Bought a receptacle tester, most outlets are good, not sure how to read the outlets that have switches.

Outlet 1: tester reads good, when I turn the switch off it reads open ground.

Outlet 2: tester reads open ground, changes to open hot when I turn switch off.

What should it say when I turn the switch off?

  • I suspect you have an XY problem here -- your Y is what the receptacle tester is saying, your X is how to get your outlets to behave :) if you want help cajoling the outlets into proper operation, we'll need photos of the insides of the switch and outlet boxes (turn off the power at the breaker panel first!) – ThreePhaseEel Jun 18 '16 at 4:27
  • Will post some pictures this week. – Frank Jun 20 '16 at 0:11
3

In a switched outlet, the following is correct:

  • Switch on = normal (2 yellow lights)

  • Switch off = "open hot" (no lights at all)

The yellow light that comes on for "open ground" indicates whether an appliance will have power in that outlet. As you might guess, it is connected between hot and neutral.

The other yellow light is connected between hot and ground. It'll light if ground is good, but it'll also light in a number of nasty failure situations - Check out this link.

The red light is hooked between neutral and ground. It should not light because there should be very low voltage (not zero) between neutral and ground.

For outlet 1, the "appliance power present" light is always on. That says the switch doesn't work. It doesn't turn off power when you turn it off. It does seem to interrupt ground -- what the heck??? Can the switch be switching the ground? That's a very, very weird situation and I suspect you have a problem that exceeds the ability of the outlet tester. It's possible someone didn't want that outlet to be switched, and rearranged wires until it wasn't. Put it back. Or at least put the grounds right.

For outlet 2, it sounds like normal behavior if the ground is not connected.

I think it's time to shut off the breaker and pull the receptacles and switches out and have a looksy. If that isn't comfortable to you, then hit a library's home electrical repair section and school up.

2

The tester should read open hot when the switch is off, as switches always go in the hot wire -- it most certainly shouldn't read open ground with the switch off!

This means that Outlet 1 is quite dodgy in some fashion or another, while Outlet 2 likely either lacks a ground or doesn't have it hooked up.

  • That makes sense, obviously the one outlet needs to be looked at. It was giving us some weird problems when trying to hook up a Playstation 3 console and that's why we bought the outlet tester to begin with. 2 fried tvs and 2 fried cable boxes niw but no issues except for when hooking up a Playstation. – Frank Jun 19 '16 at 23:58