Questions tagged [subpanel]

For questions about an [electrical-panel] that is fed from another [electrical-panel] instead of being fed directly by a utility service or separately derived service (such as a generator or inverter).

Filter by
Sorted by
Tagged with
0
votes
1answer
72 views

Electrical power to a detached shop, 60 amp panel, 80 feet of wire, what size wire do I need?

I am running power through a conduit to a detached shop, 80 feet of wire, a 60 amp panel. What size and type of wire do I need?
2
votes
2answers
98 views

Grounding subpanel

I have a simple question, that I believe I already know the answer to, but just need confirmation before moving on. I had an electrician install a 100 amp subpanel installed on a newly built ...
1
vote
1answer
135 views

70 amp service from 200 amp main

We need to run conductor from a 200 amp main service panel to a sub panel that is approximately 200 feet away (50 inside garage, and 150 underground.) The breaker in the main panel that will feed ...
2
votes
1answer
57 views

Grounding a subpanel using existing wiring

I had a 60 amp breaker that was connected to an oven in the kitchen. Since this is no longer needed, I'm trying to re-purpose this #6 wire to connect to a new Electric water heater I'm putting in the ...
0
votes
1answer
74 views

What type and gauge ground wire do I need when using 1/0 hot and neutral wires

I have a 260 ft run from my main 225A panel to a 100A subpanel in a steel shop out in my yard. I have a #4 bare copper wire grounded to the rebar in the foundation of the shop. Not knowing what I ...
0
votes
1answer
36 views

RV pad with 125amp sub-panel

i built a RV pad for my brother. I also built a small laundry/storage room next to pad. I wanted him to pay for his own electricity so I ran 4 wires (2 hots, neutral, ground) from a 200 amp outside ...
1
vote
1answer
55 views

ground wire to neutral in a boathouse [duplicate]

Recently a home inspector flagged the panel box in a boathouse for having a ground wire attached to the neutral bus bar. The ground came from a jet ski lift attached to the boathouse. This 10 yr old ...
2
votes
1answer
84 views

What size breaker and wire for a barn feeder circuit?

February winds blew down my overhead service to my barn. I would like to replace the 1950's two wire service and update to a safe, sub feed using a complete new underground from a 150 amp house box. ...
1
vote
1answer
138 views

Can I connect a 70 amp sub panel to a 40 amp 240 breakers?

Can I connect it to a sub panel that is rated for 70 amp? I just want to put 3 or 4 20 amp 120 breakers in. Is it safe to do it?
1
vote
2answers
76 views

How can I reconfigure my breakers to make room for a sub-panel feeder?

Right now I have a 100amp main panel, it is full as of now. I have looked into tandem breakers for a Federal Pioneer Breaker Panel. I could not find any tandem breakers for this panel. So would my ...
0
votes
1answer
62 views

Main Load Center for subpanel

Can a main load center box with no main breaker be used as a sub panel in a detached garage. Was told to run a #2 copper since it was about 150 ft away from the house.
2
votes
2answers
527 views

Electrical design for a house with an ADU, solar, and backup generator

I recently moved into a fixer-upper house, and have some questions about how to go about (re)designing the electrical system in a way that meets my somewhat unique timeline and site requirements. ...
2
votes
2answers
407 views

Can a sub-panel have a larger main breaker than the feeder breaker in the main panel?

I have a weird setup that I'm trying to configure, but I'm only 90% certain of my logic (and with electrical items I want to be 100%). I have a new 400A meter/main combo unit with 1 built-in (...
0
votes
3answers
73 views

Outlets for 2 sheds

I want to run a couple of lines from my main box, 1 for 50 amp for my RV and then I want to have 9 shop lights installed (4 to run on one switch and the other 5 on a second switch) and 5 110 outlets ...
0
votes
0answers
36 views

GFCI Breaker Serving GFCI Receptacles Tripping in Extreme Fog and Cold

Lately, I have had an issue where sometime during the night the main GFCI breaker would trip. The only thing different on the nights that this happened was that one of the nights was (1) extremely ...
3
votes
1answer
265 views

Can I do a 125A subpanel feeder with slightly-larger-than-#3 wire?

How they are all connected: With all the details and data given below. So Can I do a 125A subpanel feeder with slightly-larger-than-#3 wire? This is detail directly related to the post. Question. ...
1
vote
2answers
46 views

Does a subpanel ground need to be insulated wire

I am installing a 60amp subpanel and want to ground the panel to a grounding rod. I have 8awg non insulated copper and want to know if it can be used for this or does it need to be insulated. It will ...
1
vote
2answers
100 views

Is a 60 amp breaker adequate for a 220v sub-panel to my garage?

150 panel in house. I want to run a 220 (sub-panel) feed to garage 25 feet away for 10,000 watt electric heater. There's room in the 150 panel. Would 60 amp breaker in the garage meet the 1.25 safety ...
0
votes
1answer
56 views

3 wire subpanel to a new 3 wire subpanel

I want to add a 100 amp RV service panel to my existing, detached garage, 3 wire subpanel. I understand that my current setup is grandfathered in and code is now 4 wire but I won't be able to add this ...
1
vote
1answer
583 views

Ground size for 100 amp sub panel 200ft away

I would like to install a 120/240 volt 100 amp sub panel on a detached garage that is about 200 ft away. I have read that one should strive for a voltage drop of less than 3% and from what I can tell ...
1
vote
2answers
815 views

Main Breaker Panel or Main Lug Panel for Sub-panel in Attached-Detached Garage

I am installing a ~100-amp sub-panel in my "attached-detached" garage (an "attached-detached" garage is a detached garage that shares a continuous roof with the home). The sub-panel will be fed by my ...
0
votes
1answer
55 views

How to wire a sub panel from a 15 amp circuit existing run

I'm adding power for an outdoor pond, I will need four outlets in the end. I have an existing 15 amp circuit out of my main house service panel that connects to an outside wall. I want to tie into ...
0
votes
3answers
159 views

When splitting a 240v circuit, what happens to neutral's amperage?

My garage has very limited power with only one outlet that I share with 3 bathrooms and every outdoor outlet, 4 total, on a 20 amp breaker. (House hastily thrown together in 97' for your reference) I ...
0
votes
1answer
67 views

Is my ground correct at my subpanel?

I have a subpanel at my garage. It has 2 hots, one neutral and one ground from the service panel. The neutral and ground in the subpanel are not bonded. All the outlets including GFCIs all work ...
0
votes
1answer
78 views

Can I run just one wire to the sub-panel via schedule 40 separate from the others?

I have a 25 year old recalled sub panel, three wire, converting to new Eaton 100A. Want to add a wire to meet code Is it allowed by code to run just one wire to the sub panel via schedule 40 to the ...
0
votes
1answer
97 views

Grounding a 3-wire sub-panel in attic

Early 1960's home. 200-amp main service panel on first floor. 3-wire (L-L-N) feeder to 100-amp sub-panel in the second floor attic, about 25-30 feet from the main service panel. Neutral and ground ...
2
votes
2answers
87 views

Mount subpanel on below grade stem wall

I am redoing my basement and I am putting in a new subpanel to handle a few extra circuits since my current panel is undersized (I wanted to replace it, but according to the electrician who I’ve been ...
0
votes
1answer
246 views

Does a sub-panel in an outbuilding require a ground wire or rod? [duplicate]

My main elect panel in the house has a common neutral/ground bar and not separate bars. If I run from this panel to a sub panel in a detached pole barn and attach the two hots for 240V and one ...
6
votes
3answers
1k views

Can I add a subpanel?

Let me start off with the facts: I have 125 amp service that is fed via overhead lines to a center fed panel. I am maxed out on breakers, as every 110v breaker is now a tandem breaker. When other ...
0
votes
1answer
105 views

Use existing 200A panel as temporary sub-panel off of new 320A service panel

Currently I have 200A electrical service that's brought to my house above ground and into the basement on the right side of the house, which feeds a 200A panel. I'm in the process of getting my ...
0
votes
1answer
82 views

Is the blue conduit connected to my sub-panel suitable for a 50A branch circuit?

I have to add a 50 amp circuit to the sub panel in my garage. I found one of the open knockouts in the top of the panel to have a blue flexible conduit looking stuff in it which runs up into the ...
2
votes
1answer
138 views

What size sub-panel and wire do I need for my three-season room?

I have a 15x22 room that is roughly 50' from the main panel, that I am converting from a 3 season room, into a conditioned space (heating and cooling, enclosed with windows and doors, etc.). ...
1
vote
1answer
429 views

How to deal with subpanel that does not have ground wire back to main panel

I am in the process of renovating a house that was built in 1933, and had an addition put on in the 1960's. Original 1933 panel is 100 amps. When the addition was put on, the electrical drop was ...
1
vote
1answer
138 views

Junction box above ceiling to add second sub panel from existing sub panel feed

I'm posting this question to determine if there is a safe manner to do this that meets code and isn't a redneck solution. The sub panel in my garage is run off a 50 amp breaker that is in my service ...
1
vote
1answer
106 views

Basement Sub-panel Breaker Size

I am confused about small-appliance branch circuit for service load calculation. I am trying to size my breaker for a sub-panel in my basement from my main 200A panel. I will have a main room, wet ...
2
votes
1answer
1k views

When did the NEC code start to require the separation of neutral and ground bus bars after main disconnect?

You gave the answer below to the question of the requirement for separate bus bars after the main disconnect box ... my question is ... In what year did the NEC start to require this separation? What ...
1
vote
1answer
70 views

Can I do subpanel this way?

I need 240VAC, single phase, 27 kW at 113 amps. Required breaker is 3 x 40 Amp I don't have enough space for (3) 40 Amp in my panel. Question is: can I kill 30 Amp (hot water heater) breaker and ...
3
votes
1answer
85 views

Adding subpanel to a shed

Thanks in advance for anyone providing insight for me. I apologize if answers for my situation can be found in another post that I've missed. I have a shed outside my home that currently has no power....
4
votes
2answers
482 views

What conductor and burial depth are appropriate for my garage subpanel circuit?

We are building a 2-story detached garage. The upstairs will be my wife's studio. She is a painter and quilter. The lower level will be a standard garage for tools, etc. I do not plan to weld but who ...
0
votes
1answer
28 views

Wiring a compressor to an external building

I have run 2,2,2,4 in conduit underground to a 100amp box. In the house the ground an neutral are bonded together but in the shed they are separated(isolated). I'm connecting a compressor through a ...
2
votes
2answers
39 views

Metal or PVC Conduit in Metal Outbuilding?

I'm running wiring under ground from main panel to 100 amp panel in metal garage. When installing lighting and receptacle circuits mounted against interior walls, does it make any difference what ...
2
votes
3answers
110 views

Turning 100A Main to subpanel of 200A new main

I have a 100A old-style circuit breaker main (~1970, 2 conductor & ground) in the basement. I want to upgrade the circuits in the garage to allow for solar panels and PEV cars, so my thought ...
1
vote
1answer
158 views

How to wire main feed in a tiny house subpanel for 120v and 240v?

Initially, I'm going to be plugged into basic 120v from an outlet. However, I'll be moving in a year, and want to be able to plug into 240v if available. How to achieve this flexibility in the ...
1
vote
1answer
209 views

Adding sub panel, odd main panel configuration

I am in the process of adding a sub panel to a detached garage and I have the proper gauge wire connected up to the sub panel (neutral and ground NOT bonded) with 3 conductors + ground running in ...
0
votes
2answers
69 views

Other than unforeseen surge in draw, what can cause breaker tripping?

My house originally had a single main panel, 150A. Some years ago, I decided to split the basement apartment and the main unit. The original main panel is in the basement but I wanted the main unit to ...
0
votes
1answer
123 views

Yes, I'm dumb - I drilled into wall backing my electrical panel

so... I was drilling into a wall and the drill was having a hard time. I figured I just needed to keep going and I did and it finally went through. Afterwards I realized my electrical panel was ...
0
votes
0answers
36 views

60A sub panel located 220' from source…in conduit..what guage al wire to meet ONT Elec code?

I want to wire a 60A subpanel that is 220' from the main source. The wire will be AL and run through a buried conduit.... Must meet Ontario Electrical code
2
votes
2answers
95 views

Powering Subpanel from CSED via Feed-Through Lugs

I'm wiring my house and would like some feedback on the sizing and routing of conductors between the exterior service entrance and an interior subpanel. On the outside, I have installed a combination ...
5
votes
2answers
1k views

Why does my subpanel have 4 wires feeding into the lugs?

Background: This is a sub-panel for my pool equipment (filter pump, cleaner pump, and pool light). The wires coming from the main panel come in through the bottom, and the wires going out the left ...
1
vote
3answers
495 views

Can I install a 60A main breaker in a load center rated for 125A?

Following my previous question about feeding a sub-panel... I have access to a new-in-box 125A load center, which is more current than I need, but the form factor is good. Can I drop to a 60A feeder ...