What size aluminum wire for a new 60 amp garage panel to be fed from a 200 amp main service in my house 130' distance? How many wires?
  • Attached or detached garage? And are you running a cable or wires in conduit? Commented Jul 9, 2016 at 14:04
  • Assuming US/Canada, 4 wires for standard 120/240VAC service. Hot, Hot, Neutral and Ground. Neutral and ground isolated under current code.
    Commented Jul 9, 2016 at 16:09
  • The garage is unattached. The wire run is 30' through he house rafters, then 22' outside the house in conduit, 10' drop into the ground, 50' underground in conduit, and then 8' up from the ground in conduit and into the new garage panel box.
    – Joe
    Commented Jul 10, 2016 at 3:55
    If you are running 60A wire and a 60A breaker in the main panel, feel free to upsize to a larger sub-panel, which will give you more breaker spaces. The 60a breaker will continue to protect the wires, and a 100A sub-panel can obviously handle 60A. The "main" breaker in the sub-panel can be ignored. Commented Jul 10, 2016 at 21:54
Number 4 aluminum is good for 65 amps at 130' the voltage drop at 60 amps would be 2.55% . Up to 3% is allowed by code.