I would like to wire multiple motion detector light kits in parallel, so when one motion detector is tripped it will turn on all three lights. Each light kit has 2 LED lights on it. Schematic and text description below.schematic below

2

That looks fine. Only thing is, every motion detector I have seen only has one white, and all the whites (neutrals) get spliced together.

At the motion detector:

Black hot in - MD black

Blacks from the two lights - MD red

ALL whites in the box together

  • The only problem I can think of is if the motion detector switch can't handle the combined power of more than one set of lights. – batsplatsterson Dec 22 '15 at 23:24
  • Only the cheapest of MD heads would be that limited. RAB Stealth are good to 1000 watts. Even most cheaper heads I have seen were good to 500W. – Speedy Petey Dec 22 '15 at 23:25
  • If you did have a need to switch more load than the MD relay can handle (not likely with 6 LED lights) or if you wanted multiple motion detectors to turn on the lights, you just add a relay to the system that can handle the load, and the MD red wire powers its coil. – Ecnerwal Dec 23 '15 at 5:01
1

Another much broader question was marked as a duplicate to this one, so I'll provide a general answer here. But first, the specific:

In your drawing, note how the supply neutral (lower) is separate from the internal "neutral" (upper). That's a red flag: Likely it's 12 volts DC. These preassembled lamps often use 12VDC internally since the LED heads require it, and 12VDC motion sensor modules are much cheaper than 120VAC ones. So you'll have to test the lamp assembly further to see if it's adaptable.

Many lamp makers don't make sensors or even lamp heads. They kit together common off-the-shelf parts, commonly seen on Alibaba or eBay. If the sensor part doesn't work for you, and you can bypass the sensor and make it an "always on" light, there's good news. You may be able to replace the sensor - many screw into fittings like this, and then proceed as I describe below.


Generally:

I use separate detectors from lamps (they could be in the same assembly), and here's how I wire them.

First, I use the type of sensor which has its own neutral (rather than the type which has no neutral and sits in a "switch loop".) This is very important. The sensor needs to be able to power itself independently (via hot and neutral) and does not care what is on the output. That means it won't interfere/clash with other sensors.

I run 4 wires down the length of all the sensor and lamp sites. The 4 wires are:

  • Green - Equipment Ground
  • White - Neutral
  • Black - "always hot"
  • Orange or Red - "switched hot"

enter image description here

I connect ground, neutral and always-hot back to power supply at the service panel.

I attach each sensor to always-hot, neutral and switched-hot.

For a plain switch (pictured in position 5), use always-hot and switched-hot. It does not need neutral, but Code requires you bring neutral to the junction box.

Each lamp gets switched-hot and neutral. If the far end of the string is all lamps, you don't need an always-hot.

Grounds everywhere grounds go.