5 votes

How do I keep a GFCI outlet with tight clearance from shorting inside a steel electrical box?

Why bother using boxes at all? Reasons. When you get down to the reasons we use junction boxes, metal is better at every single one of them. All that to say, don't let this deter you or make you ...
user avatar
5 votes

My GFCI red light is on and it won't reset

Sounds like you killed it with water, or you've created a persistent ground fault that's triggering it with water. I would guess that repeated wetting has just finally killed the GFCI itself. This is ...
user avatar
  • 132k
5 votes

Does NEC require a refrigerator outlet within six feet of a sink to be protected by GFCI?

I would say that 210.8(A)(6) pre-empts 210.8(A)(7), since as a general rule, specific overrides general. E.G. air conditioner rules override motor rules. However, you can tiebreak that with your AHJ (...
user avatar
5 votes

Is there any issue with wiring a GFCI to a switch?

Use a switch-rated deadfront GFCI I'd replace the existing garbage disposal switch with a switching-rated deadfront GFCI device, such as the Legrand 2087 depicted below. That way, it's clearly ...
user avatar
4 votes

My GFCI red light is on and it won't reset

Turn the power off, pull the GFCI receptacle out. remove any wires off of its "Load" terminals, and cap them off. Put the GFCI back in the box, power back up and hit "Reset". If ...
user avatar
4 votes

Safe breakout for an RV outlet

You can get "a solution in a can". It is called an "RV subpanel" and it replaces the 30A socket. It contains a 30A breaker for a TT30 socket, as well as a 15A or 20A breaker to ...
user avatar
3 votes
Accepted

Safe breakout for an RV outlet

You need a portable subpanel, or "power distribution box" though this one will be unusual (most of those "off-the shelf" are designed for NEMA14-class 4-wire input. There might be ...
user avatar
  • 132k
3 votes

Does any manufacturer make a fused 240 V 60 A steel AC disconnect with GFCI receptacle?

Typically, the mandatory A/C service receptacle is fed from a different and unrelated circuit. Usually this is an "outdoor outlet" circuit that is already there, and already has GFCI ...
user avatar
2 votes

Debugging nuisance trips on 2-pole GFCI breaker

I found the actual problem, and I'm extrapolating here to what I think is one good general answer to this question. Don't do what I did here: Don't assume a GFCI trip is a "nuisance" one ...
user avatar
  • 16.9k
2 votes
Accepted

Why are my Outdoor Outlets not GFCI?

Why don't I have GFCI on my outside receptacles? You've answered your own question: the code changed since then. The code has changed since 1992. GFCI wasn't required anywhere back then and, in '92 ...
user avatar
  • 29k
2 votes

GFCI Test Trips Arc Fault Breaker

The common assumptions is that all GFCIs are receptacles. If an outlet needs to be GFCI protected, and you don't see a funny receptacle with a Test and Reset button, therefore somebody messed up. ...
user avatar
1 vote

Does NEC require a refrigerator outlet within six feet of a sink to be protected by GFCI?

Okay, I will answer my own question in the hopes it might help someone else. YES, all outlets within six feet of a sink must be GFCI see https://www.nfpa.org/codes-and-standards/all-codes-and-...
user avatar
1 vote

Why are my Outdoor Outlets not GFCI?

From an NEC standpoint: 406.4(D)(3) Ground-Fault Circuit-Interrupter Protection. Ground-Fault Circuit-Interrupter protected receptacles shall be provided where replacements are made at receptacle ...