Are you sure you aren't doing this the hard way? 
----

A **lot** of people believe that "GFCI" means the ugly square receptacle with the Test and Reset button.  That's not true at all.  

GFCI is a level of protection provided to a *circuit*.  Current flows in loops -- GFCI compares current on the hot and the return (neutral) - if they are not equal, leakage is occurring.

This can work anywhere in the circuit.  The closer to the circuit breaker, the better, because that protects more of the circuit (including the wires, which does help).  In fact they make [GFCI circuit breakers][1], and those are a very elegant way to solve this problem!  **The GFCI Breaker protects every single receptacle on its circuit.**

*Super important point right there.*

GFCI *breakers* can be expensive.  You can do the same thing by adding a **GFCI module** *before the first receptacle*.  The module takes hot and neutral from the panel (in its LINE inputs).   It gives GFCI-protected power out its LOAD outputs.  Easy peasy, cheaper than a breaker. 

Wiring that can be a little awkward.  But receptacles are wired in a chain.  You can just find the first receptacle in your chain, and replace it with a GFCI module, and feed the rest of the circuit off tis LOAD terminals obviously.   A GFCI module designed to replace a receptacle [looks like this][2]. 

*Hold on. That looks like there could be sockets there.*  That's true.  *Can it protect the downline circuit via the LOAD terminals and also have sockets there?*  Yes it can.  *Can I get those?*  **You already have.**  That's what you've been installing all along.

The point 
----
Stop thinking of GFCI "receptacles" *as receptacles*.  Think of them as **dedicated GFCI protective devices** designed for the *singular purpose* of **protecting downstream loads** via their LOAD terminals... and also they *just happen* to have a couple of convenience outlets on their front.  

Back to your switch
-----
It's rather awkward to fit a half-GFCI half-switch.  Aside from being an expensive oddball, it raises more questions than answers - is the switch side protected?  Do I break tabs off, or not?  How do I avoid confusing my neutrals and causing a big problem? How do I even wire this thing?  HELP!

We can **avoid the entire exercise** by simply fitting a GFCI protective device upstream if it.  Either *as* the breaker, or at a receptacle location that is before the switch location.

I would just change the coverplate so it matches. You could change the switch/receptacle, but those darn things are like $10.  Ouch. 

Get yourself a GFCI tester (a common 3-lamp tester with an extra "Test" button) and you will be able to defintively tell when an outlet is protected. 


One more thing.

When you install a GFCI receptacle or deadfront, reset it (make sure it's on) -- and then shut off the breaker for 10 seconds.  Turn it back on.  Did the GFCI trip *simply* from shutting off the breaker?  If it did, back to the store it goes - that one is a poorly made piece o' junk.  Quality GFCIs don't do that.  

**And the labels.**
Lastly if a plain receptacle is protected by a GFCI, it needs up to 3 labels on it, if the fact on the sticker is not obvious.  (2-prong sockets don't need "No Ground" stickers, duh... things with Test and Reset buttons don't need "GFCI protected".)

 - "GFCI Protected" - the inspector must see these on *plain outlets* to approve them.
 - "No Equipment Ground" - required only if the receptacle has a ground pin, but isn't grounded.  
 - *Reset in laundry room* etc. for unexpected locations of the GFCI reset.  This isn't required by law, just a good idea.