Hot answers tagged

48

I always wonder “what else is wrong” when there are so many obvious errors. You’ve noted the obvious problems, but you’ve probably missed some major items that are not so obvious: In Picture #1 you’ve noted the gap issue, but missed the “double spliced sole plate”. (Splices are to be a minimum of 4’ apart, unless at intersection of a wall.) In Picture #1 ...


43

Leave a gap and use a cornice(crown) molding to cover it.


36

This gives all the impression that is was designed and installed to support the basement wall that the "arrow" of the diagonal bracing points to. The vertical post against that wall is what was put there to support that wall. The bottom of that post is most certainly held up against the wall securely by the bottom plate in that wall which is likely ...


28

As long as they are normal screws and you unscrew them they won't compromise the studs or their integrity. If you rip the screws out (with a hammer for example) that could compromise the studs. If you plan on reusing the exact same holes there are things you can do to help future screws grip just as well by adding toothpicks to the holes, but otherwise you ...


25

Yes, you can remove the brace because: The wall is non-load bearing (not carrying a load) The diagonal brace is not secured in a manner to transfer any load at the top or bottom The diagonal brace is not secured to top plate The diagonal brace is not secured significantly to vertical stud...the picture cuts off a portion of the brace that crosses the stud ...


23

No, it's not ok. For one thing, by the time the city inspector looks at the fully framed building, it will be a little too late to fix it. Secondly, the builder's attitude seems very questionable. Either his framing crew or the concrete sub messed up. At the very least their job is not done in a workmanlike manner. They shouldn't wait and hope things 'slip' ...


23

It's probably a good time to review the contract you entered with the framers. Does it allow you to withhold payment until defects are resolved? Does it stipulate how claimed defects are to be resolved? Do what the contract requires of you to ensure that you don't end up in breach too. There appears to be a pattern of careless work and failure to abide the ...


23

Those are called "finger jointed studs". These joints are weaker than regular 2x4 or 2x6. I do a lot of woodworking and when gluing boards together (for like a table top) the glue joints are actually stronger than the wood itself. But for some reason, that's not the case with finger jointed studs, they are just much weaker than the intact 2x. ...


22

If this is a load-bearing wall you'll want to frame the pet door in, just like you would a window. This will allow you to properly carry the load down, and around the pet door. The king studs should go all the way from the top plate, down to the bottom plate. The header will be made up of 1/2" plywood/OSB, sandwiched between two 2x4s. If you don't want to ...


22

Many community colleges offer construction trade courses. Have a chat with the instructor, he can often offer enthusiastic young students who are ready and willing to provide some sweat as an on-the-job learning opportunity. The students get class credit, the only cost to you is to buy them lunch and provide water, no insurance/license, etc. required ...


22

I think your husband just wants the shoe bins to remain where they are and doesn't want to buy new ones.. LOL. Removing the screws will not damage the studs even if they were load bearing. Patch the holes with a vinyl spackle, sand lightly and you're good to go.


18

That joist is carrying something, even if it the weight of the material that make up that part of the house. I would say it is more than that since the new 2X with the framing anchor is attached to it, is telling me it is passing the load from the new 2X onto the one you wish to drill. Now onto drilling dimensional lumber. Code only allows you to drill a ...


16

If you're in the US, and you want to work within the bounds of the law, contact a 'construction temp agency'. They'll have insurance and workers comp. They might seem expensive on an hourly basis, but probably worth the peace of mind.


16

That wall is load bearing; it is helping to support the stairs and that landing. As such, it can be subjected to significant load (think two 250 lb guys, plus heavy furniture, for starters). More importantly, it is subject to lateral impulses from people and things going up and down the stairs so it should have lateral/diagonal bracing to help stop "...


16

Yes, that is shoddy work! Did you pay for shoddy work or did you pay for quality work? But things like this turn into squeaks, cracks, wobbles, etc. over time. So yes, if this was MY project I would get them back in to do it properly!


16

Horrible work. I don't think "I commissioned an independent review" will hold any weight with the contractor, unless the contract allowed for that. The contractor might dispute the qualifications of your reviewer. Instead, I would contact the local city planning office (who gave you the planning permission), and ask them for an inspection. If they say that ...


15

Normally rough opening is 2 inches larger then the nominal door size. This leaves approximately 1/4" on each side for shimming to plumb. Some carpenters prefer 2-1/2", leaving a 1/2" gap for shimming. In case framing isn't very precise (say when using unskilled volunteer labor), 1/4" can sometimes be inadequate.


14

If it is not too large of wall I would recommend removing all the old drywall and its fasteners. Then I would shim out the studs with extension strips that even out the wall with the top plate. You may find that not all of these shims are uniform in dimension of any of the studs are bowed or out of plumb. The shims are easily ripped from a 2x4 or 2x6 using ...


14

Studs are cut to length at the mill so you can build your 8’ walls without cutting the ends off the top and bottom plates with studs make a quick tilt up wall, the rest is true 8’ 10’ 12’ . Note if remodeling verify length prior to building a wall.


14

As J comments, this is not a joist, it is a beam on which the joists are hung. Likely there used to be a load-bearing wall there that a prior owner had removed to enlarge the space. They could have opted to have the beam under the joists, which would have allowed space above it but would have reduced ceiling height. Instead they opted (surely at higher cost) ...


13

Good on you for leveling up your knowledge and learning where not to drill or saw on joists. On that same note, here's an excellent summary from BuildingAdvisor titled Guide to Notching and Boring Joists: Don’t make any holes with a diameter greater than 1/3 the depth of a joist. No holes closer than 2 inches to the top or bottom edge. No holes closer than ...


12

OK this is easy. The answer is NO. The construction has issues: There are no bolts for the sill plates. 2.The sill plates should be spaced on the slab so that wall plus exterior finish meets slab. It looks like this house is getting brick or thick stone given the 3 inches or so from the edge. I am not sure about your situation. You are having a ...


12

International Residential Code 2012 Chapter 6 Wall Construction Section R602 Wood Wall Framing R602.7 Headers. For header spans see Tables R502.5(1) and R502.5(2). So if you're on the top floor, you can use 2 2x4's (unless the building is 36' wide, in which case you'll need 2 2x6's). If you have a floor above, you'll need 2 2x6's (unless the building is 36' ...


11

The brace is providing lateral support. If you build a wall with the top and bottom plate plus some studs, it's easy to shift the wall out of square and turn it into a parallelogram. Under load, a house would take an 8' shift to one side and flatten to the ground. With the brace, the wall remains square and holds perpendicular walls plumb. In typical ...


11

You could use one of the many variations of the mortise and tenon joint, depending on the look you're going for. Though I agree with HerrBag, that the strength of a mortise and tenon joint should not rely on glue. Tusk Tenon This is a through tenon variation, where a wedge is used to lock the joint together. Fox tail (Wedged) Tenon This is another through ...


11

No, the wall between the home and garage is designed and built as an interior wall. HOWEVER, it is a fire wall. Your code in Oregon requires 1) fire rated door between the spaces, and 2) fire rated wall "assembly", and 3) insulation. 1) The door needs to be fire rated door and frame, which can be a solid core door and a solid wood frame (not a frame with ...


11

Clues that it is likely load bearing are the sheer size (two side by side planks, you don't do that without a reason) and the fact that it looks like it's supporting the studs. What is the span between walls if you follow its length? I don't think you can safely put a hole in that without reinforcing it, and you'd need an engineer to tell you how much ...


10

A bunch of ways to do this. What I would probably do myself, which is not what you are currently planning, is: Cut a piece of plywood, probably 3/4" thick, 24" tall by ~ 20" (studs 16" apart) or ~ 28" (studs 24" apart). Mount the plywood with 3 screws on each stud. Paint the plywood to match the wall. It doesn't have to be perfect because it will be mostly ...


10

Structural engineer and former carpenter and contractor here. Check your plan general notes for your code and other criteria to which your contractor's quality of work must meet. Discuss with your building official, or a local structural engineer for advice and direction. From what I see in your pictures after a very quick precursory review, it appears ...