Does the California Electrical Code allow one of the two required 20A circuits powering the wall / floor receptacles to also power a dishwasher?
Bonus question: If not, and the dishwasher requires its own circuit, may that circuit also power the gargabe disposal?
Please cite code sections if you can. My hunch is that the answer is 'no', based on this:
210.52 B.1
In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
and
210.52 B.2
No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets. Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electrical clock in any of the rooms specified in 210.52(B)(1). Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired ranges, ovens, or counter-mounted cooking units.
thanks
tom