Your gas dryer vents its combustion products outside along with the moisture from your clothes, so it is vented to the outside. Your oven doesn't vent out mostly for sake of having limited combustion. There are ventless heaters available. However you run it, though, any natural gas burning device will create water vapor and carbon dioxide. If it ...


23

The actual amount of combustion air - i.e., air flowing past the burner to provide oxygen and leave with less oxygen but more CO2 and possibly other combustion byproducts - is very little. The gap allows additional air to flow in and the combined air, if the ductwork is designed and installed properly, flows through the ductwork and out of the house. If you ...


13

There are a few things I can find in the NEC that may apply here. NEC Article 300.8 states that no raceway or cable tray can have elements of any other system besides electrical in it; no plumbing, no fuel gas, no ductwork. This implies that using the vent line itself, or any of its mounting hardware, to support the cable is a no-no; if the wire and the duct ...


12

manassehkatz covered a lot, but the simple answer is constant air flow The draft will change in the chimney as exhaust vents towards it – especially when going from cold air to hot. A draft hood is placed above the upper most part of the gas furnace to draw air into the chimney and makes it possible to draw more or less air through the chimney as ...


12

This is a draft diverter. If the heater was connected directly to the chimney, the hot flue gas would rise, creating draft in the heater. While that is a good thing, the amount of draft would depend on the particular chimney configuration in that installation, amongst other things. Excessive draft can cause problems, such as too much air being drawn ...


10

Before you do anything, you must figure out where it goes. It really has to vent outside. If it vents into the attic, you are going to have serious issues, including the potential of mold and rot as the hot, moist air is vented into an unconditioned space. It is (usually) against building codes to vent into the attic for this reason. If it is venting ...


10

What you show in the picture is known as a One-way Breather Vent (there are also two-way). Its intended purpose is to provide pressure equalization throughout the roof system and also provides ventilation for the insulation system. In some buildings that do not have a vapor barrier (even some that do), pressure changes inside the building can be forced ...


9

DO NOT DO IT!!!! Chimney vents must not be compromised! All heat and gas related stacks must be left intact. No additional venting or other holes may be put in them. As the comments have noted, you run the serious risk of carbon monoxide poisoning, as well as the risk of chimney and house fires. Find another route well away from the chimney.


8

I am a Local HVAC Tech in the Toronto area. As stated, this exhaust is not installed according to local codes and the manufacturers installation instructions. There is no surprise that you are getting freezing condensation on the brick of the house. The reason for having the vent terminate straight out and away from the building is to avoid this. The facing ...


8

This appears to be a simple misunderstanding of how a gas dryer works. The gas dryer creates heat by burning air and the gas together, then blowing the heated air and combustion mixture through the clothes and then out the dryer vent. In other words, the combustion gases are vented to the outside, per code, along with the moisture from the clothing. Since ...


8

You can install a reducer, but you'll cut your flow volume by an equal proportion: 28.3in2 - 7.1in2 = 21.2in2 (an area reduction of 75% when going from 6" to 3" duct) This will negate a significant amount of your fan upgrade, will make it work harder, and may shorten the motor's life due to reduced cooling. You might ask yourself whether you really need ...


6

The "best" approach is to take the shortest straight path to get the exhaust air out of your house. Generally that's via a roof vent. Check out this answer for a little more info. Your plan A, two bends and out the gable end is fine as an alternative. 10 feet is not a very long way for a bathroom exhaust vent. If possible, use a rigid vent to avoid ...


6

I would completely disagree with your builder. Since it is a new garage, I do see merit in the "build it in" approach. There are two important considerations: how many CFM do you need and what kind of noise level is tolerable? Are you using anything flammable? Water based paints should not be a problem but solvent based paints require special attention. ...


6

A vent at the soffit can be done, but so could venting directly into the attic, and both are poor choices. This is because soffits are used for air intake into your attic (and out a ridge or gable vent). If you vent too close to the soffit, the warm moist air that you're trying to get out of your home will get sucked back up the soffit and into the attic, ...


6

I think you just need to find a better built vent hood. The first one I found searching on HD specifically calls out this problem in the description: Unlike other versions that tend to rattle in the wind, the back draft damper on the ProMax cap has been designed for noise and wind resistance and its stylish wide mouth appearance helps to optimize the ...


6

I can't answer whether it complies with code or not since that depends on where you are, but I doubt it would matter. It's compressed some, but the volume is the same; it's just a different shape, and only slightly at that. Codes regarding airflow (and water flow) issues are mostly concerned with turns. A 90 degree angle will limit airflow whereas a larger ...


6

No. Your traps need to have water in them to prevent sewer gasses from getting into your home. If your vent "seal" was strong enough, you could "clear" the trap allowing gas into the home. Flammable, stinky, potentially deadly gas into the home. So no. Don't do it.


5

In the past I was a big fan of soffit vents. I figured if you used quality vents with a good back-draft damper, and sealed and insulated the duct well, it was a great way to vent bathrooms. There are several key benefits: First and foremost, it avoids penetrating either the roof or a gable wall, so it eliminates any risk of liquid water intrusion from ...


5

Well first, the outlet being at-grade is a no-no for those pest reasons. They don't have to get up the vertical pipe to cause problems; a mouse or bird can nest in there and cause problems. They did it anyway because it was easier to run it down through the crawl space then up to the ceiling (where, if this is your garage, they'd then have to build a sealed ...


5

There should be a vent cover on the outside of the house, at the end of the exhaust with a damper or louvers. Something like this The damper or louvers will be shut when the hood fan is off, preventing air from coming in or going out. If you don't have a vent cover like this, you should install one. If you already have one, you'll want to inspect it to ...


5

I'd recommend venting out the gable. Run a rigid vent from the gable wall to a point near your install, and use a 2' piece of flex duct to connect the fan to the rigid vent. The flex duct makes the bends easy (don't kink it) and allows the fan to be repaired from below in the future. For that length, I don't think you need to worry.


5

The exhaust pipe discharge is too close to the house. It should extend 8 to 12 inches from the wall if using tee on vent end. The exhaust might have been placed in its odd position because of a gas regulator vent. I see the pipe exits near the gas service. From a survey of high efficiency furnace installation manuals, and my own experience installing my ...


5

If possible, you want everything rigid: the connection from the dryer to the wall, the duct in the wall, and the duct in the attic. Sometimes rigid for the connection between the dryer and the wall is difficult to get right with a rigid duct so if you have to go with flexible duct then use the smallest piece practical. A secondary lint trap is probably not ...


5

You'll want to check with your local government. The sale of a house often requires some things to be brought up to current code. What things are required, depends on the local government. For example. In my area, sump pumps are required. If you're selling a house without a sump, you'll have to install one before you can close. A nearby area requires ...


5

If you have access to the attic; and presumably the top of the bathroom fan, you may be able to follow the duct. If you don't have access to the top side of the fan, you could remove the cover and take a peek inside. You should be able to get a glimpse of the outlet, which should allow you to determine if there's ducting attached. In my house, the ...


5

According to IRC, the duct must be made from galvanized steel, stainless steel or copper. It must have a smooth interior, and be air tight. Which means you're not going to want to use a flexible product for this application, especially that flexible plastic crap. Instead, you'll want to use rigid duct like this. And you'll want to make sure you seal all ...


5

Let's back up here for just a second and note something You almost certainly don't need a 150CFM fan. So your original fan was a stock 50CFM (probably NuTone or one of its predecessors) that's a 4-sone fan, meaning it sounds like it's been cleared for takeoff when you flip that switch. So you went out and bought this bad boy and though "I'll solve this ...


4

In general, yes an exhaust vent (or any vent) can turn corners. But there are many other factors to consider. Different vent materials or dimensions resist air differently. Different ways of turning corners resist air differently. The best place to start looking for info on this is the vent installation manual. It will talk about different ways to ...


4

It is possible that the previous dryer was a stacked unit with the dryer mounted above the washer.The general rule for dryer vents is not any longer than necessary.Two concerns I have are the flex hose if you can replace it with an elbow do that if not use metallic flex not the plastic type.The second concern is if you live in an area that sees snowfall ...


4

Duct Tape is good for a lot of things, except duct work! It will eventually dry up and pull away from the heat in the vent. I would bend/dent one of the ends slightly so that it will fit easily inside of the other. Then I'd secure it with proper HVAC foil tape, followed by a clamp around it. Foil Tape (source: homedepot.ca) Metal Gear Clamp (...