7 votes
Accepted

Melted GFCI receptacle

Most likely a poor connection - connection not properly torqued (to a measured value, with a calibrated tool, neither too loose nor too tight - some folks think "properly torqued" means as ...
Ecnerwal's user avatar
  • 221k
5 votes

Cost for grounding an entire house?

Cost estimates are off-topic as they vary tremendously by location, and of course go up over time as well. That being said, we can still offer some advice that may help. Grounding performs two ...
manassehkatz-Moving 2 Codidact's user avatar
4 votes

Why are there two cables connected to this GFCI outlet?

GFCI outlets have two sets of connectors: Line and Load. The Line terminals receive power from the breaker/fuse box. The Load terminals carry power onto other outlet(s). These “downstream” outlets are ...
DoxyLover's user avatar
  • 13k
4 votes

Outage in half of house

If in North America, one of your main hots is gone. Call your power company now to check the outside wires. Your system uses two hots and a neutral from the pole outside to the meter. Each hot/live ...
crip659's user avatar
  • 26.4k
4 votes

Amp Breaker is Tripping. Would the Amount Of Appliances Going do That? And is 30 Amps reasonable?

Yes, you could be exceeding the 30A limit for the apartment's master breaker. ACs generally draw the most power when starting up, so your average load may be acceptable but peak load may not be. Look ...
keshlam's user avatar
  • 31k
4 votes

How can I charge two EVs from a 16A fuse box?

Power Sharing Yes, there is technology for this, but you'll need to evolve past the flimsy charge cords. Tesla used to call it "Power Sharing" and now calls it "Group Power Management&...
Harper - Reinstate Monica's user avatar
4 votes

Adding circuits to service disconnect panel

It's normal and customary for the main (first) panel to have ground and neutral sharing the neutral bus, as the (one, singular) neutral-ground bond is there. If all other panels are wired as sub-...
Ecnerwal's user avatar
  • 221k
3 votes

How do I trace back a dead outlet?

There are professional versions of the circuit tracer that power the transmitter with a battery and do not require that the outlet be live. They appear on eBay fairly frequently. Not cheap, but when ...
keshlam's user avatar
  • 31k
3 votes

Is it OK to run electrical under floor joists in basement?

NO. It is not okay. Yes, it is against code. No, it is not allowed. NEC 334.15(C) restricts this type of run to cables not smaller than 8/3 or 6/2. 334.15 Exposed Work (C) In Unfinished Basements ...
Robert Chapin's user avatar
2 votes
Accepted

Did old knob and tube wiring tend to run hot and neutral wires separately?

K&T did route neutrals separately. If you have new NM cable being used the way you describe it is possible that someone made a repair to K&T using Romex cable, in a situation where the K&...
jay613's user avatar
  • 41.8k
2 votes

Did old knob and tube wiring tend to run hot and neutral wires separately?

The preferred option with old knob and tube wiring is to rip it all out and redo it according to modern standards. Those modern standard include keeping the return path of the current (the neutral to ...
ratchet freak's user avatar
2 votes

How should I run cable across a steel beam?

For a 14awg wiring you may consider running the connections that cross the beam using metal jacketed cabling that extends fully between junction boxes on each end. This type cable is often referred to ...
Michael Karas's user avatar
  • 65.3k
2 votes

Confirming correct wiring on replacement AC contactor

Yes ... The layout doesn't matter, so long as the new contactor fits, and can be mounted physically, so that the wires can reach their respective contacts. You must follow the documentation of the new ...
jay613's user avatar
  • 41.8k
2 votes
Accepted

Mounting an outdoor box, but there's an existing recessed box

Those boxes typically come with little mounting lugs (basically little metal straps with 2-3 holes) that you fasten with machine screws into holes that are tapped into the back of the box. You use ...
Huesmann's user avatar
  • 4,000
2 votes

How to relocate an outlet forward into a new wall?

Depending on the route of the wires behind/inside the wall you might be able to generate enough slack cable to move the socket forwards, by relocating it up/ down/ sideways. Obviously this also ...
nigel222's user avatar
  • 858
1 vote

How should I run cable across a steel beam?

Since running through existing joist holes, or even boring new ones, seems the best way to run cable parallel to the beam, it seems OP's question could be reduced to how to achieve perpendicular runs ...
AdamO's user avatar
  • 844
1 vote

How do I trace back a dead outlet?

Important: The non contact testers only work if you have power. Turn off the breaker, disconnect the wiring at the plug, otherwise you get false reading. Then use one of these tracers. They have ...
Traveler's user avatar
  • 18.1k
1 vote

Wiring a 240v GFCI Breaker for NEMA 6-20R

It's not an uncommon thing for a GFCI device to trip when first powered up. By design. The important question is what happens when you reset it. As already commented you need to mark the hot white ...
Ecnerwal's user avatar
  • 221k
1 vote

Amp Breaker is Tripping. Would the Amount Of Appliances Going do That? And is 30 Amps reasonable?

OK, so you have a 30A branch circuit breaker feeding 120V receptacles powering a number of A/C units, some quite hungry. You've already gone too far Normal 120V bedroom receptacles are placed on 15 ...
Harper - Reinstate Monica's user avatar
1 vote

Did I troubleshoot this 3-way socket correctly?

Between hot of the plug and the outer contact on the bottom of the socket: regardless of the position of the switch, always infinite. This image from Wikipedia by user:Icysubdweller, CC BY-SA 3.0, ...
manassehkatz-Moving 2 Codidact's user avatar
1 vote

Two 30 amp manual transfer switch with 50 amp inlet & 12500 KW generator

Can't do that. If you have 2 or more transfer switches, all but one must switch neutral. Those hinky, obsolete 6-8-10 circuit "transfer switches" don't even support neutral, let alone ...
Harper - Reinstate Monica's user avatar
1 vote

Should I plan for potential current capacity demands when sizing a circuit?

If you ever decide to install a small generator, ie any one that is not "whole house", you'll want to ration power to the sump pump and other moderate loads while ignoring small but critical ...
jay613's user avatar
  • 41.8k
1 vote

Should I plan for potential current capacity demands when sizing a circuit?

7 + 4 = 11 amps. This is never a problem on a 15 amp circuit. Sump pumps are not a continuous load in normal situations. If you treat the pump as a fastened motor for load calculation, it's still ...
Robert Chapin's user avatar
1 vote

Confirming correct wiring on replacement AC contactor

I would replace the old one and connect the wires to the new one in exactly the same pattern. Make sure your wire from the capacitor has the same continuity to the left side terminal you described in ...
ArchonOSX's user avatar
  • 20.2k
1 vote

How to relocate an outlet forward into a new wall?

Don't leave the old box buried inside a wall cavity. Remove the old box, then reroute the cable into a new box installed in the new wall. The question is whether your existing cable is long enough ...
bta's user avatar
  • 2,039
1 vote

How can I charge two EVs from a 16A fuse box?

My Volt and probably most EVs are able to be programmed for "time of use" charging" since some utilities charge more during the day. My utility charges about 50% more during the hours ...
ArchonOSX's user avatar
  • 20.2k
1 vote

How can I charge two EVs from a 16A fuse box?

Assuming 16 amperes (A) at 240 volts AC (VAC), the maximum charge rate would be ~4 kilowatt-hours (kW-h) per hour of charging, whether for one vehicle or split among two, e.g., each vehicle getting ~2 ...
DrMoishe Pippik's user avatar
1 vote

How to relocate an outlet forward into a new wall?

It depends if the new cable run is buried or not, which I can't tell from the description of the problem. In either case, you need to deprecate any receptacle that has no purpose or accessibility. (I ...
AdamO's user avatar
  • 844
1 vote

Cost for grounding an entire house?

FWIW I own a similar style home 1910 vintage, 2100 square feet, horse hair plaster and ornate woodwork. The wiring was a mix of everything used for the last hundred years (knob and tube, BX, Romex, ...
mikes's user avatar
  • 11.4k
1 vote

Does electrical wire need to run though floor joists or can it run above the side of foundation?

It is required to be protected. Conduit is one way to protect it, but hiding it in some kind of groove works too. So yes, if there is a recess between the top of the wall and the joists you can run ...
Jasen's user avatar