10

This is not a question about whether it is in code, or safe to wire a 110 outlet with its neutral to the ground of a 240 circuit. I accept that it is unsafe, and it's certainly not up to code, I'm trying to get my head around what makes it unsafe. What exactly could happen with this type of bad wiring?

4
  • Is the 240VAC circuit one without a safety GND?
    – Michael Karas
    May 22, 2016 at 20:07
  • 1
    3 wire 240. One being ground, the other two being hot from each pole of the panel. May 22, 2016 at 22:48
  • Possible duplicate: Can I connect ground to neutral in a 3 wire outlet?
    – BMitch
    May 23, 2016 at 3:24
  • 1
    Is this "3 wire 240V" going to a dryer or range? That's not a ground, that's a neutral. That uses the "NEMA 10 loophole" to bootleg ground to dryers and ranges. It's leeeegal, but is still bootlegging, and unsafe for below reasons. Mar 28, 2018 at 16:27

4 Answers 4

11

Neutral is not ground. Neutral is the desired current return, ground is a safety device only.

Let's look at some fault conditions, and we'll lead up to the problem with the bootleg ground. First, consider a broken neutral wire (near the service panel) with no loads on the circuit whatsoever.

enter image description here

Nothing is connected to the neutral; it's floating. That's not the same as being at zero. Nothing pulls it down to zero (neutral) but nothing pulls it up to hot either.

But what if something did?

enter image description here

This is concerning. You see the broken neutral is being pulled up to 120V. Not toward 120V - all the way, because absolutely nothing pulls it down to real neutral. This is deadly if you have a NEMA 10 dryer or stove circuit, where they intentionally attach chassis to neutral as a substitute for ground. But other than that, this situation is not that hazardous if everything is perfect and to code, and probably wouldn't even trip a breaker. And since neutrals stay with their mated hots, this problem is contained to a single circuit.

Now to your hypothetical: a bootleg ground. Same, but substitute ground for neutral.

enter image description here

Holy smokes! We've now lit up every ground downstream of the break. Unlike neutrals, grounds may be cross-connected, so it can affect every circuit. Every screw in every outlet cover, any metal conduit, any appliance which properly grounds its chassis (particularly NEMA 14 connected dryers and stoves), the exterior of your metal power strips, maybe even the chassis of your PC.

In fact a single point of failure - the ground-neutral bond in your main panel - combined with a bootleg ground, will create the worst case scenario: energizing every ground in your house including the service panel itself.

Other than that, I see ground breaks all the time - especially in EMT conduit, where those flimsy zinc couplers can snap off.

Here's why the grounding rod won't help. Dirt is a lousy conductor, except when it's not. Grounding is done to force the house's ground system (and neutral) to be near earth, to reduce shock hazard. It's not meant as a current return, and it works so badly as one, that using it that way creates the hazard!

enter image description here

Power wants to get back to neutral, not ground. The only place ground can reach neutral is back at the transformer pole, and that current path goes through unreliable dirt. Code says a single ground rod must be 25 ohms (but if you have two, you don't even have to test! This is because of the practical difficulty of getting good earth connections in some places.) Run the math: E=IR, 120V=4.8A*25Ω. In other words a dead short would flow 4.8 amps. That's not going to trip a breaker, and can't be counted on to reduce shock hazard from that bootleg ground. The bootleg load could be considerably less than 25 ohms, so it's going to pull ground up toward 120V better than earth may pull it down.

I know it's a busy drawing, click to zoom. Here's what else is going on there: High voltage 3-phase delta (yellow orange brown) feeds a single-phase neighborhood transformer, whose secondary is 240 volts center-tap. The center tap is Neutral, and it's bonded to a grounding rod at the transformer. Those 3 wires, hot-neutral-hot, are bundled together and carried to each house via its meter. Each house has a grounding rod bonded to ground, which is also bonded to neutral in the main panel.

6
  • 1
    Let's say you have a long extension cord and as a result you have 114V at the load rather than 120V. Hot-neutral will be 114V. Neutral-ground will be 3V. Hot-ground will be 117V. Ground is not in parallel with neutral. Ground is not connected except in a fault condition. Ergo it does not suffer voltage drop. May 23, 2016 at 0:16
  • 1
    It doesnt, I just use it to drive home "ground is not neutral" because it's so common for people to get stuck on "ground is neutral" once they see that bonding wire in the panel. My second paragraph is a hard concept, but it is the crux of the matter. This tends to confuse even the experts, as it is counterintuitive. I disagree with the effects of no load, but as long as you grasp that the broken neutral will immediately float up to 120V, you have the crux. May 23, 2016 at 1:00
  • 1
    If I read your answer 10 more times I think I might understand it. I'm about 80% there. If I understand what you are saying as much as I think I do, it seems like dropping a grounding rod at the outlet would improve matters to some degree if the ground was lost somewhere closer to the panel. I'm sure that's got issues too.... May 23, 2016 at 1:14
  • 2
    @GregTaylor a ground rod will not help. Electricity is trying to get back to the source, not to ground.
    – Tester101
    May 23, 2016 at 3:15
  • Does this mean if I have a bunch of 15A space heaters and they are all on the same phase, all of that current is coming in through the left bus, through the load, back to the neutral bus, into the grounding rod, through the earth, back to the transformer neutral? Isn't that like adding a 25Ohm resistor in series to the load, and wasting a ton of power? May 7 at 14:36
4

Electricity follows every available path back to the source. If you connect neutral to ground, you're putting current on the grounding conductor. This includes conduit, boxes, device chassis, enclosures, bare (uninsulated) wire, etc. If a person comes into contact with any of those devices, they can become a path as well.

This can lead to injury, and/or death.

1
  • 2
    Tester is 100% correct , Code calls this objectionable current. The requirements in this area have not changed for quite a few code update cycles.
    – Ed Beal
    May 23, 2016 at 2:59
4

The risk of a bootleg ground is that grounded devices can become energized and potentially lethal to touch should the neutral connection ever fail or simply have too high of a resistance.

To give a sample scenario, suppose you have an electric heater on a circuit that uses a bootleg ground. And downstream of that bootleg, the neutral goes through an old outlet where the neutral connection finally fails in a chard mess that luckily doesn't light the house on fire. The heater stops working, you pick it up to see if you can see why. And to get a better look, you flip the light switch. When you touch the screw on the light switch, you have up to 120v and a whole lot of amps going in the hot of the heater, out the neutral, through the bootleg ground connection, back out to the grounded metal casing of the heater, through your body (eek), and back out to the grounded screw on the light switch.

2

The whole point of grounding devices and other conductive parts inside an structure is to establish effective ground fault detection. Circuits normally feed multiple appliances and while not readily obvious, rely on a clean, zero potential reference to ground in case an actual fault to ground occurred.

Why this is really dangerous

The obvious reason is someone can get shocked, especially electricians working on the system. This is because a non-current carrying conductor ( the ground ) is now carrying current on a regular basis for which it is not designed to do.

7
  • 1
    I'm looking for specific examples of what the dangers are in this scenario. If x happens, then y could happen because of z. May 22, 2016 at 22:50
  • 1
    Updated. Hope that helps!
    – Kris
    May 22, 2016 at 22:54
  • 2
    @Kris - You are aware that GFCI's detect current flow differences in the neutral line versus the hot line through them. If an appliance or fixture has a short or leakage path to the safety ground then that will likely imbalance the current in the hot/neutral pair through the GFCI causing it to trip.
    – Michael Karas
    May 22, 2016 at 23:59
  • @Michael Karas, correct. The current transformer in a GFCI measures the load side of both conductors which should be equal, if not then it trips. I will modify my description to be more clearer.
    – Kris
    May 23, 2016 at 0:06
  • By the way, why are you telling answerers that they are right or wrong? It lends the impression that you think diy.SE is a quiz game. May 23, 2016 at 0:41