What size aluminum 3 wire should I use to run 200 feet underground at 100 amps 110/220 volts? This is in Colorado and will be used to run a mobile home with an electric dryer as the only 220 volt appliance.
1 Answer
It can only be 3 if this is the service drop - if it's a sub-panel it needs to be 4-wire.
3/0 (000) should do it. There are MANY voltage drop calculators on the web, as well as tables/charts. I happen to like the one linked, but they are mostly similar and should all give similar results. Shoot for 3% or less drop at rated (or calculated) load. I added 10 feet to account for getting the wire in and out of the ground, rather than just the horizontal distance - wire length, not "as a bird flies" is the number that matters for length.
I prefer to allow for the full load (100 amps) rather than attempting to finesse 30A 240V dryer + 120 volt loads unknown; I've lived with an undersized feed and I'm not fond of self-induced brown-outs.
-
1If this is for the main service to the home then IMO 3/0, even AL, is a bit big. No need AT ALL to go that large. Knowing the calculated load would be a big help, as opposed to simply using 100A, which is quite unrealistic. Jul 4, 2016 at 14:12