I'm trying to replacement my bathroom's light switch with a combo switch and outlet. It looks like this:

enter image description here

However when I opened up my light box I had two black wires and two white wires. The two white wires are connected together while the two black are connected to the old switch. On the box of the switch/outlet, it says it's not to be used to replace a switch with only two wires present. Can I still use this outlet? Where do I connect what? Do I leave the two connected white wires alone?

  • 5
    You need GFI protection for a receptacle in the bathroom. This can be achieved several ways, but the same device you show except the GFI version is easiest. – Speedy Petey Sep 12 '15 at 19:16
4

The switch/outlet combo you have could physically work, but as pointed out by @Speedy Petey, it would not be code complaint since all outlets in bathrooms need to be GFCI. Consider replacing it with a GFCI/switch combo such as this.

enter image description here

The wiring you have should work. One of the cables (which consists of one black and one white wire) is from the mains, and the other cable (black and white) goes to the existing light fixture. You need to determine which is which. The easiest way to do this is with a non-contact tester.

non-contact

With the power on and the old switch turned off (first make sure no bare wires or contact points are touching anything metal), check to see which black wire causes the tester to beep. If they are already disconnected, just check each wire separately. The one that beeps is the constantly hot wire from the mains. The other black wire is a switched hot going to the fixture. Turn the power off at the circuit breaker and mark the constantly hot wire with a piece of tape. Disconnect the old switch.

Look at the new switch/outlet on the right side (the side with the black screws). If there is a metal connector showing between the two black screws, you only need to attach the hot wire to one of them. If there is no connector, you need to attach the hot to both of them. This can be done by adding two short pieces of black wire (called pigtails) to the hot wire and then connecting the other end of those new wires, separately to each screw.

Now connect the other black wire from the box (the switched hot to the fixture) to the brass screw on the left side of the switch.

If there is no green or bare wire coming from the existing cables, you cannot properly ground this device unless the box is metal and the cables are armored (covered in a spiral metal casing). If there is a green or bare wire, it should be attached to the ground screw. If the box and cables are metal, the metal attachment strap of the device provides a form of ground (but not the best).

If the cable is not armored and there are no ground wires, the outlet is protected by the GFCI circuit, but it is not grounded. It needs to be marked on the outside as No equipment ground.

 Images and links are for illustration only, not an endorsement of goods or sources
|improve this answer|||||
  • It DOES NOT matter if it's close to the sink. GFI protection is 100% required for a receptacle like this in a bathroom, regardless of where it is. – Speedy Petey Sep 12 '15 at 19:15
  • @SpeedyPetey You are right. Answer modified. Please feel free to edit further if there are other errors or clarification would be helpful. – bib Sep 12 '15 at 19:33
2

You've got everything you need.

  • Turn off the breaker, and make sure power is off. -Use a small bit (6-8") of white wire, to make a pigtail from the bundle of white wires.
  • Connect the other end of the white pigtail, to the silver colored screw terminal on the device.
  • Follow the instructions provided with the device, to connect the black wires.
  • Use a bit of green or bare wire to ground the device.
  • Mount the device in the box.
  • Restore power to the circuit, and test the functionality of the device.
|improve this answer|||||
  • Thanks for the help. I don't have a green or bare wire within the existing setup though. Do I still need to ground it then? I've also found some differing diagrams about where to put the black wires so pardon if this is stupid but do I just attach the two black wires to the two black screws on the right? – Alex Sep 12 '15 at 17:06
  • @Alex Read the instructions that were included with the switch, it will tell you how to connect the black wires. – Tester101 Sep 12 '15 at 19:16
1

You cannot do what you want to do with only 2 insulated wires between the light and the switch box unless there is a second cable in the switch box.

By your description the switch is in a "Switch Leg." That is the electrician vernacular for a 2 wire cable which originates at a lighting outlet and ends at a switch box and is used to take the energized conductor of the lights supply down to the switch and back. It is important to note that the National Electric Code requires that the white or Grey wire be coded to a different color when it is used as an energized conductor. The NEC further requires that the White or Grey colored conductors; in addition to being re-identified; must only be used as the supply to the switch and not as the return from the switch.

Before re-identifying was required the splicing of the black of the supply cable to the white of the switch leg cable was a "tell" that the cable with the white wire spliced to the to the black was a switch supply. That was done to assure that the 2 wires attached to the fixture would also be black and white and were therefore more likely to be attached to the fixture correctly. It was not that long ago that nearly all luminaires were assembled with Edison screw shell bulb sockets. The NEC requires that the grounded current carrying conductor be terminated to the screw shell and not to the center contact.

If I misunderstood your question please tell us so that we can try again.