Mechanical or electrical device used to control a heating, ventilation, and air conditioning (HVAC) system, or other temperature reliant system.

2 votes

Smart thermostat with external transformer

) to diode pack at thermostat conductor 5: use for thermostat C. … Connect the loose wire to thermostat C. …
Greg Hill's user avatar
  • 33.4k
3 votes

4-wire to 5-wire thermostat conversion

Connect the new thermostat to the white, yellow, and green wires also. The last step is to bring the shared/common R and the local C from the new transformer to the thermostat. … The second terminal of the new transformer connects to the thermostat C terminal. …
Greg Hill's user avatar
  • 33.4k
2 votes

Where to "splice in" 24v C wire with no control board for new smart thermostat

The wiring diagram indicates that there's a yellow wire coming off the transformer, going into a wire nut with a blue wire. That's your C. I've highlighted it in the image below.
Greg Hill's user avatar
  • 33.4k
2 votes

Is my thermostat keeps losing power due to a furnace fault?

But the original text asks twice "how can I tell whether the furnace is hitting a temperature limit" or, said differently, "how can I tell whether the furnace stops heating before the thermostat said to … Disconnect the thermostat and connect the R and W wires directly. …
Greg Hill's user avatar
  • 33.4k
2 votes
Accepted

Theory: How do thermostats without a "C" common wire get powered?

A power stealing thermostat can let some nominal current flow -- not enough to activate the furnace relays -- and use this power for part or all of its own operation. …
Greg Hill's user avatar
  • 33.4k
3 votes

Controlling electric aux heat and oil heat as two separate stages with an Ecobee 3 Lite

A two-stage thermostat might normally make its decision about calling for the second stage of heat based on how far the present temperature is from the setpoint, or based on a timeout if it has been calling … An ordinary non-programmable thermostat mounted outdoors could even fit the bill (if it'll allow you to program a set point this low!). Two operating modes come to mind. …
Greg Hill's user avatar
  • 33.4k
6 votes

Modifying the thermostat of a regular AC to create a refrigeration room?

So modifying the thermostat is easy -- you can set the thermostat aside and use a jumper wire or wire nut to start experimenting right away. … There's more to it than just modifying the thermostat though. …
Greg Hill's user avatar
  • 33.4k
2 votes
Accepted

sampling low-voltage HVAC signals with digital hardware

A white "W" wire came back from the thermostat and connected to one side of a relay's coil. … A thermostat will open-circuit or tri-state its W/Y/G outputs when these are de-asserted. …
Greg Hill's user avatar
  • 33.4k
0 votes
Accepted

C-Wire for thermostat

Yes that blue wire sticking out of the cabinet looks like it's intended to be used that way. To verify use a volt meter to measure AC volts between the blue and the red wires. It should be somewhere i …
Greg Hill's user avatar
  • 33.4k
1 vote

April Aire 600 powers off while furnace is firing

Humidifier must run while the furnace runs Aprilaire model 600 operates on the principle of evaporation. It's an evaporative cooler ("swamp cooler") installed in the heating system. It's installed as …
Greg Hill's user avatar
  • 33.4k
1 vote

Aprilaire 600M Wiring to Honeywell TH8321 Stat

When the thermostat turns off its signal the water valve closes and the humidifier dries up. … Or, if the damper should operate only when the thermostat calls for heat, you could add a relay to make it so. …
Greg Hill's user avatar
  • 33.4k
3 votes
Accepted

Baseboard heaters turn off before reaching desired temp

The thermostat is actually switching off early: While the thermostat should be calling for heat, check the output voltage at the thermostat. … If you ever find that the thermostat output has switched off then you can focus your efforts on the thermostat. …
Greg Hill's user avatar
  • 33.4k
2 votes

Connecting two thermostats in parallel to control old millivolt wall gas heater

It seems that such a thermostat could control a millivolt system, though, if you wire things so that the thermostat operates a relay and the relay interfaces to the millivolt system. …
Greg Hill's user avatar
  • 33.4k
3 votes

Did I fry my Furnace Control Board? (C -> G rewire attempt)

How thermostat signaling works (and how to test manually) First, a little background about the thermostat control: It's dumb. Really dumb. The signaling is done by simply shorting wires together. … What probably went wrong To call for fan the thermostat will short R to G. But you had C on the G terminal, so the thermostat shorted R to C. …
Greg Hill's user avatar
  • 33.4k
2 votes

Trane comfort 2 thermostat keeps going blank

It appears your thermostat is a "communicating" type, which means that it uses a two-way digital communication between the thermostat and the air handler. … If you still have trouble with this arrangement then you can be confident there's a fault in the thermostat or in the air handler -- but it won't be clear which has the problem. …
Greg Hill's user avatar
  • 33.4k