I have a 15 year old house, with a GFI in the basement, yesterday when I came home I found that it had tripped. I took everything off of the circuit and reset it. Within a couple of minutes it tripped again. Why is this happening?
1GFCI's will fail eventually. If it was installed 15 years ago it probably needs to be replaced.– ojaitSep 30, 2015 at 15:16
1 Answer
There are essentially two possible reasons:
- There is a ground fault in the wiring/fixtures/appliances it's protecting
- The GFCI itself is faulty
It really depends on what's on the circuit to determine if there is a fault somewhere. 15 year old wiring is likely to not be a huge issue. There could be water in a junction box. Simple receptacles and switches aren't too likely to have issues (though it wouldn't hurt to open them to take a look at the connections), but anything with active electronics in it (dimmers, USB chargers, etc) could definitely be the cause. Same goes for other fixtures -- lights, ceiling fans, etc.
You could replace the GFCI and see if it still happens -- if so, there's definitely a fault. If you don't have another GFCI already, this is a somewhat expensive way to test (though if it's fault, you'll have to buy one anyway).
If you happen to have another one you could swap in, that would be a cheap and easy way to test. Swap two, see if it still trips and if the same breaker trips, or the same circuit trips the new breaker.