46 votes

Loss of power when I remove item from the outlet

Defective receptacle. Kill it with fire, before it kills you with fire. And if it has backstab connections (wires jabbed in back holes that auto-grab them) this is a good time to get rid of em. ...
Harper - Reinstate Monica's user avatar
29 votes

When to change Cutler-Hammer electrical panel and breakers?

Not in your lifetime. Nah, it's cool. Eaton has owned Cutler Hammer since 1978. Alien breakers require immediate attention! BRLAFGF115 and BRLAFGF120 are fine. This looks like a Cutler Hammer "BR" ...
Harper - Reinstate Monica's user avatar
26 votes
Accepted

Why does my waffle maker regularly trip AFCI?

While doing some more troubleshooting (repeated cycles on multiple circuits to verify how consistently the problem occurred) I noticed that it worked one time on a different circuit. I noticed that ...
jcoleman's user avatar
  • 597
24 votes
Accepted

Looking for some guidance on knob and tube

Thus far, I've replaced the first receptacle in most of the series of receptacles with an AFCI/GFCI because I'm so confused. Don't do electrical work in a building owned by someone else. To do that ...
Harper - Reinstate Monica's user avatar
20 votes

Bosch Drawer Microwave causes ARC Faults

Dealing with the problem now: One of the first things to try is just swapping the breaker with an identical one in the same panel. In my experience, there's a lot of individual variation in the exact ...
Peter Duniho's user avatar
  • 1,875
20 votes
Accepted

Square D Homeline AFCI breakers trip for all appliances

3 different units, you haven't used AFCIs before, and any appliance does it, but it does not trip when nothing's plugged in: Did you neglect to connect the circuit's Neutral wire to the matching ...
Ecnerwal's user avatar
  • 214k
19 votes

Loss of power when I remove item from the outlet

Chances are about 90% that you have a loose connection in the outlet. If I had to guess, I'd say it is a "stab-in" wire connection on the back of the outlet (as opposed to the wire attaching with a ...
JRaef's user avatar
  • 15k
19 votes

Is it possible to tell from labels if the breakers are AFCI / GFCI in the main panel?

First, none of you current breakers are GFCI or AFCI. If they were, they would have a "Test" button. Second, you will not be able to fit enough AFCI/GFCI breakers in your panel, even if the ...
DoxyLover's user avatar
  • 12.7k
15 votes

Square D Homeline AFCI breakers trip for all appliances

There are 2 huge problems with AFCIs that blindside people new to them (and GFCIs as well). Neutral to the breaker If you're new to AFCIs, circuit neutral needs to go to the breaker, NOT the neutral ...
Harper - Reinstate Monica's user avatar
14 votes
Accepted

Ground Fault Circuit Interrupter vs AFCI

What can happen... If you look closely at the way many AFCIs behave, they will trip on a gross ground fault. This is no accident; instead, they rely on this behavior to catch arcs-to-ground ...
ThreePhaseEel's user avatar
14 votes
Accepted

Do AFCI and GFCI protect against cheap equipment and bad wiring?

Do AFCI and GFCI protect against cheap equipment? Not really. A GFCI will limit a shock and an AFCI will limit arcing. There are many other things that can happen with non listed equipment. I ...
Ed Beal's user avatar
  • 103k
14 votes
Accepted

Dual Function AFCI/GFCI breakers trip under any load

It looks like your photographs show the neutral wires landed on the neutral bar. This is wrong. For GFCI breakers, the neutral wire must be connected to the neutral screw on the breaker and the white ...
DoxyLover's user avatar
  • 12.7k
11 votes

Bosch Drawer Microwave causes ARC Faults

Don't ignore the possibility that this may be an actual fault in the appliance, or at least that the manufacturer may accept responsibility. I have had a similar issue with two different appliances (...
StayOnTarget's user avatar
  • 5,545
10 votes

When to change Cutler-Hammer electrical panel and breakers?

Panels normally get replaced because more breakers are needed than are available in the existing panel or the total load requirements exceed the panel rating. Panels can also be replaced because the ...
JACK's user avatar
  • 80.5k
10 votes
Accepted

Bosch Drawer Microwave causes ARC Faults

Just got off the phone with both Leviton and Siemen! Thank you to Peter Duniho for having me file that AFCI Safety form, was super helpful in me getting in touch with Siemen! I'll put everything I've ...
Arian F's user avatar
  • 371
9 votes

Device keeps tripping AFCI device

we are the manufacturer of this device. We've never recommended to a customer to replace an AFCI with a non-AFCI breaker. What we recommended is simply to get your AFCI circuit breaker replaced with ...
Mark Aramli's user avatar
9 votes

Ground Fault Circuit Interrupter vs AFCI

GFCI and AFCI are as different as a seat belt, vs. the barrels on the highway that absorb impact energy if you would otherwise smash into a concrete bridge abutment. They are both vaguely about ...
Harper - Reinstate Monica's user avatar
9 votes
Accepted

How is "continuous wiring" defined in context of the 2017 NEC code?

Nope. Nope nope nope. You cannot use 210.12(A)(4) to put AFCI at an outlet. There are certain fairly rare cases where you can put AFCI at the first outlet. However, there is a misconception that ...
Harper - Reinstate Monica's user avatar
9 votes
Accepted

Is there a problem with using a dual function breaker when a CAFCI would suffice?

There's no downside to over-protecting a circuit beyond cost. So having GFCI on a circuit that isn't required to have it isn't an issue. You're more likely to have an arc fault on a lighting circuit ...
Machavity's user avatar
  • 24.8k
9 votes
Accepted

Does a laundry room circuit need GFCI protection?

The laundry room can be served by any number of circuits. However, at least ONE of the circuits must be a 120V/20A circuit that serves only receptacles in the laundry room. Any number of receptacles ...
Harper - Reinstate Monica's user avatar
9 votes
Accepted

New AFCI/GFCI instantly trips when installed downstream from a GFCI - no obvious reasons

I connected a new wire to the load screws, and attached the ground into the same ground screw, so this plug has 2 ground wires on the same ground screw Not allowed to do that. The screw isn't ...
Harper - Reinstate Monica's user avatar
8 votes
Accepted

What should I do if the AFCI breaker neutral pigtail is too short?

The AFCI wire needs to connect to the neutral bus. Put it on the other side, or add on to the length of the wire with a wirenut.
longneck's user avatar
  • 21.3k
8 votes
Accepted

Klein RT210 GFCI tester not triggering AFCI breaker

No. It should not. AFCI is designed to trip when the waveform changes to indicate arcing. It is primarily to protect against fire hazards from sparks. GFCI is designed to detect leakage to ground (...
Chris Cudmore's user avatar
7 votes

Refrigerator trips new AFCI/GFCI circuit breakers

Kitchen counter receptacles need to be GFCI protected. Refrigerators do not, and should not. A refrigerator is simply not what GFCIs are for, like manassehkatz says. All the electrical bits are ...
Harper - Reinstate Monica's user avatar
7 votes

should 30 yr old home have some/all breakers replaced with AFCI /GFCI? If so, which ones?

You've told us almost nothing about your house, and it's possible you wouldn't even know how to tell us what he is seeing. On the one hand, there are certain reasons why such breakers can be a very ...
Harper - Reinstate Monica's user avatar
7 votes

AFCI trips when adjacent breaker is switched on

Neutrals were crossed in the breaker panel. AFCI is happy now. Many many thanks 🙏 to everyone who took a few seconds from their busy day to help me.
Handydoc's user avatar
  • 121
7 votes

Why are multiple AFCI breakers tripping randomly in my new home?

Your grounds are certainly not the problem. More grounding is better, and an Ufer ground tied into the foundation is the best there is. 19 AFCI breakers, eh? And people wonder why we say "Go BIG&...
Harper - Reinstate Monica's user avatar
7 votes

Is it possible to tell from labels if the breakers are AFCI / GFCI in the main panel?

What you have there is a 10-space panel. The 100A main breaker is on the upper right. It is intended for 10 circuit breakers, but the panel permits use of "double-stuff" breakers. This ...
Harper - Reinstate Monica's user avatar
7 votes
Accepted

Is it worth installing AFCI and not just GFCI?

They protect from different things. AFCIs are primarily about preventing fires started by electrical arcs. They were (IMHO) not ready for prime time when they first hit the market, I think they have ...
Ecnerwal's user avatar
  • 214k
7 votes
Accepted

Can I use AFCI/GFCI outdoors

You can always use a higher level of protection than is required by code so the answer is yes you can. With the above statement I would caution you that there are distance issues and if you plan on ...
Ed Beal's user avatar
  • 103k