I moved into a home recently and found the old thermostat temperature controls to be inaccurate at turning on and turning off A/C as set so I purchased a Honeywell RTH6580WF thermostat as a replacement. The current thermostat is an old Honeywell round mercury bulb model. In attempting to replace the current thermostat I found that I need a C wire for the new thermostat to work correctly, although my old thermostat only had G, Y, W, and R wired up. I read more into this issue and found that I should be able to take the G wire and move it to the C on the new thermostat as well as at the furnace, and then place a jumper from Y to G at the furnace and that should take care of it.

The problem I run into is that the Y slot on the furnace is empty and I have a wire in the C slot on the furnace even though there wasn't one at the old thermostat. I've since discovered that the A/C compressor is wired in at the furnace as well, with the Y from the thermostat and the Red cable from the A/C compressor twisted together with a wire nut, and the white cable from the A/C compressor going to the C slot on the furnace. I spoke with Honeywell support on the phone and they said I'd need to have an HVAC contractor come out to resolve this issue, saying I would not be able to use the new thermostat with the current wiring situation. (I've included a diagram of the current wiring setup.

My idea is that I can run new 18/5 thermostat wire (current installed wire has only 4 wires) and then wire up the new thermostat from thermostat to furnace as R-R, W-W, Y-Y, G-G, C-C and then instead of twisting the Y from thermostat with the red wire from the A/C compressor I can just put two wires on the Y on the furnace and also have two wires on the C on the furnace, with the second of each coming from the A/C compressor. I've included a diagram of this hopeful configuration. I'm not sure if this is the proper method and I haven't been able to find anyone with the exact same setup to verify so I thought I'd ask for anyone's assistance on this. Does that sound like the best solution? I appreciate any guidance with this. Thank you very much for your time.

Old Thermostat Wiring New hopeful Thermostat Wiring

1

Yes, that should work just fine.

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.