My hydronic system has a loop (or ladder) that visits baseboard radiators on four floors. All piping is hidden in the walls.

On the attached diagram, squares are windows, red is baseboard radiators, and black lines are potential configurations of the pipes in the wall. The tops of the black lines have bleed vents.

I would like to install Danfoss valves (TRVs) where the blue circles are, but this will only work if my hydronic system is in a 'ladder' configuration, rather than a 'loop' configuration.

Are most systems set up one way or another? Are there good ways of telling, short of ripping holes in the wall?

1

The temperature gradient between heaters will be different depending on how the system is arranged. A larger system is likely a two pipe system with the supply and return piped to each floor. Get an accurate clamp-on pipe temperature probe and the appropriate meter:

enter image description here

Open all windows, turn all heat full on at all locations and let the system stabilize for 20 minutes or so. Record the temperature at the inlet pipe and outlet pipe for each radiator. Highest temperature indicates closest to the supply line. Coolest temperature indicates closest to the return line. If the floors are run in parallel between supply and return, then the radiators closest to the supply line on each floor will be about the same inlet temperature. Follow the temperature gradients and map out your piping.

Edit: I should mention that this test relies on the boiler running continuously. If your boiler is cycles frequently because it is oversized, then measuring the system temperature gradients will be tricky. You will need to pay attention to the varying supply temperature.

  • Interesting idea. In theory, there should be a 10-20 degree loss across the entire loop. However, as there are four radiators, this implies a roughly 3-4 difference between one end of the pipe and the the other, which is within the range of error of the gadget. Seems, however, that using TWO of these simultaneously might work. Alternatively, an arduino with two accurate temperature readers at both ends of the pipe might work. – gbronner Oct 15 '15 at 14:37
1

So, there are no service valves on your radiators?

If you have service valves and you close one then all flow would stop in a loop.The parallel setup would still work on the other floors.

If there are no service valves you would have to break loose a union somewhere in the system remove ½ the union toward the supply and cap the pipe and then turn the circulator on. If it is a loop you won't get any flow. If it is a parallel setup the other floors will flow.

This would be some work but I think the verification would be more solid. Also, you were going to take the pipe apart for the valves anyway.

Good luck!

  • Nope :) From what I can tell, the house has 2 big loops (front and back) and 2 mini loops (basement, extension). Each loop has isolation ball valves at each end, as well as drain valves at each end. There are no valves at either end of the radiators -- the radiators appear to be simple copper pipes with aluminum fins. – gbronner Aug 6 '17 at 16:59