## Your problem isn't "two load centers on one meter", its "two wires in one lug that's probably not tested for such use"

While having multiple service panels fed in parallel from a single meter is fine, the devil is in the details, and that's where your current setup likely fails.  Atop the possibility that this is a dual 100A meter base to begin with, the more likely issue with inspection is that right now, you have *two wires connected to the same lug* in a way that the lug was never intended for, which is a violation of NEC 110.14(A).  Fixing this would require using some mechanical lug (Polaris) connectors to splice the two wires for each leg to each other and a 2/0 Cu pigtail that leads up to the meter base lug for that leg.