Is my plan for adding a sub-panel reasonable?
I'm not a licensed electrican, but know quite a bit about it and the code and have done a lot of wiring. …
3
votes
Powering multiple switches from one switch
As usual, hate to say it, but "it depends". There are essentially 2 popular ways to connect switches for fixtures:
Provide power to the fixture and run a "switch loop" to the switch. If that's the …
0
votes
Using 2 3way switches in a single pole double gang box
Not sure what you mean by "The 3 way switches have a "neutral wire in, a hot wire in and 2 traveler wires coming out of them". Then you said, "all the whites are connected". So that needs clarificati …
5
votes
Can I repurpose an HVAC circuit for shop outlets?
Short answer is yes, but... You might want to consider a small sub panel (outdoor rated) there if you have a 4 wire service to that location. That way, if your needs change (IE: grow), you'll have the …
1
vote
NEMA 6-20R amperage
That panel is already populated with many double-stuff breakers, so no loving there for making more room. Unless you are willing to replace the entire main panel with one that has more spaces, your b …
2
votes
Wire size to run 200' to a shed
The capacity of the sub-panel isn't what's important, you could put in a 200 amp panel configured as a sub-panel and feed it with 14 ga wire on a 15 amp breaker. Not a good idea at all, but it could …
2
votes
Lights in swimming pool not working
If you get power across the 2 terminals when the switch is "on" (closed), it means your switch has failed and needs to be replaced. Of course be sure to turn off the power before replacing and if this …
0
votes
100 amp service wire size from transformer to meter/panel
If running aluminum (which is fine), 2/0 is the right size for 100 amps. You also have to consider what you are running is it a continuous load, like lamps for a grow operation? Bitcoin mining? Or ju …
0
votes
Accepted
Is one of these wires inducing a current in the other?
Voltage and Current are 2 very different things. Voltage is like pressure in a water line, current is the flow rate. A tiny 1/4" at high pressure isn't going to flow a lot of water, a fire hydrant at …
-1
votes
How does a "pulling grip" wire puller work?
I"ve used fish tapes in the past and really don't like them. Now when I need to pull wires thru conduit I use a thin but strong rope with the end tied to a plastic shopping bag (or other means) and …
2
votes
Can I run a #6 circuit from a subpanel fed by #6 wire?
The important part is proper over-current protection for the wiring and, since it's hard wired, the device (the hot tub). …
3
votes
Accepted
Wiring an induction cooktop
I agree with Jim. Just cap the white wire in the box. You are fortunate to have a 4 wire feed, in most cases here people have the opposite problem: "Requiring a 4 wire feed for a new cooktop but on …
2
votes
Should lights on a three-way circuit connect to the switch with the power cable attached?
There are several ways to connect 3 way switches. I always prefer the 2nd method you posted. There is no "code taping" needed, since all the wires are already the correct color. The 2nd method is s …
4
votes
240V outlet not working, reading 120V on each leg, 0V between legs
Hmmm. Are the working and non-working outlets on different circuits? If so, it sounds like your alleged "electrician" put the 2 hot wires for the non-working outlet on the same phase. If so, I'd have …
2
votes
Is it ok to switch wires from gauge 12 to 14 inside a box?
I don't think so. Unless you change the breaker protecting that circuit to 15 amp and mark the wires. I made the mistake of running 12 ga wire for lighting when I built my house 15 years ago. LEDs did …