Does anybody know the pressure number (PN) of schedule 40 and schedule 80 PVC pipe commonly sold in the United States and Canada?

The PVC in my part of the world is classified by PN number, and I'd like to know which PN number is ideal for DWV applications.

I'm interested in finding out the pressure number that is equivalent to schedule 40 PVC. We'll be using 5 cm, 8 cm, 11 cm and 16 cm diameter pipes for DWV applications. Also, our climate is subtropical (i.e. warm) and the temperature does not go below freezing.

1

Schedule 40 PVC has a pressure rating of 120 psi to 810 psi, depending on pipe size, and temperature.

At 73°F the pressures are as follows:

  • 2" = 280 psi
  • 3" = 260 psi
  • 4" = 220 psi
  • 6" = 180 psi

Then as the temperature increases, you'll derate the values as such:

  • 80°F - 88%
  • 90°F - 75%
  • 100°F - 62%
  • 110°F - 51%
  • 120°F - 40%
  • 130°F - 31%
  • 140°F - 22%

-Source

Schedule 80 PVC has a pressure rating of 210 psi to 1230 psi, depending on pipe size, and temperature.

At 73°F the pressures are as follows:

  • 2" = 400 psi
  • 3" = 370 psi
  • 4" = 320 psi
  • 6" = 280 psi

Then as the temperature increases, you'll derate the values as listed above.

-Source

Pressure depends on temperature, size, and schedule.

0

We were always using sch 40 and 80 but on fire sprinklers (CPCV)and hydrostatic tested systems at 200 psi but make no mistake about it...you should have NO air in a system We pressured water pumped with water hydro pump...Air alone would blow up pipe but not sure what amount.Bigger systems we air tested at like 80 mainly to hear leaks before real inspection tests,with,say,fire dept. officials......just saying............