I have an existing switch that controls the lower half of an outlet we use for a floor lamp. no other lights or fan in the room.
If I use a triple rocker how can I wire the switches to control a fan light combo on the ceiling?
Can I draw power from the switch?
How do I maintain the switch control of the outlet but also use the same box??
I would run 14/3 from the switches to the light and fan. But and unsure what wires go where and get pigtailed ect. A diagram would be appreciated
enter image description hereenter image description here
    If your plan is to run wires to the ceiling fan/light unit from the existing switch box you need to first ensure that there is a neutral conductor available in the switch box. Older homes often have only "hot" and "switched hot" conductors in the switch box, no neutral. If you do not understand this... you need to do some basic study of common household electrical circuits before attempting this job, or hire an electrician. Aug 17, 2015 at 2:20
  • Turn off the power at the breaker. Remove the switch cover plate. Remove the switch mounting screws, and gently pull the switch out of the box. Take some photos, or draw a diagram depicting the wiring within the box. Then post the photos/diagram here.
    – Tester101
    Aug 17, 2015 at 10:16
  • hope the photo helps tester101
    – Ian C
    Aug 17, 2015 at 21:35
You currently have two cables in the box. One is the power source, and has just a black (hot), a white (neutral) and a bare (ground) wire. The second cable has a black (hot), a red (hot), a white (neutral) and a bare (ground).
As currently wired, the incoming black is attached to the outgoing black and to the switch via a pigtail. This makes the unswitched half of the outlet always live and provides a hot connection to the switch. The red wire is attached to the other side of the switch and provides a switched hot to the second part of the outlet. The neutrals are connected together in the box and the white wire at the outlet itself covers both halves of the switch (only the hot side has separate connections).
Adding other switched lines is fairly straightforward (this assumes that you have sufficient amperage to cover the additional fan and light).
As you surmised, you need a three wire (plus ground) cable. The new white is connected to the existing whites. If you pick a triple switches with a common hot terminal (most are configured this way), just move the existing hot pigtail from the old switch to the common terminal on the new switch. This provides hot to all three switch units. Then attach the red wire for the outlet to one of the other switch terminals, and the new red (from the fan or light) to another switch terminal and the new black (light or fan) to the last terminal. You can swap these three wires to assign whichever switch unit you want to each device.
Connect all ground wires together.
You are good to go.
[I will try to add a diagram later if I have time.]