Plywood would be laying horizontally and be cut 8' x 8". Assuming fairly uniform load, with plates the full top and bottom length of it, is there a compression at which the plywood will fail? I'm assuming it would split or the glue would give at some point? But is this above 50,000 lb?
  • This would depend on the situation, but I'm sure the manufacturer can provide the PSI spec of the plywood you purchased. Sep 16, 2015 at 23:56
  • Need more info: are you compressing it through the 1/8" thickness, or along one of the long dimensions? How wide/tall is it? Sep 17, 2015 at 0:05
You appear to mean compression perpendicular to the plane of the plies.
Depends a good deal on what the plywood grade and material is, and the conditions it's operating under.
http://www.g-lumber.com/pdf/APA_Plywood_Design_Specification.pdf Suggests that between 340 and 160 lb/in**2 for dry service and 105-210 for wet service (for grades appropriate to wet service) so you'll need a fair number of square inches (which you have inconveniently left out of your question) to support 50,000 lbs.
Looks like 476 square inches on the low end to 147 on the high end (of loading) though any sensible person would derate a bit more for additional safety factor, or use 1/8" steel as a shim rather than 1/8" plywood. That's 3.3 square feet to a bit over 1 square foot.
8 feet (96inches) by 8 inches = 768 square inches, resulting in a loading for 50,000 lbs evenly distributed of 65 pounds per square inch, so per the above document you should be safe at that loading.