Skip to main content
Search type Search syntax
Tags [tag]
Exact "words here"
Author user:1234
user:me (yours)
Score score:3 (3+)
score:0 (none)
Answers answers:3 (3+)
answers:0 (none)
isaccepted:yes
hasaccepted:no
inquestion:1234
Views views:250
Code code:"if (foo != bar)"
Sections title:apples
body:"apples oranges"
URL url:"*.example.com"
Saves in:saves
Status closed:yes
duplicate:no
migrated:no
wiki:no
Types is:question
is:answer
Exclude -[tag]
-apples
For more details on advanced search visit our help page
Results tagged with
Search options answers only not deleted user 27099

For questions dealing with 240 volt electrical circuits, devices, and equipment. This tag covers the similar voltages as well (i.e. 220, 230, etc), since they generally refer to the same thing. Use with the [electrical] tag.

1 vote

Using ent conduit “smurf tube” for 4 4awg wires

ENT is A-OK for residential mains wiring Actual UL listed ENT ("smurf tube") is a perfectly fine mains wiring method in 99% of the work we see around here, allowed basically everywhere NM can be used …
ThreePhaseEel's user avatar
1 vote

240V outlet not working, reading 120V on each leg, 0V between legs

This is fine as long as you're dealing with 120V circuits; however, a 240V circuit requires two breaker poles that land on adjacent bus stabs. … As a result, either your faulty 240V circuit was fed by a pair of handle-tied single-pole half-width breakers (which the rejection feature can't stop from being mis-inserted), or the installer must have …
ThreePhaseEel's user avatar
0 votes

How many amps per leg on a 220V circuit?

10A in one hot, 10A out the other hot A 240V-only piece of gear connects to two hot legs and a ground (no neutral), so if it pulls 10A, that 10A has to be going in one hot leg and out the other hot leg …
ThreePhaseEel's user avatar
4 votes
Accepted

Do 240 volt dryers need to be AFCI protected

No -- the 2014 NEC only calls out AFCIs for 120V, 15 and 20A outlets -- the dryer is 240V, so it doesn't need an AFCI. 210.12 Arc-Fault Circuit-Interrupter Protection. …
ThreePhaseEel's user avatar
0 votes
Accepted

New mini split ac on existing Spa disconnect

You either need to run a ground or get rid of the outlet Right now, the GFCI hooked to the disconnect in your picture effectively bootlegs ground off of neutral, and the disconnect box itself is grou …
ThreePhaseEel's user avatar
2 votes

Whirlpool electric dryer works on 120 but not 240

However, whoever wired your house wired it as if they had a normal, 120/240V, 3-wire, split-phase service coming in; we can tell this both from the undersized service neutral coming in (for a 100A service … In particular, using a 120/240V, 3-wire distribution panel with a utility-supplied 120V, 2-wire (Form 1S metered) service is forbidden, as if it were allowed, NEC 710.15(C) would then be superfluous: …
ThreePhaseEel's user avatar
2 votes
Accepted

Two 240 volt runs off same breaker

Disconnect the old run then hook up the new one Since we're dealing with EVSE (a Tesla charger) here, we need to provide a dedicated branch circuit for that EVSE as per NEC 625.40: 625.40 Electric Ve …
ThreePhaseEel's user avatar
1 vote

Best way to add a 240v 30A circuit

Your easiest bet will be a cross between 1 and 3 Your easiest and simplest bet is a cross between approach 1 and approach 3, using a subpanel with a breaker interlock between the two breakers in it to …
ThreePhaseEel's user avatar
1 vote

How to splice 220 line to use for multiple uses

Furthermore, once you did that, the generator inlet would be live, with live prongs sitting there waiting to zap unsuspecting folks with 240V. …
ThreePhaseEel's user avatar
2 votes

240v outlet not delivering 240 volts

I would treat the 277V reading as equivalent to 240V in your case, as your tester is likely just a bit out of calibration (single-family dwellings are served by 240/120 split phase or occasionally 208Y …
ThreePhaseEel's user avatar
2 votes
Accepted

What wire do I need when replacing with a higher gauge for a new cooktop?

Running 6/3 is future-resistant, but only a conduit is future proof While many modern cooktops are designed for worldwide usage, running all controls and power electronics on 240V as that's what's guaranteed …
ThreePhaseEel's user avatar
4 votes

How should I secure an unused wire in my breaker panel?

Land it on the neutral bus Since you have the correct breaker in there for a mixed 120/240VAC circuit, simply land the white wire on the panel neutral bus -- this way, it'll be readily available for …
ThreePhaseEel's user avatar
1 vote

Add 240V / 60A for Swim Spa

You should be good to go on service size I ran a quick load calculation with your square footage, 4 kitchen + 1 laundry circuit (counting GD+DW as one SABC and treating the fridge as lighting load), a …
ThreePhaseEel's user avatar
4 votes
Accepted

Can I extend a 240 V line?

You'll have to pull the box out and rearrange things While it sounds like you have all the correct wires available to extend this on as a four-wire connection to your new range location, your last in …
ThreePhaseEel's user avatar
4 votes
Accepted

Can I handle-tie two 120V CH breakers for a 240V load?

This means that the combination of 2 single pole type CH breakers and a handle tie is only usable for 240V only or 120V only circuits as per NEC 240.15(B)(1) and 240.15(B)(2): (B) Circuit Breaker as …
ThreePhaseEel's user avatar

15 30 50 per page