Why is this airduct twitching and making a noise?

I have an air duct in my basement. It leads from my furnace (I think?) to the outside world. However, as you can see from this video, it is "twitching". Every second or so it jerks slightly and ...
0
votes
0answers
22 views

I have replaced the fan motor and the heating unit in a goodman electric furnace

I need an easy wiring diagram for the motor and control board. where do the wires go from the board to the heating unit? I know the heat strip has a plug in but the old strip has a brown wire and the ...
0
votes
0answers
47 views

Can a Nest work in my setup (or am I stuck with Lyric, as they claim)?

Before crucifying me for the subjective question let me clarify that my question is quite specific if you read on. I bought an old home with bad insulation and a 55-year-old furnace 3 months ago. I ...
2
votes
2answers
1k views

Water dripping from outdoor HE furnace vent

Newly purchased home (December, northeast U.S.) has a high-efficiency furnace that vents to exterior of the house. When the furnace is on, the vent drips every few seconds, creating a puddle in the ...
5
votes
1answer
6k views

Why does my furnace only work after power reset?

I’m having issues with my furnace sometimes not kicking on. I hear the furnace start, But then it will not fire. However, If I go down to the basement and flip the power switch off and on the ...
2
votes
1answer
836 views

What kind of tubing should I use for draining condensate from a furnace / boiler?

"High efficiency" & condensing boilers or furnaces produce an acidic water byproduct called condensate that has to be drained away. My boiler has an outlet fitting for this condensate water but ...
1
vote
1answer
226 views

Finding the c-terminal on my furnace

I have a two wire furnace. I’ve been doing a lot of research but haven’t found anything super similar to what I have at my house. I’m trying to find where to connect the c-wire. I have a couple of ...
0
votes
3answers
83 views

Do HVAC technicians need to be registered or licensed? [closed]

We had several HVAC companies come out on a Sunday to look at our furnace. Unfortunately, it could not be fixed. Each contractor offered their solution and did not charge us for their time- but if ...
3
votes
1answer
98 views

York furnace not firing up correctly

I have a York TG9S080B12MP11A up-flow configured natural gas furnace. We have had the furnace since 2007. I am having an issue where the furnace is not starting correctly. When I power up the blower ...
1
vote
1answer
49 views

New primary control switch problems

About a week ago , I had someone to come in and replace my old RA116 stack switch with a Honeywell R8184G oil primary , for the first day it was fine, next thing I know the furnace turned off and ...
1
vote
0answers
83 views

Do I need to replace my pressure switch in my Goodman furnace?

We have a Goodman GKS9 Gas-Fired Warm Air Furnace. I've changed the air filter, cleaned the flame sensor, and checked the condensation pipes for clogs. They're clear. The behavior seems strange to me. ...
2
votes
1answer
159 views

What causes popping in new wood floor when furnace turns on?

I just had new solid wood floors installed and i hear popping where the floor meets my kitchen wall each time the furnace turns on (lasts for about 3 minutes). what causes the popping and how do I ...
0
votes
1answer
64 views

How do I create a C wire? [duplicate]

My furnace is old and only has 4 wire connections, but I require a C wire. How can I create one based on this diagram? I do have 5 wires running between the furnace and thermostat.
1
vote
1answer
751 views

How do you increase humidity with HRV system?

I’m wondering how to increase the humidity in my home. I have a venmar constructo HRV system and have looked at the manual and many videos and can’t find the answer. I’d like my humidity to be 35% for ...
0
votes
1answer
66 views

Is my furnace limit switch tripping due to a flawed coil installation?

I have two furnaces - one for each floor. One of the furnaces that were replaced within a year keeps blowing cold air randomly. I would reset it by turning the main power switch off/on and then it ...
1
vote
1answer
63 views

burners out of sequence with blower motor

I have a Bryant furnace plus 90 model #398AAW036060D. I just changed the blower motor. In the last five years I've changed the main board, inducer board, pressure switch, and cleaned the igniter the ...
0
votes
1answer
70 views

Home furnace not kicking on or staying on

I have a furnace question. Our house has an Amana furnace and it won't seem to kick on. For context, the temperature in the house is around 60 degrees or so. When setting the thermostat higher, a ...
1
vote
1answer
40 views

Wall grille that fits one step stair

Between my dining room and living room upstair area, there is one step down and there is a wall grille that is 5.5" tall. What drives me nut is there is no 14x5.5 grille anywhere. There is either ...
1
vote
1answer
217 views

Why is my thermostat turning the heat on too soon?

I have recently come across an issue with my thermostat and when and how my heat comes on. My thermostat seems to be an old round Honeywell. I set my temp at 65 typically. As of last night my ...
2
votes
3answers
9k views

Is it bad to close furnace dampers in order to balance temperatures seasonally?

I have a two story home. As such, it's always hotter on the second floor than the first floor. As advised by many articles and how-to videos out there, I usually close the dampers in the ducts leading ...
0
votes
1answer
185 views

Whole house humidifier when furnace is in unconditioned space

I have 2 furnaces, one in the garage and one in the attic. These are both spaces with unconditioned air, so they get very cold in the winter. The contractor who helped me configure my garage furnace ...
0
votes
2answers
70 views

Electric furnace doesn't perform a cool down stage

When my electric furnace shuts down the fan also shuts down at the exact same time. I was told that it should run for a bit afterward to cool off the coils. Doing some research it looks like this is ...
0
votes
1answer
233 views

Furnace getting power, but heat/AC not kicking on. LED on board is not lighting up. Thinking the transformer is gone

So far I've been successful in maintaining and repairing my own HVAC system in my house. First week we bought the house (we knew going into the purchase) I replaced the main board. It's been golden ...
1
vote
1answer
221 views

Furnace won’t stay running and when the blower motor runs it sounds like it is sucking up water

Part red arrow is pointing to keeps filling up with water and when the motor/fan (blue arrow) runs it sounds like it sucks up water and then furnace stops heating.
1
vote
2answers
180 views

Condensing furnace short cycling

I have a strange problem. I have an IPC/Tempstar T9MPD075F12A3 condensing furnace, roughly 12 years old. It uses a Honeywell SV9541M "SMART VALVE". EDIT: Just found the service manual, checking ...
1
vote
1answer
251 views

Connect C wire to Furnace

I have a Lenox Merit system in the house. I am trying to install Nest E thermostats and want to do it with a C wire. I noticed an unused Blue Wire (pic attached) at the thermostat location and then in ...
1
vote
0answers
288 views

Furnace not igniting with error E228

My furnace is Armstrong Air, A97USMV, today when turn on, the induce fan keep running but not ignition, then stopped with error code E228 (Unable to perform successful pressure switch calibration). ...
0
votes
2answers
70 views

How can I extend the length of my furnace run time after burner shutdown?

My new furnace has a control board with preset blower run times after thermostat satisfies. Max setting is 180 seconds. This is not enough to purge the latent heat in the heat exchanger. I need ...
0
votes
1answer
31 views

Electric Furnace, no AC, blower motor starts then slows after 1 second

I have an electric furnace 240V. The blower motor starts then slows and sounds like it is laboring after about one second. It does start at full speed, however. Does the same thing when in constant on ...
1
vote
2answers
2k views

How can I fix this furnace filter slot to prevent filters bending?

I noticed a problem with my furnace filter. In the vertical slot where it gets installed, there is a channel along the bottom but not along the top. As a result, the top corner of the filter ...
-2
votes
1answer
87 views

Payne gas furnace, model # PY3GNAA36090AATP. [closed]

Indoor fan blows continually, with 4 flashes on control board
0
votes
2answers
1k views

Can a pilot on a furnace be on but the thermocouple still be bad?

Heat just stopped working after working 3 days ago. All circuit breakers are looking good, gas is flowing, and furnace seems to be operating fine. Pilot is on and thermocouple is holding the flame, ...
1
vote
1answer
162 views

How long should electric furnace element last

I've been having elements go out in my electric furnace every year. Along with that, there's generally a burnt wire or two. Every about 2-3 years a sequencer goes out. Is this normal? I've been using ...
0
votes
1answer
59 views

Wall furnace burner not starting

My wall heater is not functioning. I had a similar post last year, and this year the problem evolved. Attached is the kind of wall furnace that I have. https://drive.google.com/open?id=...
1
vote
2answers
2k views

Do the doors on my utility closet need to be vented steel?

Our home is on a slab foundation, our furnace and hot water tank are in a closet. Currently we have vented steel bi-folding doors, I'm looking to replace the doors. Do they need to be steel and vented?...
1
vote
0answers
43 views

How to Run Fan Only with Thermostar Furnace With G Wire

I have a Thermostar Furnace that works great for Heating our home. We do not have AC and do not want that. But, we do want to be able to just run the fan without heat. The W and RH wires were ...
1
vote
1answer
71 views

Placement of evaporator unit on top of furnace (residential)

I am installing an updraft 3 ton system with the evaporator on top of the furnace. They fit nicely, but I'm not sure which front-or-back orientation the top unit should be in. In the attached ...
2
votes
1answer
334 views

How should the thermostat wires be connected to my furnace?

I have an Amana AMV90704CXBB furnace, and regular programmable thermostat. I took the furnace apart because I have to wash the blower motor wheel. It was covered in construction dust. In order to ...
1
vote
0answers
693 views

Where should I connect my C wire on Goodman GMP075-3 Rev.B

I am trying to install an ecobee4 to replace a digital battery powered thermostat. I removed the existing thermostat and found that there was a spare blue wire that was wrapped around the others that ...
1
vote
2answers
711 views

Is the ventilation in my utility closet a construction mistake?

With colder weather here in Northern Colorado (down to 22° F) my Goodman 90% efficiency furnace (GKS90453BX) came on for the first time in the (ca. 2005) home that I recently moved into. The furnace ...
1
vote
0answers
19 views

Do I need to replace the thermostat wiring leading to my boiler?

I have a boiler in an old building with four different apartments. There are two thermostats that call for heat from the boiler, and valves that direct the hot water to the respective part of the ...
0
votes
1answer
2k views

Pilot Light keeps going out when thermostat is kicking on furnace

So I have had furnace man come out 4 times, plus the Gas company. Here is what has been done: - New thermocoupler - Two new gas valves - New Orface and line blown out - Gas company changed gas valve ...
0
votes
1answer
48 views

rewiring a furnace for an inside fan

I have a Outdoor AC unit that has an A-coil in it, so it pushes all of the air from outside through huge duct work and into the ventilation, which by the time it gets to the last room its extremely ...
1
vote
0answers
972 views

Lennox furnace 3 flashing lights

Have a new construction house, and lived here about 2.5 yrs. Turned on my furnace last night worked fine. This morning, it kept turning on then kicking off with no burners coming on. I noticed the ...
1
vote
0answers
180 views

Furnace draft inducer switch tripping

I have an older furnace and a brand new natural gas instant water heater that I installed. I only start this way because the furnace had one thing break last year, so I'm not sure if things on it are ...
1
vote
2answers
9k views

Where do I connect a C wire in an old Furnace?

I am hoping to be able to upgrade to a smart thermostat but unfortunately my furnace doesn't have the "easy" option with an obvious C terminal. My furnace is OLD but it actually has the full 5 ...
0
votes
2answers
376 views

Connect Wifi Thermostat to Goodman GMP050-3?

I'm trying to connect up a wifi thermostat to Goodman furnace, specifically the GMP050-3. I've done some reading on this but I'm still not quite sure how to go about it. Specifically, I'm not sure ...
1
vote
1answer
1k views

Hot water heater T&P discharge going into furnace condensate pump?

I recently had some electrical work done at my house, and as part of that, the power was shut off. After a few minutes, we noticed water coming from the closet containing the hot water heater and ...
0
votes
0answers
81 views

Proper way to seal attic space from the living space

I am living in a one-story house with flat roof. There is an 2-feet-high empty space above the ceiling and below the roof, and let me call it my attic space (although my house has a flat roof). The ...
0
votes
2answers
64 views

Are air vents in a house intended to let some air through when they're closed? Would it be bad to completely seal it?

I would like to be able to use the vents in my house in a way that targets specific rooms/areas more than others. Sometimes I want to completely close off a room from being temperature-regulated by ...