## Your problem isn't "two load centers on one meter", its "two wires in one lug that's probably not tested for such use"

While having multiple service panels fed in parallel from a single meter is fine, the devil is in the details, and that's where your current setup fails.  Atop the high chance that this is a dual 100A meter base to begin with, which means you're overloading the currently in-service meter socket, the definite issue with inspection is that right now, you have *two wires connected to the same lug* in a way that the lug was never intended for, which is a violation of NEC 110.14(A).

Considering the issue, I would have the existing base changed out for a single 200A meter socket with suitable *tap lugs* (a Milbank 200A base with a set of Milbank K5022-INT lugs would do the job) or a 200A meter-loadcenter with 2 100A branch breakers in it.