's user avatar
  • 2,039
0 votes

Diagnosing tripped breaker on the dishwasher circuit?

It's possible that it's not the dishwasher itself that's causing the issue. Since the dishwasher doesn't have a dedicated circuit, your dishwasher may be running when another appliance or countertop ...
computercarguy's user avatar
6 votes

Diagnosing tripped breaker on the dishwasher circuit?

As Jansen said in the comments, it seems much more likely that the breaker is telling you the dishwasher is unsafe and needs repair, than that the breaker has gone bad. Especially since the GFCI was ...
keshlam's user avatar
  • 30.8k
6 votes

Level 1 car charger causing outlets and lines to break

Vehicle charging puts a fair amount of stress on circuits. Properly installed that should not be a problem, but if there are screws that were not torqued down properly or wirenuts that are not twisted ...
Ecnerwal's user avatar
  • 221k
0 votes

Does big current draw make GFCI outlets go bad?

I have killed GFCIs by plugging motors (e.g. chop saw, compressor) into them and using them. I rather suspect that the combination of a heavy inductive load, especially when starting, and on/off ...
Technophile's user avatar
3 votes
Accepted

Hot Ground Reversed when Upstream GFCI Trips

Ultimately this came down to a Bad GFCI outlet. When I nicked the neutral screwing in the outlet it tripped the GFCI and ultimately damaged the GFCI outlet. The GFCI outlet worked when it was not ...
DVS's user avatar
  • 151

Top 50 recent answers are included