Questions tagged [subpanel]

For questions about an [electrical-panel] that is fed from another [electrical-panel] instead of being fed directly by a utility service or separately derived service (such as a generator or inverter).

Filter by
Sorted by
Tagged with
3
votes
6answers
41k views

Grounding requirements for main panel and subpanel

I recently had my main service professionally upgraded to 200A and had a 60A subpanel installed in my master suite to support future additions. All work passed city inspection, for whatever that's ...
1
vote
1answer
4k views

Single sub-panel from 3 phase panel and the main breaker size

I have an old 3 phase panel next to a separate single phase 100 amp panel that is being used by one residence. This space has been used as a carpenter shop and an office in the past. Now it is being ...
1
vote
0answers
780 views

Feeder type and size for 60 amp. subpanel

Is it possible/recommended to use E18679 (UL) ROMEX SIMPull AWG 6 CU 3 with AWG 10 ground Type NM-B 600 volts as feeder from a 60 amp breaker to install a subpanel? Subpanel will be located in ...
2
votes
1answer
7k views

What size feeder do I need for a basement electrical subpanel?

I would like to know what size and type of feeder wire and feeder breaker do I need for my basement subpanel where I am planning to add six 15 Amp circuits, and three 20 Amp circuits. This will be 2' ...
2
votes
1answer
3k views

How can I make 3 wire sub-panels compliant with current codes?

The sub-panels in my house are all split-phase 3 conductor with neutral and grounds mixed. Is there any way to make this compliant without running new 4 conductor feeders? (Some of the feeder cables ...
2
votes
2answers
112k views

What size wire should I use for a 60amp subpanel?

I am installing a 60 amp subpanel in a workshop in my backyard and I will have 2 - 20 amp services with 4-5 outlets on each and 1 - 15 amp service for lighting. The length from the main panel to the ...
3
votes
1answer
2k views

Should I connect the bare ground wire from the main panel to the grounding bar in the subpanel?

I have a main panel that was converted to a sub panel when a new Main Panel was placed in a new addition to the house. So now, the subpanel appears to have two grounding wires connected along with ...
0
votes
1answer
136 views

Electric line to subpanel

I'm running 2 100 amp 110 lines 35 yards from my well house main to a sub panel in my garage. Do I need to run a ground wire and a neutral wire or can I just run one of them from the sub panel to a ...
3
votes
1answer
1k views

Can I add a sub-panel near the main disconnect outside my house?

I have an outside main disconnect of 125 amp and a inside main panel. The disconnect panel outside has an extra space that will accept a dual pole breaker. What I would like to do is add a sub-panel ...
3
votes
2answers
10k views

Sub Panel Install - Main Panel Full

I am looking into installing a sub panel in my basement which will be used to feed electrical circuits to the basement that is currently unfinished. I have an 150 amp main panel and was thinking of ...
1
vote
2answers
95 views

Grounding subpanel to box - 'tap threads'

I've installed a subpanel and need to ground the grounding bar to the actual panel box. I was instructed to run a #6 jumper to a hole on the box, attach with a screw, making sure to 'tap threads'. ...
0
votes
1answer
517 views

Adding electrical service to detached garage

Please let me know if this sounds correct- Sub panel fed from 80amp breaker in main building 200amp load center. Roughly 75' of 1" PVC conduit from existing load panel, under existing timber deck, ...
1
vote
0answers
75 views

Sub Panel Remote Control?

I would like to know if it is possible to have a relay control power to a sub panel? I am thinking of wiring a cottage with most of the lights in one sub panel. I would like to be able to power this ...
3
votes
2answers
3k views

subpanel ground requirement - attached vs unattached structure - what difference does it make?

Subpanel in the garage is currently fed by 10-2 w/ground romex and is grounded both at the main panel via the ground wire and to the plumbing next to the subpanel (underground iron pipe). I want to ...
0
votes
2answers
3k views

Should both ground and neutral in an electrical subpanel be bonded to the service ground?

I put in a 100 AMP sub panel from a 200 AMP service. The neutral and ground are separated in the sub panel. Would this bond the sub panel to the ground and neutral coming from service ground wire? I ...
2
votes
1answer
5k views

Sub panel and neutral and ground bus bar

Some HVAC people under previous home owners put in a sub panel box and ran the AC as well as some lighting and outlet circuits from the sub panel. The bus bars on the two sides of the panel box were ...
1
vote
0answers
196 views

Sub panel cable feed code

The inspector failed the sub panel box location because it only had 6 feet clearance and not 6.5. The electricians came and moved the sub panel box, but they did not run a new feed cable. They put a ...
8
votes
2answers
82k views

Why does a subpanel need separate ground and neutral?

Why does a power sub panel have to have separate neutral and ground bars other than code satisfaction? Does a sub panel need a main breaker if there is one at the main? Also, does the sub panel ...
2
votes
3answers
2k views

Can I replace the main breaker in an electrical panel with a smaller one?

I have an older 60amp fuse box in a rental property that is wired as a sub panel off my main 100amp service. I would like to upgrade to a new circuit breaker panel so tenants can not pull out the ...
4
votes
3answers
7k views

What is wrong with this panel wiring?

I have a main breaker panel downstairs, and a subpanel upstairs. After I hired an electrician to rerun the service entry cables, nothing upstairs is right, and all the upstairs lights blew as soon as ...
1
vote
0answers
43k views

What size wire do I need for a 100amp underground 300 ft run?

I want to put in a 100amp subpanel in my garage. The run will be underground and 300ft long. I have a Siemens panel with breakers rated at 60/75 deg C. What is the proper wire size I need? I was ...
3
votes
3answers
2k views

Why am I getting no power to the branch circuits with a new sub-panel?

My home had an ancient Zinsco sub-panel in which the breakers were grounding out and arcing to the panel. I've swapped it with a new Eaton 100 amp panel. I've re-installed all the breakers, and re-...
1
vote
1answer
18k views

Can you put a small breaker panel after a 30 amp breaker from main panel in the house?

Looking to run lights in my garage. If I put a 30 amp breaker in my main panel on a 10 wire to a small breaker panel in my garage, can I put 2-4 15 amp breakers out there for the lights? Likewise, ...
0
votes
1answer
2k views

What subpanel and number of circuit breakers should I install in a detached garage?

I no longer am dealing with my contractor. Long story. But he ran 2 10-3 wires out to my garage for power. I think he was planning on putting a 30 amp breaker on the panel in the house for each wire ...
1
vote
1answer
10k views

How to determine what type and gauge of wire should used for underground wiring to a detached subpanel?

I Will be installing a subpanel in a detached garage. The subpanel will be 60 amp. The garage is about 30' from the main-panel in-house, and I will of course get an exact length before selecting the ...
2
votes
4answers
25k views

How do I determine the fill rating of a conduit?

I Will be installing a subpanel in a detached garage. The subpanel will be 60 amp. The garage is about 30' from the main-panel in-house, and I will of course get an exact length before selecting the ...
9
votes
4answers
121k views

How to properly ground a subpanel in detached building?

I Will be installing a subpanel in a detached garage. The subpanel will be 60 amp. The garage is about 30' from the main-panel in-house, and I will of course get an exact length before selecting the ...
4
votes
3answers
36k views

What type of wire should I use to feed a 70 ampere subpanel?

Finishing a basement and I need to add a subpanel. Main panel is outside. Subpanel will be in the basement. 70 Amp breaker in the main to feed the subpanel. I was thinking THHN but would this mean ...
8
votes
3answers
16k views

Can an electrical subpanel go underneath plumbing?

I was about to wire up my new basement subpanel when I realized I had put it directly under a toilet. I don't think this is a code violation. I can relocate it with some difficulty. I'm also ...
0
votes
2answers
10k views

Can I connect my generator transfer switch to a subpanel instead of to the main panel?

My house has a generator transfer switch (ProTran 30310B) attached to circuits in the main panel (see photo). I added an attached garage to the house. I want to add a subpanel in the garage, ...
3
votes
2answers
10k views

Do I need conduit for an indoor sub-panel feeder line?

I'm adding a 100A sub-panel to feed a stove and water heater. The sub panel is indoors and in the same building as the mains panel. Do I need to run the supply feeder in conduit? I'm in Michigan and ...
5
votes
6answers
35k views

Can I install a Subpanel (in a seperate building) using a 3 wire connection (2 hots and 1 grounded neutral)?

Can I use a 3 wire connection (2 hots and 1 grounded neutral) to install a sub panel in a separate structure if I install a separate ground rod to the grounding bus in sub panel? I have 8/3 w/o ...
1
vote
1answer
664 views

Why is one half of a subpanel not working?

I have 12/3 wire running out to my garage. I have a double 20 amp breaker in main box and a subpanel with two single 20 amp breakers in the garage with black to one breaker and red to the other. The ...
5
votes
2answers
4k views

Does the neutral wire float or go to the neutral bus on a sub panel?

Does the neutral wire float or go to the neutral bus on a sub panel?
1
vote
1answer
596 views

Can I install a subpanel using only two ungrounded (hot) conductors and a grounding conductor?

we removed the inside part of an air conditioner / heater from a mobile home. we plan to use this area as a small pantry. The wires that were connected to the heater is 2 black connected to 2 seperate ...
12
votes
1answer
156k views

What size wire should I use to feed a subpanel in my garage?

My main panel has been upgraded to 100 amps. I would like to add a subpanel in the garage which would supply: 20 amp Mig welder running on 120 volts, but later upgrade to a larger Mig welder as i ...
21
votes
3answers
654k views

What wire gauge do I need for a 100 Amp subpanel at the end of a 60' wire run?

I am adding an attached garage to my house. I'm going to be putting in a 100 Amp subpanel which is about 60 feet away and run through the basement joists. What gauge wire do you recommend for ...
0
votes
1answer
388 views

Should I reorganize the main service panel when adding a subpanel?

I am currently in need of a new 240V circuit for a welder in the garage but my main breaker is full. Adding a subpanel seems to be the only solution that would be to code, but I have a couple ...
12
votes
2answers
147k views

How do I properly ground my subpanel that only has one neutral/ground bar?

I am adding a sub panel in an unattached building. My sub panel has the connection for the 2 hot wires coming from the source panel (a 40 amp double breaker) In addition it has one neutral/ground bar ...
4
votes
2answers
760 views

How can I insulate a stud bay containing a subpanel?

I'm putting a subpanel in the outside wall of my attached garage, which I'm also insulating so I can work out there in the winter. I'm wondering what steps are worthwhile to air seal and insulate ...
8
votes
1answer
4k views

What wire and conduit is required for an attached-garage subpanel?

To make my garage more usable as a workshop, I'm planning to add a subpanel which can feed a number of additional outlets. 60 amps would be plenty for my current needs, but I'd like to go with 100 so ...
3
votes
4answers
9k views

How can I install an electrical panel when the stud cavity is too narrow?

I am installing a sub panel in my garage and ran into a problem. I have the usual 14" of space in the stud cavity but the problem is that the subpanel I bought is 14 1/4" wide. I'm wondering what ...
7
votes
2answers
47k views

Can I feed a sub-panel from a sub-panel?

here is what I have. On the corner of my house, I have the main breaker box. I also have a 2nd sub panel that was installed later on the other side of the house which has 240V ac running to it. This ...
3
votes
1answer
3k views

Can I use my old service panel as a sub-panel when I install a new one?

The main panel in my building is 100 feet from the where the feed wire comes in from the outside meter. Can I install a new 200 amp panel where the feed line comes in and use the existing wire to feed ...
9
votes
2answers
53k views

How to determine the correct capacity for a sub-panel for a shop?

I plan to install a sub-panel for my woodworking shop, and would like to determine the total capacity that should supply that sub-panel. These are the main items that will likely be running in the ...
4
votes
1answer
4k views

How can I add 100 amp electrical service to a shop?

I am going to wire my shop and want ot run #2 copper to a 100amp breaker panel. I really do not have the space in the 200 amp panel in the house, my question - is there a way to pull this wire off the ...
10
votes
4answers
5k views

Would running a new subpanel in parallel meet NEC requirements? If not, what should I do?

Background U.S.A. Voltages/power present. My house has a 125A Power Mains breaker at the street. A buried line runs from the street breaker to my main panel on exterior wall outside of house. The ...