I'm trying to install a wifi thermostat and it won't power up. The old thermo was battery operated 2 wire but there were spare wires. At the R845A relay, red and white whites connect to terminals 5 and 6, red and white also connect to the 2 T terminals. I ran a jumper connecting the blue (common). In the relay, I get 24 volts across 5-6. and 24v between the white wire and common. 0v between red and common. At the thermostats I get 4-10 v between red and common,14v white-common, and 24v r-w. As I say the thermo doesn't work and any help will be greatly appreciated. relay and transformer
    Did it work with connecting common to rear of transformer, or did you have to get different relay?
    – DaFish
    May 3, 2017 at 2:39
According to this document, the internal wiring of that relay looks like this.
Honeywell R845A relay
It sounds like it's connected something like this.
Relay circuit
When the thermostat calls for heat, the T terminals are connected through the thermostat. This causes the relay to energize, which closes the contact between terminals 5 and 6 (It also closes a contact between 3 and 4). When terminals 5 and 6 are connected, the heater, pump, valve, etc. turns on.
Current flow through relay
Because the transformer is built into this device, it's going to be difficult (possibly impossible) to connect a C wire. You'd have to connect the wire to the other side of the transformer, something like this.
C wire connection to Honeywell R845A relay
You'll also have to check with the manufacturer, to determine if the transformer can handle the additional load of the thermostat.
You might want to contact Honeywell, to see if they offer a similar relay that exposes the C terminal. If they do, you could replace this device with the one with the proper terminals.
What you're trying to do, is something like this.
Bad wiring
Which as you can see in the diagram, is not going to work so well.
    I was able to get this working over the weekend. I removed the board and soldered a jumper wire to the back side of the transformer as indicated in the fourth image above. I connected the C wire to the jumper wire using a wirenut. I have photos but unfortunately I don't have 10 reputation points so I cannot post them.
    – user24601
    Oct 3, 2017 at 1:39
  • @user24601 You should post your photos, and the steps you took, as an answer. It could help somebody in the future, who is in the same situation.
    – Tester101
    Oct 3, 2017 at 10:39
  • I would love to. However, it appears I'm prevented from answering this question because it is protected and I do not have enough reputation. I could post a new question, reference this one, and answer that. Do you have other ideas? Thanks.
    – user24601
    Oct 3, 2017 at 11:46
    @user24601 FYI I happen to be the hypothetical person trying to do the same thing :) Though your description in the comment may be enough to go no. Thanks Dec 25, 2018 at 18:17
    @AlmostSurely I did what is shown in the other answer (diy.stackexchange.com/a/153387/41781) - and its worked great since then. Nov 18, 2019 at 18:15
I had the same problem with the same model switching relay and following the encouraging description given in a comment on Tester101's answer, made the same modification to expose a connection which provides the 'C' terminal.
This is shown in the photo below. This is a view of the rear of the modified back of the circuit board (not normally visible without disassembly):
The green insulated wire is the addition, which now provides the 'C' connection. It is connected to the second terminal of the 'secondary' side of the transformer so that it always provides the necessary return path for the low voltage circuit. Conveniently it fit through an existing opening in the board, passing by the contactor.
(Yeah, my soldering is kind of ugly).
The transformer is actually labeled "PRI" and "SEC" which was helpful. (Only "PRI" is visible in the photo).
I tested this with a Honeywell RTH8500 thermostat and it works correctly.
CAUTION #1: This thing has live 120V power to it. Make sure the power is off when working on it.
CAUTION #2: If you wired it wrong, you could run 120V to your thermostat by mistake. This could cause damage or injury. (I tested all the voltages before any wires left the box to the rest of the house, and I've done lots of DIY electrical work before so I was confident with this one.)
    Thanks - finally implemented this today. Something to be aware of should anyone else care to try it is my transformer was rotated by 90 degrees. It also lacked a backplate with labeling like yours, but I was able to see the windings as a result to determine the secondary side. Nov 1, 2020 at 16:10