My main electrical service runs overhead from a pole behind my unattached garage, to the back of the house. There is also an underground conduit from the house to the garage supplying a sub panel there. Because I've had tree limbs pull this line down in a storm, and because the overhead wires are in the way of some home improvement projects, I've been considering having the lines buried. I'm wondering if I have another option. Can I have things rewired so the garage panel becomes the main panel supplying the panel in the house? This would allow a very short overhead connection from the pole to the garage.
Thank you for any feedback.
    You'll have to have the meter moved, put new conductors between the buildings, and possibly make a few other upgrades. But it's likely possible.
    – Tester101
    Jul 12, 2015 at 22:04
There's a few ways to do this, though service conductors cannot pass through another building, so all the methods will have to avoid that.
One option would be to install a service disconnect, and then branch from that to the panels.
service disconnect
With this method, you'll handle all the grounding and bonding of the neutral in the disconnect. So you'll install 4 wire feeders from the disconnect to each panel, and keep the neutral isolated in each panel.
Another option is to use the first panel as the service disconnect, and feed the second panel from the first.
feed through panel
With this method, you'll handle all the grounding and bonding of the neutral in the first panel. So you'll feed the second panel with a 4 wire feeder, and isolate the neutral in the second panel.
With is approach, the first panel will have to be rated to handle the total current of both panels.
In all cases, you're going to need properly sized feeders, and a grounding electrode system for each building.
The scope of this project is far too vast for a short answer format site, such as this. I've given a high-level overview of how you might approach the project. For a more detailed plan, please contact a local licensed Electrician.