I needed to run some Cat5e UTP network cables and decided to add network outlets to most rooms, run new phone wiring and RG6 as well.

Much of what I've seen and read about residential and small office installations doesn't mention grounding much but I know that in the data center It's an important consideration. I called a local antenna installer (the only one I could find) to have them move an attic antenna to the roof and they said they don't recommend grounding the antenna. I'm a bit confused by both the lack of information and conflicting information. The bits I've seen on the TIA residential spec didn't mention grounding.

All the cables will be terninated on a plywood panel in the basement with 2 small wall mount racks. One for patch panels (coax and cat5e) another to hold a network switch. Cabling is cat5e UTP for data and phone. Coax is RG6 with 2 seperate runs, one for commercial tv provider, other for an attic mounted antenna that I'd like to eventually move to the roof.

Is there a requirement (USA NEC) to bond these racks, and the equipment in the racks?

If it's not a requirement are there good reasons to bond this equipment?

How would you recommend grounding bonding this setup? The current drops from providers are properly grounded.

In larger data centers I've seen those big copper grounding bus bars which seems like overkill. In smaller installations I've seen small aluminum(?) grounding bars that look like the ones in electrical panels. From there ground wires connect between the block/bar to the racks and then the racks are connected to patch panels and other equipment with ground wire and grounding lugs.

Where can the other end of the grounding conductor go? People have different opinions of what the code states. Some have said a separate ground rod, other's have tied it to all sorts of things including steel building structure, water pipes, electrical conduit....

This is what's available to me where I'm mounting my equipment.

A) Lots of copper cold water pipe on the house side of the water meter. Main line is underground copper that runs at least 10' in ground. This would be the easiest/cheapest. I know in the past the cold water line (house side) was at least once used to ground the incoming phone service.

B) Some armored cable (old 2 conductor where armor is grounded)

C) The street side of the water meter is a bit further away and a little difficult to get to but possible if necessary and less than 20' of cable run to it. Thre's a ground wire on the street side of the meter for the electric panel but I think there's also another ground wire going outside from the panel.

D) Main electrical panel. The wire run would be greater than 20' though.

The above is just to illustrate what I "know" (think?) and what I have available.

  • @Tester101 I'm not sure if it's required either and that's a big part of why I'm posting the question. NEC has codes for safety and I think those are covered with proper incoming service grounding done by providers and proper equipment grounding through 3 prong plugs. Other standards aren't required but recommended to protect equipment and increase uptime. TIA-607-B wants you to bond everything that comes in contact with cabling (including UTP) from racks to each individual section of ladder racks. If I can get better equip protection with just 20' of #6 THHN and some lugs seems worth it? – OrganicLawnDIY Nov 3 '15 at 2:24
4

This is a bigger can of worms than meets the eye. There are huge arguments over all this.

This is a coax grounding block:

coax grounding block

This is a grounding bar:

grounding bar

This is a grounding bridge, your cable company or telephone company probably has one on the outside of the house at the electrical service entrance:

grounding bridge

What I'd do:

  • Run a ground cable from your frame to the grounding bridge. Use the biggest cable that will fit properly in the bridge. Don't use A-D above.
  • Install a grounding bar that will handle that wire, at your frame in the basement.
  • Run a ground wire from your metal patch panel rack to the grounding bar, use grounding lugs on the rack. Probably not necessary, but use Noalox between the lug and the rack. Remove paint if you want to go all in.
  • Install and ground coax grounding blocks for your antenna and CATV service.
  • Use good quality surge strips, at the frame and through the house, and check your outlets with a receptacle tester to make sure they have ground wires - surge strips generally don't work without a good ground.
  • If any of your equipment has a grounding lug on the back, ground it. (For example, many of the Netgear metal cased switches have a ground lug on them.) AFAIK only necessary on equipment with a two wire power plug.
  • Remember, holy wars over all this - some will say this is all totally wrong. This is what I would do though after following all the arguments.

Edit:

There is a good chance your patch panel doesn't ground the coax that goes through the house. However if you use surge strips that have a coax port in those places, and the coax has been terminated properly so the body of the plugs are bonded well to the shiled, and the outlets those surge strips plug into have a good ground, you should be fine.

One last thing - this whole thing hinges on good grounding of your electrical system. If you want to be really careful there, have an electrician check the grounding and bonding and if possible ground resistance. This is IMO worth doing in general.

  • Thanks. Any chance you can summarize some of the arguments for and against doing it this way? Most of what you said is inline with TIA-670-B down to the use of the anti-oxidant compound and scraping paint except. I'm not sure that I have a grounding bus outside but I know there is a coax grounding block. All my coax will soon be indoors and I might have to set up a new grounding bar to act as the TMGB (telecommunications main grounding busbar) that will be tied to the electrical system ground. Need to find a local electrician with good understanding of telecommunications standards. – OrganicLawnDIY Nov 3 '15 at 16:16
  • 1
    Look at how the lug at the end of the grounding bridge is open - that's so you can clamp it right on the ground for your electrical service without disturbing that wiring. (As long as you don't tighten it like a gorilla, tight enough is tight enough, don't destroy the conductor!) – batsplatsterson Nov 3 '15 at 19:00
2

You don't need to ground UTP wiring... in fact there is nothing to ground on it. (If you were using shielded twisted pair wiring, STP, that's a different story).

Any network equipment like switches that needs to be grounded will have a 3rd pin on the power plug and ground itself. That will probably also ground the metal switch rack if the switch chassis is metal, but again the network cabling does not have a ground so it's not really important.

Unless you are having a problem I wouldn't worry about it. In a residential setting it's extremely unlikely you will ever saturate the bandwidth of CAT 5e. If you want to give yourself a little bit of extra headroom you could use CAT6 for a few dollars more but it's probably not worth it.

As for code requirements, I don't believe the NEC covers any low-voltage stuff. If your equipment has special requirements you could follow those but again a standard ethernet switch is just going to ground the chassis through its power cord.

EDIT: my answer is exclusively about twisted pair (CAT5/6) cabling and the associated network hardware. I maintain that any sort of grounding beyond using standard 3-prong plugs where applicable is unnecessary in a residential setting. Coax cable is a whole different story, since unlike UTP cable it does have a shield around it. Grounding at the service entrance should be provided by the utility.

  • TIA/EIA put out a bunch of specifications on grounding. Most recent being ANSI/TIA/EIA-607B where they want you to bond everything, including ladder racks with just UTP and even any conductive material within 6'. Not just for safety but also to protect equipment. Wondering if there would be benefits to do it at home too since it looks like it wouldn't cost too much. If I do bond everything I want to make sure it's right. – OrganicLawnDIY Nov 3 '15 at 2:32
  • There's really no need to use STP in a residential structure, it won't make the network any faster (go for CAT-6 or CAT-7 for that (which will also help somewhat with noise resistance)), and there's rarely enough electrical noise in a home environment to make STP worthwhile. Plus, there are few home installers that have enough experience with STP to install it properly, STP has more stringent guidelines on bend radius & pulling force, and more complicated terminations. Violating the bend radius could crimp the shield and make the cable worse than if UTP were just used in the first place. – Johnny Nov 3 '15 at 4:19
  • @OrganicLawnDIY: I think you are overthinking this. If your switch has a grounding 3-prong plug, use it. Otherwise there's nothing to ground. – Hank Nov 3 '15 at 5:00
  • I want to set up my network as close to data center standards as I can. My switch not only has a 3rd prong but also a ground screw to attach to data center grounding network.Tester's answer describes well how it's normally done. – OrganicLawnDIY Nov 3 '15 at 17:31
1

I'm not going to focus on whether or not you should do this, instead I'll focus on how it's supposed to be done.

Telecommunications Entering the Building

The telecommunications systems should be grounded where they enter the building, which will likely be handled by the utility. The utility will use the intersystem bonding termination; or other means, to bond the utility lines to the electrical systems grounding electrode system.

If this is not done. You can do it yourself, or ask the utility to do it for you.

Antenna

The mast for the antenna, should be bonded to the intersystem bonding termination (or other approved location) using a 10 AWG conductor. The coaxial cable from the antenna should be connected to an Antenna Discharge Unit, which should be bonded to the intersystem bonding termination (or other approved location) using a 10 AWG conductor.

Telecommunication Systems Within the Building

If you're looking to ground telecommunication systems within your home, you'll want to aim for something similar to this.

Telecommunications Bonding

The rack will be fitted with a Rack Grounding Busbar (RGB) or Rack Bonding Conductor (RBC), which the rack and all the equipment will be bonded to. The rack and equipment should be bonded to the RGB or RBC using 12 AWG Bonding Jumpers. The RGB or RBC will be bonded to a Telecommunications Grounding Busbar (TGB), via a 6 AWG Telecommunications Equipment Bonding Conductor (TEBC). The TGB is bonded to the Telecommunications Main Grounding Busbar (TMGB), using a 6 AWG Telecommunications Bonding Backbone (TBB). The TMGB is bonded to the Intersystem Bonding Termination (IBT), by way of a 6 AWG Bonding Conductor for Telecommunications. (BCT). A 6 AWG Bonding Conductor bonds the IBT, to the electrical systems Grounding Electrode Conductor (GEC). The GEC is connected to the Grounding Electrode.

Since you're in a residential application, you're probably only going to have one or two racks. Because of this, the system will likely be a bit less complex. Your system will probably look closer to this.

Residential Telecommunications Bonding

Since you said your equipment will be farther than 20' from the electrical systems grounding electrode system, you're probably going to have to install a separate grounding electrode for the equipment. This electrode system will have to be bonded to the electrical systems electrode system, using a 6 AWG Grounding Electrode Bonding Jumper.

Residential Telecommunications Bonding with Telecommunication Electrode

  • Thanks. This is along the lines of what I'm looking for but I'm not going to wall mounted racks (a small patch panel rack and vertical rack) mounted on a plywood panel. Want to make sure I'm translating the above properly for that type of setup. One of the few mentions of grounding a small installation like that is in this video to give you an idea. think it just may be a matter of using smaller grounding bars mounted to racks (paint scraped) and then using the same gauge wiring and connections. – OrganicLawnDIY Nov 3 '15 at 17:06
  • The size of the "rack" doesn't matter, it's still grounded the same. In the video, the TEBC is attached to the patch panel, and runs down to a TGB (or TMGB). From the TGB, there's either a TBB or BCT running up into the ceiling. If you had two similar "racks", you'll just ground them both to the TGB using 6 AWG wire. – Tester101 Nov 3 '15 at 18:43
  • I know the answers to these questions may seem obvious but I just want to be certain. I mentioned the size because using rack specific bonding equip will take up rack space. There's no back rail to mount a 19" RGB as pictured. I'd have to use something like the ground bus in @batsplatsterson answer on the rack as the RGB. Then a lug to rack and each patch panel with jumpers. In the video the didn't set it up to be able to run a bonding jumper to the patch panel which seems odd since they took the time to run the TEBC in the first place. – OrganicLawnDIY Nov 3 '15 at 19:22
  • You don't have to use a horizontal RGB, there are also vertical RGBs. You can simply run a 6 AWG bare copper wire vertically down the side of the rack, then use connectors to attach the bonding jumpers to it. Just don't forget to also run a bonding jumper to the frame of the rack, as well. – Tester101 Nov 3 '15 at 19:42
  • 1
    I have a fairly good understanding of what needs to be grounded it's how to attach to my equipment and how to bond it to main ground. If you say bare wire can be used then I should be good with any approved grounding devices such as lugs, blocks and buses. Just need to drill holes and scrape paint. Ignore the antenna as it might stay in the attic so it never "enters the house" or it will be grounded separately if I put it on the roof. Now that 20' restriction goes away and I can use whatever length ground wire I need for network so can run it in the basement to the panel right? – OrganicLawnDIY Nov 4 '15 at 1:17
0

Before you ground large metal structures on your roof to Earth, consider not just code, but consider why lightning happens. Electrical potential develops between the sky and the ground, and it will find the easiest path it can to discharge, even if that means breaking down hundreds of feet of air into plasma!

If you are putting a large surface area on your roof, particularly with pointy edges, and bonding that to the Earth, you are asking to get hit.

If you really really want to ground something like that on your roof, this is about the only case I could think it might be smart to use a separate ground rod, and put that conductor in a schedule 80 conduit so when it explodes its less likely to damage your home, and easier to replace.