The installation of wire and/or electrical devices, to allow the transmission of electricity from one point to another.
7
votes
Accepted
Wiring residential internet router through existing smoke detector
No. The 2011 version of the National Electrical Code made this very clear.
National Electrical Code 2011
Chapter 7 Special Conditions
Article 760 Fire Alarm Systems
760.41 NPLFA Circuit Power Source …
3
votes
I would like to eliminate 2 3-way switches on one circuit
National Electrical Code 2014
Chapter 2 Wiring and Protection
Article 210 Branch Circuits
210.70 Lighting Outlets Required.
(A) Dwelling Units.
(1) Habitable Rooms. …
0
votes
Wire Gauge/Type for 100amp detached Shop?
For a 100 ampere circuit, the conductors will likely be required to be 3 AWG copper or 1 AWG aluminum. However, if you care about power quality, you're going to want to increase the size of the conduc …
2
votes
What size metric wire is required for 240 VAC 30 Amps located in house with run of 90M or <1...
In the US, a 30 ampere circuit would use 10 AWG conductors. 10 AWG is 5.261 mm². However, if you're going 90 meters (295 feet), you might have to compensate for voltage drop. You might go up to 8 AWG …
8
votes
Will it work to hook up switches only with white wires?
And could be confusing for anybody working on the wiring, which could lead to a potentially dangerous situation. … Always use caution when working with wiring, especially live wiring.
Set the meter to measure voltage. …
1
vote
can I put 3 new light fixtures and switches on the same breaker
There should be no problem running 3 ceiling fans on a single 15 ampere circuit, though it will depend on what else is on the circuit.
Say a 52" fan is 90-100 watts (at high speed), plus three 60 wat …
4
votes
Can AWG 6 be used in the middle of a 20a AWG 12 circuit?
There's no problem using larger conductors in a circuit, other than it might be confusing to anybody that comes along later. You'd also be wasting money, if you're buying the larger cable.
2
votes
Accepted
Identifying unspliced pass-through wires in a receptacle box
National Electrical Code 2014
Chapter 3 Wiring Methods
Article 314 Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings, and Handhole Enclosures
314.16 Number of Conductors …
0
votes
Accepted
Sorting out the 3-gang box for smart switches
Your plan sounds about right, but you'll likely run into trouble fitting all the wires in the connectors. Wire connectors have a limit to the number of wires they can connect, so you'll have to be aw …
1
vote
Is there any issue with me splicing a continuous neutral wire and connecting a Wemo switch t...
No. If you're sure it's the grounded (neutral), and there's enough slack, go ahead and use it. Just make sure you turn off the power, before cutting the wire.
4
votes
Wiring connections for cooktop range
If the feed only has two wires (not including ground), it's possible that it's only 120 volts (hot, neutral, ground) or 240 volts (hot, hot, ground). If there's only a single pole breaker, then it's p …
2
votes
Cat6 shielded cable or no?
According to the National Electrical Code. You can only run communications circuits in conduit with electric power conductors, if they are separated by a permanent and listed barrier (800.133(A)(1)(d) …
6
votes
Accepted
Can I connect one end of an in wall wire to an electrical plug?
The best bet is to install an inlet where you're transitioning from cord to fixed wiring. You don't want to run flexible cords through walls/ceilings, so you'll want to find a way to avoid that. … So you'll end up with something as follows:
Surge protector -> male end plug -> cord -> female end -> inlet -> fixed wiring -> receptacle where projector can plug in. …
1
vote
What to do with white neutral wire?
Yes. The white wire is simply there in case the device also required 120 volts. as it sounds like the device is straight 240 volts, the white wire is not needed. Cap it using a twist-on wire connecto …
5
votes
converting my shop to 220v
Sure.
Pull four appropriately sized conductors from the main panel, to the new shop panel.