14 votes

Add service entrance barriers to live electric panel - tips?

Contact your power company. Say: "Am I correct that my smart meter has a large contactor in it, so that you can remotely shut off my power with a few keystrokes on your computer?" And "...
user avatar
8 votes

Add service entrance barriers to live electric panel - tips?

There's a couple of ways to play this, assuming you don't want to just YOLO this and shove them on with your bare hand (not the greatest idea) Ask your utility to kill the power to your house for a ...
user avatar
  • 19.7k
6 votes

Can neutrals be landed in an old panel which acts as a junction box?

Current flows in loops. It's not like air tools where air only has to go one way. Electric current has to come back too in a full loop. Neutral is the return path that carries 100% of the current - ...
user avatar
6 votes

Is it ok to use 14-3 wire to connect fan and recessed light

You can share neutral for devices that are all powered on the same cable. (after which can split off the live and tap the neutral in a 14-2 cable to power the new lamps So yes it's good. 14 gauge is ...
user avatar
  • 13.2k
5 votes

How to identify which live wire go with which neutral wire?

First, neutrals will generally be in the same conduit pipe as the partner live wire. To identify the neutrals, plug a load into each circuit and turn the load on. Lift all the neutrals off the ...
user avatar
3 votes

How to identify which live wire go with which neutral wire?

I'm relying on your statement that you know which wires are neutrals, but not how they are paired with lives and I will assume the neutrals on the new panel go to a common bus, so you can install them ...
user avatar
  • 16.8k
3 votes
Accepted

Understanding bad electrical panel wireing

That is not ok. The neutral wire from the second breaker ought to be blue. This is "just" a code violation, altough a severe one and an indication of shoddy workmanship and further issues. ...
user avatar
  • 330
3 votes
Accepted

Wire type from meter base to panel, conduit end to end, underground, and through a crawl space

I would go one size up in Aluminium, to 250 kcmil. 4/0 Aluminium is technically under the 200A at 75ºC in the ampacity chart. There may be a carve-out in the NEC for service feeders specifically but I'...
user avatar
  • 1,168
2 votes
Accepted

Must SEU cable between the meter and load center be in conduit?

The NEC would permit this, but Washington State code doesn't The Washington State electrical code amends NEC 230.43 to prohibit the use of SE cables for service conductors within buildings. Since you ...
user avatar
2 votes
Accepted

Different vintages breakers in main panel

Top left doesn't look like a Murray. It looks like a GE maybe -- and it's an A/C unit! Alien breakers are most common on A/C units because the contractors don't care and aren't electricians. As far ...
user avatar
2 votes
Accepted

Can I reuse an existing grounding rod and water pipe ground location?

Panel to first electrode needs to be uninterrupted, but from there you can use connectors Since the existing grounding electrode conductor is large enough and in good enough condition, you can go ...
user avatar
2 votes

Grounding electrode conductor

Go ahead and use a bare wire NEC 680.25 on feeders specifically calls out equipment grounding conductors, so you're fine using a bare copper grounding electrode conductor for your pool subpanel. Note ...
user avatar
2 votes

Does Square D make an extension lug kit for adding a sub panel?

A subfeed lug kit and the wires behind it must be protected by a breaker. Electrical equipment and wiring must be protected by a circuit breaker. A subfeed lug kit is Square D's name for the thing. It ...
user avatar
1 vote

How to identify which live wire go with which neutral wire?

1 - Finding the room behind every live wire To find which neutral goes to which live wire, I first found where each live wire went. To do so I just switch on every light. Then one by one I unpluged ...
user avatar
1 vote

Can i run a 30amp rv outlet with gfi outlet with 30 and 20 amp breakers in box off my main 100amp breakers

The 20A breaker opposite the main breaker cannot be moved or changed, however if it is powering a bog-standard 4500W water heater it needs to be changed to 25A. (siemens QP225). If it is a 3800W ...
user avatar
1 vote

Where is my neutral bar?

Notice the panel has a steel box (enclosure). Look closely at the construction of the bar(s) in question. If the bar is on insulated standoffs to isolate it from the chassis, then it is designed to ...
user avatar
1 vote
Accepted

Where is my neutral bar?

Your neutral is the large white wire going into the middle of the top bus bar. It appears that the three bus bars are all connected together and there are neutral wires going to each bar. There is ...