I am replacing a receptacle (15A) and it has three hot and 3 neutral wires. Previously two backstab plus one screw were used on each side. I won't be using the backstabs on the replacement receptacle.
My question is: Do I have to use all four hot and neutral screws or can I simply pigtail all three hot and connect to a single hot screw? I'd do the same for the neutral side.
In this configuration I'd have only three leads going to the receptacle (including ground) instead of 7.
  • It would depend on the size of the box (total wire fill) You may be able to add an extension to the box but this sounds like a 2x4 outlet so the total wire fill and device would be larger than the the box is rated for. I will pig tail every time and NOT use back stabs but the total cubic inch size of the box will tell if this is close to legal or not.
    Jul 4, 2016 at 0:12
  • Yeah, it's a 2x4 box... Was pretty tight to begin with. I may go and get a receptacle that I can back wire... So pigtailing the hot and neutrals to one screw each is a valid approach?
    – Eric
    Jul 4, 2016 at 0:17
  • The box fill is based on the device and the wires in the box even with a deep 2x4 I am sure you need more space a box extension won't work with a in wall 2x4 but you could upgrade to a 4x4 old work box with a mud ring, this will require a bit of cutting and some Sheetrock mud to cover but then it could be legal. Some 2x4 or single gang boxes are able to be joined together making a double gang but then a blank plate would be required and mud similar to a 4x4 with a mud ring.
    Jul 4, 2016 at 1:29
Use pigtailing here -- the Code doesn't charge for pigtails in the Article 314 box fill accounting. However, by Article 314, your box is already overflowing -- so put an extension ring/box on it while you are at it. (You need to get the box's rated volume up to 18 in^3 to fit everything in, or 20 in^3 with internal clamps)