To test a bad neutral simply test the known hot to a good ground. Hot to ground should return 120 Volts and hot to neutral would read something irregular.

In the case the ground is either bad or missing simply run a drop cord from a working outlet and test the ground to the hot.

Isolating the open neutral can take a bit more work, but you can save yourself some time by following these steps...

  • Isolate the branch circuit breaker. See if it is labeled and what portions of the house may be using it.
  • Identify what is working on the branch circuit breaker and work your way upstream toward the non-working area until you can localize it to a room or similar area.
  • Once you've localized the area turn off the circuit breaker.
  • Next, start by inspecting the attic or other unfinished areas such as the basement or crawl space to learn the layout of the wiring. This will give you a better idea of how the electrician wired the branch circuit and help you better isolate the problem. If you don't have any unfinished areas then one by one inspect behind each outlet, switch box, recessed light, or similar for any signs of a lose neutral.
  • After checking and reconnecting any suspicious taps you can reset the circuit breaker and test.
  • Repeat as necessary.

###Alternative Step

  • Purchase a 77HP-G Tone Generator
  • This device goes on the source conductors ( black and white ) after the breaker has been turned off. This only works on open circuits, that is, non-continuity between conductors. A fault to ground for example will not work.
  • It sends out a audio frequency on the conductors that the probe will amplify.
  • The source of the problem can be isolated to some extent but using the device takes practice.

Worst Scenario

  • It does happen that some junction boxes will get covered up and hidden from previous renovations and remodels. This is an unfortunate reality that makes isolating the problem quite messy. Other than opening up the walls there is no other way.
  • Similar to hidden junction boxes are wire staples and nails that during the building of the house either were hammered too hard damaging the wire conductors or penetrated the wire because of negligence and/or improper installations. Again, the only solution is to open up walls and ceilings.