Skip to main content
Search type Search syntax
Tags [tag]
Exact "words here"
Author user:1234
user:me (yours)
Score score:3 (3+)
score:0 (none)
Answers answers:3 (3+)
answers:0 (none)
isaccepted:yes
hasaccepted:no
inquestion:1234
Views views:250
Code code:"if (foo != bar)"
Sections title:apples
body:"apples oranges"
URL url:"*.example.com"
Saves in:saves
Status closed:yes
duplicate:no
migrated:no
wiki:no
Types is:question
is:answer
Exclude -[tag]
-apples
For more details on advanced search visit our help page
Results tagged with
Search options not deleted user 18763

Grounding (also called earthing) refers to the practice of providing an un-energized path back to the main neutral. This is done to allow any electrical faults to flow into that circuit, instead of anyone touching the fault. Use with the [electrical] tag.

1 vote
Accepted

Apartment with no grounding/earthing... do I really need it?

Ungrounded systems have existed for 100 years and still do in the USA and Europe. The National Electrical Code in the USA still allows many systems to remain ungrounded including older systems insta …
ArchonOSX's user avatar
  • 20.6k
2 votes

old home. no ground wire

No. "Romex" is a trade name and is actually a brand of non-metallic cable or NM cable. Article 334 of the National Electrical Code. If your house was wired with NM cable in the 50's or before, it mos …
ArchonOSX's user avatar
  • 20.6k
2 votes

Outlet tester shows "bad ground"

The equipment grounding conduc- tor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. … Any installed grounded conductor shall not be connected to the equipment grounding conduc- tor or to the grounding electrode(s). …
ArchonOSX's user avatar
  • 20.6k
4 votes

How do you add a separate ground back to panel on 2 wire ungrounded outlet?

The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following: (1) Any accessible point on the grounding electrode … system as described in 250.50 (2) Any accessible point on the grounding electrode conductor (3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle …
ArchonOSX's user avatar
  • 20.6k
1 vote

Off Grid PV System Grounding Question

First off you should tell us where you are on the planet in order to get accurate answers. 1)There are 8 grounding points in the drawing. Which of them should be bond together? … There is no exact answer here. 3) Where should I connect the Neutral Line to the Grounding Rod? As close to the main service panel as possible. Good luck! …
ArchonOSX's user avatar
  • 20.6k
2 votes

Can I put 15 amp switches on 12 gauge wire

Yes. As long as the switch is rated for the amperage of the load served and the voltage of the circuit. Your instance is an example of this (as long as the switches are rated for the voltage). Here is …
ArchonOSX's user avatar
  • 20.6k
1 vote

Can I ground junction box directly to panel?

You should run another equipment grounding conductor from the panel to the box. … Then splice the equipment ground and bond it to the box with a #10/32 green grounding screw in the tapped hole in the box. Good luck! …
ArchonOSX's user avatar
  • 20.6k
3 votes

What problems might a single ground rod above 25 ohms resistance cause?

less than 1.83 m (6 ft) from any other electrode of another grounding system. … Two or more grounding electrodes that are bonded together shall be considered a single grounding electrode system. …
ArchonOSX's user avatar
  • 20.6k
7 votes

Installation of a GFCI without a ground wire

From the 2011 National Electrical Code 406.4(D)(2)(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). … An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle. …
ArchonOSX's user avatar
  • 20.6k
3 votes

Looking for or adding a ground to an existing NEMA 10-30 socket

Electric vehicle supply equipment intended for connection to nonlocking, 2-pole, 3-wire grounding-type receptacle outlets rated at 125 V, single phase, 15 and 20 amperes or from a supply of less than 50 … Grounding for a circuit in a garage is especially important. …
ArchonOSX's user avatar
  • 20.6k
6 votes

Main service electric panel has no neutral wire - both neutral and ground wires on same bar ...

Up until 2011 the National Electrical Code allowed a "3 wire" method of connecting a sub-panel. This means you have the two "hot" wires and a neutral running to the sub-panel as opposed to the "4 wire …
ArchonOSX's user avatar
  • 20.6k
2 votes
Accepted

Where should shielded data cables be grounded?

The industry practice is to ground the main panel end and leave the field end ungrounded. If you ground both ends you create an antenna for RF interference. Search the web for dipole antenna design. …
ArchonOSX's user avatar
  • 20.6k
1 vote
Accepted

Should a stove flue be grounded for lightning protection?

A lightning protection system is a building wide system. You don't just protect things individually. The ridgeline of your house would get air terminals and then if the antenna and chimney are withi …
ArchonOSX's user avatar
  • 20.6k
1 vote

Open ground on all outlets, voltage meter beeping on metal boxes and MC cable

Well, don't trust the no-contact tester to tell you anything but the presence of voltage somewhere close to the end of it. Beyond that they aren't much use. From what you said in #4 you have an open …
ArchonOSX's user avatar
  • 20.6k
1 vote

Is it personal preference or code to connect grounding wires and neutrals to separate buses?

In the Main service panel it is personal preference as that is the location where the neutral and ground are bonded anyway. At a sub-panel separation of the neutral and ground is required by the Nati …
ArchonOSX's user avatar
  • 20.6k