0

What are the recommended clearances for a gasoline or natural gas powered portable electrical generator, on all sides and top and bottom? The generator is about 5,000 watts.

3
  • 2
    I would imagine the manufacturer has specific recommendations in the manual for the generator, as it will also partially depend on where the exhaust and air intakes are located. Since you're saying "all sides" does this mean you're also intending to put it inside a structure of some sort? This may invoke fire and/or other building codes, depending on your jurisdiction.
    – gregmac
    Commented Oct 13, 2015 at 21:44
  • What is the make and model of the generator?
    – Tester101
    Commented Oct 13, 2015 at 21:55
  • @Tester101 I am considering the Honda 3000is and a tri fuel (to run on Nat Gas).
    – Yehuda_NYC
    Commented Oct 13, 2015 at 22:54

1 Answer 1

1

The general advice seems to be

  • 3 feet (1 meter) from buildings, equipment, and combustible materials.
  • 10 feet away from bystanders, children, and pets.

But the only way to know for sure, is to read the manufacturer's documentation for your specific unit.


This service manual says "Keep the generator at least 1 meter (3 feet) away, including overhead, from any structure..."

enter image description here

This owner's manual says "Operate generator at least 3 feet (1 meter) away from buildings and other equipment."

enter image description here

This operator's manual says "Keep the generator a minimum of 3 feet away from all types of combustible material."

enter image description here

and also says "Keep all bystanders, children, and pets at least 10 feet away."

enter image description here

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.